What is the fault current calculation for a broken line touching a pole?

AI Thread Summary
The discussion centers on calculating fault current when a broken line contacts a grounded pole, with the assumption that the neutral of the distribution transformer is not grounded. The participant acknowledges the role of capacitance between the lines and the ground, questioning whether this model is sufficient for calculating fault current. They suggest that the fault current would be minimal, primarily influenced by the capacitance of the healthy phases and the transformer winding. The impact of a hypothetical scenario where a monkey touches a live line while on the pole is also considered, with the conclusion that the current would likely remain insignificant. The participant expresses uncertainty about the nature of the Earth as a conductor and its ability to handle large currents.
I_am_learning
Messages
681
Reaction score
16
Last time I was talking about Isolated Voltage, and some of you people were really helping me about, but I posted (did) something stupid and got the thread deleted.
I am sorry for that.

Now, I want to talk about my confusion in a different (safe) way.
fault.jpg


The above figure shows a distribution line along with a Pole. I understand there exist capacitance between lines (shown in pink) and between lines and ground(shown in green) if we treat the Earth as an infinite equipotential surface (conductor). Also the pole is grounded. But please note that the neutral of Distribution Transformer isn't grounded. Also assume that no grounding is done in any other part of the system.

Now, the question is what happens if one of the lines break and comes in contact with the body of the pole? How much fault current will flow?

Thanks.
 
Engineering news on Phys.org
The point I am unsure off is, can I calculate the fault current based on above model (capacitances between lines and Between line and earth) only OR I have somthing missing in that model?
If I follow only that model, the fault current will not be significantly large, only the capacitor between the faulted Line and Earth shorts out. The faulted line is still capacitively Isolated from other lines.
Do the circuit breaker trip?
 
in this circuit , fault current would depend on capacitance of healthy phases with ground. capacitance of transformer winding with tank(which would be grounded) will play significant role.

current would be proportional to system voltage. and for low voltage <1kV current would be insignificant.
 
Ok, instead of one of the phase shorting to the pole, If a monkey sitting on the pole touches one of the phase how much (tentative) current will flow?
Its again dependent upon the various capacitances and, I think its magnitude will be insignificant.

The reason I am being not totally sure is because someone here had previously told me that the Earth isn't something to be taken just as a plain conductor. It can sink in huge currents, weather you close the circuit or not! Its actually at 0 potential he said, and that anything that comes between Earth and high potential will be burned down.

I don't have enough reason to agree to that.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top