Air to steam heat exchanger

In summary, the original design for the tin plating line was superheated steam at 300 degrees Celcius, but the plant reduced steam pressure and now our steam inlet temperature is much lower (less than 150 degrees Celcius). The inlet air is what we want to heat up for the drying. It comes in between 15 degrees Celcius in winter to up to 40 degrees Celcius in the summer.Since I am limited to steam inlet temperature being lower, is there a simple way to locally heat the steam again to make my outlet air temperature higher? Would an tankless boiler be effective? I have a tank of condensate at about 100 degrees Celcius in the basement below the line, but I am
  • #1
rnmconnor
2
0
Our tin plating line has several of these. Original design was superheated steam to 300 degrees Celcius, but the plant reduced steam pressure and now our steam inlet temperature is much lower (less than 150 degrees Celcius). Inlet air is what we want to heat up for the drying. It comes in between 15 degrees Celcius in winter to up to 40 degrees Celcius in the summer.

Since I am limited to steam inlet temperature being lower, is there a simple way to locally heat the steam again to make my outlet air temperature higher? Would an tankless boiler be effective? I have a tank of condensate at about 100 degrees Celcius in the basement below the line, but I am no better off unless I can heat this up to superheated steam again, but at least I have a source to start from. Any feedback would be great!

Thanks;
Rob
 
Engineering news on Phys.org
  • #2
Why would reducing the pressure reduce the superheat? Or do you really mean saturated steam? The main problem with reducing pressure is generally a loss of flow rate and adding superheat won't fix that. Can you increase the pipe size?
 
  • #3
Hi Russ;

Thanks for your response.

I guess my numbers are off. I am new to the area and still coming up to speed with the equipment.

You are right, it is saturated steam, and the temperature follows the steam table. Reduce the pressure and temperature goes as well. From what I am told, looking at the drawings as well, the original spec on the steam to air heat exchanger was 150 psi for steam at 366 deg. F. But they applied 250 psi saturated steam into the system, which was over 400 deg. F, my guess is with a high temperature like that, it doesn't matter so much efficiency wise for the heat exchanger, you could get outlet air temperature at 250 to 300 F no problem. But now with saturated steam pressure at 100 PSI we are seeing steam inlet temperature of 300 deg F in and outlet temp of 295 F on the piping. Our air outlet temp is only 146 deg. F

The heat exchanger has been rebuilt once. We were thinking of adding a tankless boiler locally since there is no plant plantwise to increase steam pressure. Somehow we have to boost either steam inlet temperature or heat exchanger efficiency to get the maximum out of air outlet temperature. If we need to go back to the drawing board to increase the heat exchanger iefficiency, then that may be our best cost effective option.

Regards;
Rob
 
  • #4
Reducing the Air flow will increase the Air temp but the heat output of the heat exchanger will drop badly.Ie must less air coming off at a higher temp. less total heating value of said air as there is less of it. Make sure there is no air trapped in the heat exchanger (steam side) Don't burn yourself I know nothing about how to do that.
 
  • #5
I guess if the end bends pipe temp. matches the saturation temp. for the pressure of the steam there will be no air trapped.
 
  • #6
otherwise some one is going to have to spend some money bigger heat exchangers or another one in series in the air flow, a higher pressure boiler or perhaps one could add electric elements or heat some other way.
 
  • #7
Can exhaust air from the system be used to preheat the incoming air in a air to air heat exchanger to save heaps of energy?
 

1. What is an air to steam heat exchanger?

An air to steam heat exchanger is a device used to transfer heat between a hot steam source and a cooler air source. It typically consists of a series of tubes or plates that allow the steam to flow through and transfer its heat to the surrounding air.

2. How does an air to steam heat exchanger work?

An air to steam heat exchanger works by using the principle of heat transfer. The hot steam flows through the tubes or plates, and as it comes into contact with the cooler air, heat is transferred from the steam to the air. The cooled steam then exits the heat exchanger, while the heated air can be used for various purposes.

3. What are the benefits of using an air to steam heat exchanger?

An air to steam heat exchanger offers several benefits, including energy efficiency, cost-effectiveness, and versatility. It allows for the efficient transfer of heat between two sources, reducing the need for additional heating or cooling systems. It is also a cost-effective solution compared to other heating methods, and it can be used in a variety of industries and applications.

4. What are the common uses for an air to steam heat exchanger?

An air to steam heat exchanger is commonly used in industrial applications, such as in power plants, chemical plants, and refineries. It is also used in commercial and residential heating systems, as well as in HVAC systems to improve energy efficiency. Additionally, it can be used in food processing, oil and gas production, and other industries that require heat transfer.

5. How do I choose the right air to steam heat exchanger for my application?

Choosing the right air to steam heat exchanger depends on several factors, including the desired heat transfer rate, the temperature and pressure of the steam and air, and the available space for installation. It is important to consult with a knowledgeable engineer or supplier to determine the best heat exchanger design and materials for your specific application.

Similar threads

  • General Engineering
Replies
6
Views
3K
  • General Engineering
Replies
7
Views
2K
  • General Engineering
Replies
5
Views
3K
Replies
1
Views
1K
  • General Engineering
Replies
1
Views
2K
  • General Engineering
Replies
9
Views
4K
Replies
1
Views
2K
  • General Engineering
Replies
2
Views
3K
Replies
5
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
Back
Top