A customer requested a quote for a plate heat exchanger with specific flow rates and temperature deltas on both sides. The discussion highlights that different flow rates cannot yield the same temperature drop if the delta T is identical, due to energy conservation principles. It is noted that if the specific heat capacities of the fluids were different, varying flow rates could potentially result in the same delta T. However, given the close temperature values presented, the specific heat is effectively constant, making different flow rates unfeasible. The consensus emphasizes the importance of understanding energy conservation in heat exchange systems.
TSN79
Messages
422
Reaction score
0
A customer of mine came to me asking for a price on a plate heat exchanger for water. The data he brought me was the following:

Primary side: 1,9 l/s and 12/16 C.
Sec. side: 2,4 l/s and 14/18 C.

I was just wondering if it is even possible to have different flows when the delta T is the same on both sides...?
 
Engineering news on Phys.org
No, conservation of energy requires that they be the same.
 
Thx, good to get that confirmed. Any tips on how I can easily explain this to him so that he "gets it" ?
 
If the temperatures of the fluid were drastically different it would be possible for different flowrates to give identical drops in temperature as specific heat is temperature variant. However, in this case the temperatures are so close that specific heat is in effect constant.
---------------
http://www.cfdengineer.com.
 
Is it the same liquid on each side? If the specific heat capacities are different you might get the same Delta T with different flow rates.
 
I agree with doc.

I am not an engineer, just a Mechanical contractor. The Delta T's you listed are so close, they are in effect the same. If the fluids were different, then maybe. But you deltas are so close...
 