How to estimate the Startup torque of a pump motor

AI Thread Summary
To estimate the startup torque of a pump motor, it's essential to gather the torque-speed curve from the motor manufacturer. If this data is unavailable, the starting current can be approximated using a locked rotor test, where the starting current is calculated by multiplying the locked rotor current by the ratio of rated voltage to locked-rotor voltage. The equation for startup current is I_starting = I_lr * (V_line,rated / V_line,lr). Additionally, knowing the motor's impedance allows for theoretical calculations of starting current, taking into account both transient and steady-state components. Proper specifications on the motor nameplate can significantly simplify these calculations.
Su Solberg
Messages
72
Reaction score
0
Hi Guys,

I have a problem about the starting current of a pump's electrical motor.

I have the working condition of the pump (torque, power, speed, P and Q)

But how could I calculate the start up current of an IEC standard motor?
Seems I has to gather a Torque-speed curve from the supplier, right?

Also, in case it is not provided, how can I estimate the starting current and how to protect my motor to burn (since the starting current is 3 times more!? than the operation current )

p.s. since it's a a 10" pump, starting with inverter would not an economic choice. Direct on line would be better, I think.

Thanks in advance.

Regards,
Solberg
 
Engineering news on Phys.org
Su Solberg said:
Hi Guys,

I have a problem about the starting current of a pump's electrical motor.

I have the working condition of the pump (torque, power, speed, P and Q)

But how could I calculate the start up current of an IEC standard motor?
Seems I has to gather a Torque-speed curve from the supplier, right?

Also, in case it is not provided, how can I estimate the starting current and how to protect my motor to burn (since the starting current is 3 times more!? than the operation current )

p.s. since it's a a 10" pump, starting with inverter would not an economic choice. Direct on line would be better, I think.

Thanks in advance.

Regards,
Solberg

The manufacturer should be able to provide this information to you. However, you can also find it by testing the motor with a locked rotor. You can then find the starting current by multiplying that value by the ratio of the line (rated) voltage vs. the line (locked-rotor test) voltage.

CS
 
stewartcs said:
The manufacturer should be able to provide this information to you. However, you can also find it by testing the motor with a locked rotor. You can then find the starting current by multiplying that value by the ratio of the line (rated) voltage vs. the line (locked-rotor test) voltage.

CS

Thanks alot. I wonder which manufacturer, the pump or motor.

Is the equation is "start up current" = "normal current" * [Normal V / Start up V]?

Also, I wonder is there any method to know how to calculate the current theoritically without perform a test?
p.s. is that include as a specification of a motor?

Thanks in advence.
 
Su Solberg said:
Thanks alot. I wonder which manufacturer, the pump or motor.

Is the equation is "start up current" = "normal current" * [Normal V / Start up V]?

Also, I wonder is there any method to know how to calculate the current theoritically without perform a test?
p.s. is that include as a specification of a motor?

Thanks in advence.

The motor for sure. If it were a NEMA motor the name plate would have a Code Letter designation that could be used to determine the starting current.

The equation I gave you would be if you tested the motor and had some empirical data. In that case it would be:I_{starting} = I_{lr} \cdot \frac{V_{line,rated}}{V_{line,lr}}

If you don't test it yourself or have the data on the name plate (I'm not sure what IEC motor nameplate have on them off hand) then you will need to know the impedance. You can calculate the starting current using the impedance. Just note that their are two components to the current, the transient and the steady-state. The total can be found (again assuming you know the impedance) with this approximation:

i_{lr} = \sqrt{2} \left[ \frac{V_{phase}}{Z_{in}} \right]_{s=1.0} sin(2\pi ft - \theta_z) + A\epsilon^{-(\frac{R}{L})t}

This is obviously in the time domain so the current will be dependent on where the waveform is when the motor starts (i.e. the peak current occurs at a zero voltage crossing).

Also note that the exponential term on the far right is the transient component.

This calc is a lot easier if you have the right name plate data...so buy a NEMA motor if you have the choice (unless IEC nameplates have the same type data)!

Hope this helps.

CS
 
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...