Confirmation of transformer efficiency

In summary, the conversation revolved around determining the equivalent circuit model and efficiency of a transformer. The steps for both open circuit and short circuit tests were discussed. There was a discrepancy in the calculations for the voltage reading, but it was eventually resolved. The final efficiency of the transformer was determined to be 96.7%.
  • #1
sandy.bridge
798
1

Homework Statement


The problem at hand involved determining the equivalent circuit model of the transformer and then determining its efficiency. I for the life of me cannot get the results that he has provided us with, so perhaps someone here can either confirm my results or indeed confirm his.

Here are my steps:
For open circuit,
[tex]\theta_{OC}=arccos((186W)/((240V)(5.41A)))=81.7639° [/tex]

[tex]Y_E=(5.41A)/(240V)e^{-j81.76°}=0.003229-j0.02231[/tex]

[tex]R_{G,S}=1/0.003229=310Ω,X_{M,S}=1/0.02231=44.825Ω[/tex]

Short circuit test:

[tex]\theta_{SC}=arccos(617W/((48V)(20.8A)))=51.3°[tex]

[tex]R_{eq,p}=1.42615Ω, X_{eq,p}=1.81426Ω[/tex]

I put everything in terms of the LV side and hence [itex]R_{G,S},X_{M,S}[/itex] remain the same. The primary equivalents are divided by a factor of a=2400/240-100.

Full load on secondary side at 0.8 PF:
[tex]I_S=(50 000VA)/(240V)e^{-j36.9°}[/tex]

hence
[tex]V_p/a=(0.0142262+j0.0181426)(208.33e^{-j36.9°})+240V=484.641e^{j0.146956}[/tex]

[tex]P_{Cu}=(208.33A)^2(0.0142262Ω)=617W[/tex]
[tex]P_{Core}=(484.641V)^2/(309.7W)=758W[/tex]
[tex]P_{Supplied}=(240V)(208.33A)cos(36.9°)=39984W[/tex]

The efficiency turns out to be 96.7%.
 

Attachments

  • Soln Transf Example.pdf
    33.5 KB · Views: 195
Last edited:
Physics news on Phys.org
  • #2
How can there be a voltage reading if the transformer is short-circuited at the output? The problem makes no sense to me.
 
  • #3
The voltage reading is not on the short circuit. This is a standard problem in the textbook we are using.
Short circuit comes with a voltage reading, current reading and a power reading.
Open circuit comes with a voltage reading, current reading and a power reading.

I already know where my mistake was which was at this point:
[tex]V_p/a=(0.0142262+j0.0181426)(208.33e^{-j36.9°})+240V=484.641e^{j0.146956}[/tex]
Somehow I managed to calculate this step wrong three times. The values are right, but the end result should have been:
[tex]V_p/a=(0.0142262+j0.0181426)(208.33e^{-j36.9°})+240V=244.643e^{j0.29112}[/tex]
Using this result I ended up with the same percentage at 0.8 PF.
 

1. What is the purpose of confirming transformer efficiency?

The purpose of confirming transformer efficiency is to ensure that the transformer is operating at its optimal level and is not wasting energy. This helps to improve the overall efficiency of the system and can also lead to cost savings.

2. How is transformer efficiency measured?

Transformer efficiency is typically measured by comparing the amount of power that enters the transformer to the amount of power that exits. This is known as the transformer's power loss and is expressed as a percentage. The higher the percentage, the more efficient the transformer is.

3. What factors can affect transformer efficiency?

There are several factors that can affect transformer efficiency, including the type of transformer, its design, the materials used, and the operating conditions. Other external factors such as temperature, voltage fluctuations, and load variations can also impact efficiency.

4. How often should transformer efficiency be confirmed?

It is recommended to confirm transformer efficiency at least once a year, or more frequently if the transformer is operating under harsh conditions or experiencing high loads. Regular maintenance and testing can help to identify any potential issues and ensure the transformer is operating at its best.

5. What are some methods used to confirm transformer efficiency?

There are several methods that can be used to confirm transformer efficiency, including open-circuit test, short-circuit test, and ratio test. Other methods may include infrared thermography, dissolved gas analysis, and power quality analysis. The most suitable method may vary depending on the type and size of the transformer.