How to calculate reactive power for 3 phase induction motor

by ws0619
Tags: induction, motor, phase, power, reactive
Share this thread:
ws0619
#1
Nov19-12, 03:58 AM
P: 54
Hi all,
I would like to install Capacitor Bank into my control panel board which contains of few 10HP induction motors. Currently I'm just able to measure the Ampere for every induction motor by using current meter.
How to calculate the reactive power for 10HP 3phase 4pole induction motor by just using Amp value?

One of my 10HP motor:
Voltage: 415V
Amp: 7.8A (measure)
I am using 10HP Teco motor with 4pole and 1450rpm.
Please enlighten me.
Thanks!
Phys.Org News Partner Engineering news on Phys.org
Eye implant could lead to better glaucoma treatment
Electricity helping the blind navigate
Lawsuits challenge US drone, model aircraft rules (Update)
russ_watters
#2
Nov19-12, 11:13 AM
Mentor
P: 22,292
It can't be calculated from that information. Can you read the motor nameplate? What is the model number? Full load amps?
Windadct
#3
Nov19-12, 02:09 PM
P: 564
This will really depend on how the motors are loaded as well - a 10HP motor that is mechanically delivering 10HP has much better PF than the same motor with only 7HP pf load. Really the only way to do this IMO is with measurements - and if the load on the motor varies, you really only want to compensate for the "best case" - not the worst.
Starting motors on a system with excessive online capacitance provided too much inrush and can over time damage the motor.
You can add the cap to each motors line - so they are switched on an off with the motor - but this also causes large inrush currents - not something I would just throw together. In larger systems they actually us a controller that measures the current and PF and then switches in the appropriate capacitance....
Lastly - if you are getting a KVAR charge on your electric bill the utility may offer some engineering - they would prefer to sell you energy - not VARs because they can charge more for them.

russ_watters
#4
Nov19-12, 11:02 PM
Mentor
P: 22,292
How to calculate reactive power for 3 phase induction motor

Quote Quote by Windadct View Post
This will really depend on how the motors are loaded as well - a 10HP motor that is mechanically delivering 10HP has much better PF than the same motor with only 7HP pf load.
I'm a bit unclear on this point. My thought was that while you are certainly correct that the PF depends on the load, that's just because the active power depends on the load. That would leave the reactive power constant and make the the PF (the ratio of the active to total) vary. The OP actually just asked about the reactive power. I am uncertain of this, but I do know that motors are generally provided constant size/output capacitors for PF correction. Still:
Really the only way to do this IMO is with measurements - and if the load on the motor varies, you really only want to compensate for the "best case" - not the worst.
Agreed. Another reason besides what you said is the utilities generally don't want leading power factor, so the capacitors should be sized to not quite compensate for all of the reactive power.
Lastly - if you are getting a KVAR charge on your electric bill the utility may offer some engineering - they would prefer to sell you energy - not VARs because they can charge more for them.
Indeed the bill itself probably provides some insight. But depending on how big of a facility it is, it may not be enough information to size the capacitors.

Either way, yes: a true power meter attached to the motor is preferred here. Second choice would be to find the manufacturer's rating.


Register to reply

Related Discussions
How to calculate the slip in an three phase induction motor Electrical Engineering 2
How do calculate the current when I have the active power and reactive power and volt Electrical Engineering 7
Electrical Machines and Power Electronics - 3 phase, 6 pole induction motor Engineering, Comp Sci, & Technology Homework 1
3-phase Induction Motor Electrical Engineering 0
Effect of sudden loss of reactive power for an induction generator Electrical Engineering 0