    Overhead power lines wires and strings deviation

    What I was saying was that when I tried to solve this problem, I tried to find the transverse load from the sine of this 29 deg angle, which was obviously a mistake. The angle between the suspension insulator string and the straight line has nothing to do with the calculations for transverse...
  2. S

    Overhead power lines wires and strings deviation

    Hello PhanthomJay, thank you for your reply. You are pretty close for the tension - it's about 40MPa, which for this conductors makes about 17,6kN. What I was not sure was how to calculate the transverse load from the conductors tension. At first I got confused that I have to use the angle...
  3. S

    Overhead power lines wires and strings deviation

    Hello to all of you. I have the following case to solve. I have three overhead power line towers. The first and the third are with tension insulator strings, and the second is with suspension insulator string. During the design process i noticed that the second tower is located incorrectly and...