In summary, each phase of a three phase delta connected generator supplies a full load current of 100A at a voltage of 240V and at a power factor of 0.6 lagging.
  • #1
JGrecs
14
0

Homework Statement



each phase of a three phase delta connected generator supplies a full load current of 100A at a voltage of 240V and at a power factor of 0.6 lagging.

Find:
a) line voltage
b) line current
c) the kVA rating
d) the KW

2. The attempt at a solution

a) Line voltage = Phase Voltage (in delta)

VP= VL/1.732
VP= 240/1.732
VP= 138.5V

Therefore the line voltage is 138.5 volts.

b) Phase current at full load= 100A

Line current= Phase current x 1.732

IL= (100)(1.732)
IL= 173.2A

Therefore the line current is 173.2 amps.

c) kVA= (1.732)(VL)(IL)/1000

=(1.732)(240)(173.2)/1000
= 700VA

d) P= (1.732)(VL)(IL)(0.6)

= (1.732)(240)(173.2)(0.6)
= 43kW

How do these answers look? I am a little unsure of which voltages/currents to substitue into the kVA and P formulas.
Thanks,
 
Last edited:
Physics news on Phys.org
  • #2
I may be a bit rusty at power circuits, but aren't the line voltages equal to the phase voltages for a delta-connected generator?
 
  • #3
^ Yes. What I am unsure of is question c and d. I am not exactly sure which values to substitute into kVA= (1.732)(VL)(IL)/1000 and P= (1.732)(VL)(IL)(0.6). I used the line current and line voltage for both. Is this right? (assuming that the line current I calculated is correct to begin with.)
 
  • #4
Hi JGrecs, my answers.

a)240 volts
b)100 amps
c)240*100*1.732=41.6KVA
d)240*100*1.732*0.6 =25KW

The thing here is that the question IMO isn't worded very well so that might be half the problem.

Remember when connected in delta the line and phase voltages are the same, while phase and line currents will be different.

When connected in star line and phase voltage will be different, while line and phase currents will be the same.

Is there an actual answer included with the question?
 
Last edited:
  • #5
Aussielec said:
Hi gneill, my answers.

a)240 volts
b)100 amps
c)240*100*1.732=41.6KVA
d)240*100*1.732*0.6 =25KW

The thing here is that the question IMO isn't worded very well so that might be half the problem.

Remember when connected in delta the line and phase voltages are the same, while phase and line currents will be different.

When connected in star line and phase voltage will be different, while line and phase currents will be the same.

Is there an actual answer included with the question?

No answers provided. You say for b), that the line current is 100A. Does this mean that the Load current=Line current for delta connections? Also for question a), If I am not mistaken, the phase voltage is calculated Vload/1.732 which comes out to 138.5V. So shouldn't VLine be 138.5V?
 
Last edited:
  • #6
When connected in delta line and phase current will be different. But this what I can't understand- Where is this 100 amps measured from? The generator windings or the line?

The question reads. "supplies a full load current of 100A"? But from where?
 
  • #7
Aussielec said:
When connected in delta line and phase current will be different. But this what I can't understand- Where is this 100 amps measured from? The generator windings or the line?

The question reads. "supplies a full load current of 100A"? But from where?

each phase of a three phase delta connected generator supplies a full load current of 100A

The Windings?

100A per phase/winding
 
Last edited:
  • #8
As I said, I'm a bit rusty on multiphase power system measurement/specification conventions. But if we were to assume that the load consists of identical impedances across the phases supplies, and each is drawing 100A with a power factor of 0.6, then we could determine the appropriate impedance (pf corresponds to 53.13° lag angle for the current) and create a Spice model:

attachment.php?attachmentid=56738&stc=1&d=1363319778.gif

[note that the ground is for the convenience of the simulation software]

Each load will draw its 100A, and each phase voltage source will produce 100A, all shifted according to the phase angles of the supplies.

In order to answer the given problem, I would first have to recall or find out: does a single impedance and the power it dissipates characterize the system, or should the power phasors of each load be summed to find total kVA and kW numbers?
 

Attachments

  • Fig1.gif
    Fig1.gif
    6.1 KB · Views: 1,166
  • #9
Ok,

A) According to textbook: VLoad=VPhase=VLine (Delta)

Therefore VLine in this case = 240V

B) According to textbook: ILine=IPhase X 1.732 (Delta)

IPhase=100A (Would you agree)?

Therefore ILine= 173.2A

c)

kVA= kW/PF

kVA= 43/0.6
kVA= 72kVA

or

kVA= 240 X 100 X 1.732
kVA= 72kVA

or

kVA= 240 X 1.732 X 3
kVA= 72kVAD) Textbook: P= 1.732 X VLine X ILine X PF or P= 3 X VPhase X IPhase X PF

P= 1.732 X 240V X 173.2A X 0.6
P= 43kW

or

P= 3 X 240V X 100A x 0.6
P= 43kW These should all be correct. Any objections brehs?
 
Last edited:
  • #10
Thanks for the help, Gneill & Aussielec.
 
  • #11
Your results look okay to me!
 

What are 3-phase circuits and how do they work?

A 3-phase circuit is an electrical network that uses three alternating current (AC) power sources with a phase difference of one-third of a cycle between each source. This creates a more efficient and balanced distribution of power compared to a single-phase circuit. In a wye or delta configuration, the three phases are connected in either a star or triangle shape, respectively.

What is the difference between a wye and delta configuration in 3-phase circuits?

In a wye configuration, the three phases are connected at a common point, forming a "Y" shape. This allows for a neutral wire to be connected, providing a return path for unbalanced currents. In a delta configuration, the three phases are connected in a closed loop, forming a "triangle" shape. This does not have a neutral wire and may require more insulation for higher voltages.

What are the advantages of using 3-phase circuits?

One advantage is that 3-phase circuits are more efficient in transmitting and distributing power compared to single-phase circuits. They also require less wiring and have a higher power capacity. Additionally, they provide a more balanced distribution of power, reducing the risk of overloading or voltage drops.

How do you calculate the total power in a 3-phase circuit?

The total power in a 3-phase circuit can be calculated by using the formula P = √3 x V x I x cosθ, where P is the total power, V is the line voltage, I is the line current, and cosθ is the power factor. This formula takes into account the three phases and the power factor, which is the ratio of real power to apparent power.

What are some common applications of 3-phase circuits?

3-phase circuits are commonly used in industrial and commercial settings, such as factories, power plants, and large buildings. They are also used in electric motors, heating and cooling systems, and high-power appliances. In the home, they may be used for larger appliances such as washing machines and air conditioners.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
11
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
14
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
23
Views
5K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
15
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
Back
Top