In pump installations, using two pumps in parallel typically aims to double flow, while series configurations are intended to double pressure. However, in practice, flow rates often do not reach the expected combined capacity due to system resistance and design limitations. Increasing the diameter of the main pipe can help, but it may also reduce head and increase power consumption, complicating the flow dynamics. The resistance in the piping system can hinder achieving the desired flow rate, as it follows a binomial relationship with flow rate. To optimize flow with two pumps, it is suggested to minimize the length of connecting pipes and use valves for better control.
eaaaazizo
Messages
12
Reaction score
0
in college days it is known that if you want double pressure install the pumps in series if you need double flow install the pumps parallel. but in actual field i have two pumps installed in parallel in Sewer Pump Station one as on duty and the second one is assist. but while both pumps running, i never get flow rate equal to two pumps flow rate for example i have two pumps with each pump capacity 100 l/s but if both if them runing i have only 120 l/s

i can't understand this ? and how to control raising main diameter to get maximam flow while both pumps are running ? it is really difficult ?
 
Engineering news on Phys.org
In a fixed piping system, you can neither double the pressure without affecting flow nor double the flow without more pressure. The rule of thumb ignores the piping system.
 
russ_watters said:
In a fixed piping system, you can neither double the pressure without affecting flow nor double the flow without more pressure. The rule of thumb ignores the piping system.

Thanks for your kind replay but now in design stage how could I reach douple flow while both pump runing by increasing pipes dia ??
 
With two pumps in parallel and twice the piping cross sectional area.
 
but if i increased the cross sectional area to be twice. while one pump runing the area will be very wide which will reduce the head and increase the flow and increaing the power consumed
 
The pipe system flow resistance normally is binomial equation to flowrate. So when two pumps working together, the system flow resistance will also increase, finally you will not get double flowrate.

One way to increase the flowrate for two pumps working, you'd try best to separate the connecting pipe of the two pumps. Like as: the pipe for each pump only gather with short length; each pump outlet need valve to control "open" or "close".
 
How did you find PF?: Via Google search Hi, I have a vessel I 3D printed to investigate single bubble rise. The vessel has a 4 mm gap separated by acrylic panels. This is essentially my viewing chamber where I can record the bubble motion. The vessel is open to atmosphere. The bubble generation mechanism is composed of a syringe pump and glass capillary tube (Internal Diameter of 0.45 mm). I connect a 1/4” air line hose from the syringe to the capillary The bubble is formed at the tip...
Thread 'What type of toilet do I have?'
I was enrolled in an online plumbing course at Stratford University. My plumbing textbook lists four types of residential toilets: 1# upflush toilets 2# pressure assisted toilets 3# gravity-fed, rim jet toilets and 4# gravity-fed, siphon-jet toilets. I know my toilet is not an upflush toilet because my toilet is not below the sewage line, and my toilet does not have a grinder and a pump next to it to propel waste upwards. I am about 99% sure that my toilet is not a pressure assisted...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...