Door Grilles/Pressure relief grilles in hospital rooms

  • Thread starter Thread starter tj00343
  • Start date Start date
AI Thread Summary
The discussion centers on the challenges of using door grilles in hospital settings, particularly in critical areas like isolation and operating rooms, where maintaining specific pressure differentials is essential for contamination control. While door grilles can complicate achieving desired pressurization due to airflow variations, designing these rooms to be tightly sealed and incorporating pressure relief dampers is suggested as a potential solution. The importance of balancing airflow to prevent excessive pressure that could hinder door operation is emphasized, along with the acknowledgment that hospital regulations may vary. The conversation also touches on practices from laboratory and GMP environments that prioritize precise pressure control. Overall, the design and ventilation strategies for hospital rooms require careful consideration to ensure safety and functionality.
tj00343
Messages
59
Reaction score
0
TL;DR Summary
Hello,
Are door grilles/pressure relief grilles recommended in hospital spaces. Specifically, rooms that have negative or positive pressure requirements.
I'm wondering about the provision of door grilles in hospitals. I can imagine that they would not be allowed in critical environment rooms such as isolation rooms and operation theaters as it wouldn't be possible to achieve the recommended pressure difference if air is continuously leaking in or out and the idea is to isolate these areas, However, how can I be sure that these spaces won't become excessively over pressurized (or under pressurized) and cause my fans to be choked off or cause problems with doors opening. All fans are constant drive based on the request of the client.
 
Engineering news on Phys.org
I'm less familiar with hospitals, but I do a lot of lab and GMP manufacturing work...

I wouldn't say "not allowed", but yes, due to the large airflow through the grille/louver it is harder to achieve the desired pressurization. And it isn't just the total airflow that is a problem, but the variation is large too. Typically if you are trying to achieve a specific pressure*, you would provide a supply and return, and start with an assumed differential airflow needed across the door (frame) and any other leakage sources. Then the balancer will adjust the return to achieve the exact pressurization value desired. Smaller gaps mean less total transfer airflow and less adjustment to "dial-in" the pressurization you are looking for.

Conversely, if you have automatic control and a very "tight" room, it could have trouble making fine enough adjustments to maintain the pressure. I wouldn't expect hospitals to be too tight, though.

And again, I'm not sure of the regulations for hospitals; for some less critical applications, you just keep a certain differential airflow and don't worry so much about the exact pressure. That's common in labs. For GMP you need the pressure to be exact.
 
  • Informative
  • Like
Likes berkeman and Lnewqban
russ_watters said:
I'm less familiar with hospitals, but I do a lot of lab and GMP manufacturing work...

I wouldn't say "not allowed", but yes, due to the large airflow through the grille/louver it is harder to achieve the desired pressurization. And it isn't just the total airflow that is a problem, but the variation is large too. Typically if you are trying to achieve a specific pressure*, you would provide a supply and return, and start with an assumed differential airflow needed across the door (frame) and any other leakage sources. Then the balancer will adjust the return to achieve the exact pressurization value desired. Smaller gaps mean less total transfer airflow and less adjustment to "dial-in" the pressurization you are looking for.

Conversely, if you have automatic control and a very "tight" room, it could have trouble making fine enough adjustments to maintain the pressure. I wouldn't expect hospitals to be too tight, though.

And again, I'm not sure of the regulations for hospitals; for some less critical applications, you just keep a certain differential airflow and don't worry so much about the exact pressure. That's common in labs. For GMP you need the pressure to be exact.
Thank you , I've been reading up on isolation rooms and the general consensus is that they must be kept tight for the obvious reason of contamination prevention. Operation rooms and isolation rooms require a specified minimum pressure difference 2.5 Pa. I'm thinking about encouraging the architectural team to design these critical spaces specifically tight and placing pressure relief dampers ,as Lnewqban implied, in case of excessive negative or positive pressure.
 
tj00343 said:
I like it, if I'm getting you right, you're suggesting that the rooms be designed tight and utilizing pressure relief dampers in case of excessive pressure.
Please, take it only as an option to be considered, as I don't know what the code and regulations regarding ventilation and air balance in hospitals of your area is.

That is a common way to prevent excessive force to be applied to open or close doors of emergency-pressurized stairways in high-rise buildings.
Upon activation of the smoke alarm system, the shaft is pressurized by emergency fans, so people have fresh air in it while escaping the building.

The doors to get in and out of that shaft should be able to be opened by a elderly person, so the actual pulling or pushing force is measured during tests and is adjusted via balancing-weight manipulation of the gravity dampers.
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...
Back
Top