ok so everytime I think that I have understood the concept of Energy transmission, losses and voltage drop, I get even more confused about things.
I have searched several threads on this forum and the physics forum but failed to find anything that directly answers my query. So I kindly request your help on the fundamental concept.
I will try to give an example and I would like you guys to correct me where I am wrong -- Thanks in advance!
-------------------------------------------------------------------------
If a 1 MW load is to be supplied by a 10kV feeder, and the cable resistance is 1 ohms, then the current drawn by the load (or the current traveling on the cable) is:
I = P/V = 100 A
The line losses are I^2*R = 10 kW and the Voltage Drop = I*R = 100 V
Is it right to say that:
a) Voltage at supply point is 10kV
b) Voltage at consumer end is 9.9kV (10kV - 100V)
c) The current through the cable is 100A
d) The power required is 1 MW but the actual power being delivered is 0.99 MW [ (P - losses) OR (V*I = 9.9kV * 100A) ]
e) hence the efficiency of this system is 0.99MW/1MW * 100 = 99% efficient?
------------------------------------------------------------------------------
Please correct me where I am wrong.
Thank you.
ok so everytime I think that I have understood the concept of Energy transmission, losses and voltage drop, I get even more confused about things.
I have searched several threads on this forum and the physics forum but failed to find anything that directly answers my query. So I kindly request your help on the fundamental concept.
I will try to give an example and I would like you guys to correct me where I am wrong -- Thanks in advance!
-------------------------------------------------------------------------
If a 1 MW load is to be supplied by a 10kV feeder, and the cable resistance is 1 ohms, then the current drawn by the load (or the current traveling on the cable) is:
I = P/V = 100 A
The line losses are I^2*R = 10 kW and the Voltage Drop = I*R = 100 V
Is it right to say that:
a) Voltage at supply point is 10kV
b) Voltage at consumer end is 9.9kV (10kV - 100V)
c) The current through the cable is 100A
d) The power required is 1 MW but the actual power being delivered is 0.99 MW [ (P - losses) OR (V*I = 9.9kV * 100A) ]
e) hence the efficiency of this system is 0.99MW/1MW * 100 = 99% efficient?
------------------------------------------------------------------------------
Please correct me where I am wrong.
Thank you.