Mass flow rate of cooling water in condenser needed

In summary: You know everything in the equation except dmw/dt, which is what you are trying to solve for. Just plug in the values and solve for dmw/dt. In summary, in order to solve this problem, you need to find the mass flow rate of steam going into the turbine and then use an energy balance equation to find the mass flow rate of cooling water needed in the condenser. You can assume a pressure of 1 atm for the cooling water.
  • #1
staceybiomed
12
0

Homework Statement


Adiabatic Steam turbine produces 4000 kW
Steam is fed at 21 bar/475 deg C
Exhaust is saturated steam (P=0.1bar)
Exhaust is fed into condenser where it is cooled to 30 deg C

Problem asks for flow rate of cooling water supplied to condensener if water enters at 15 deg C and is heated to 25 deg C


Homework Equations


Turbine:
Assume Q = 0
H2 - H1 = -W
m dot steam * (H2 - H1) = - Power (or W dot)
Condenser:
Power (in) = Power(out)
m dot steam in (H steam in) + m dot water in (H water in) = m dot steam out (H steam out) + m dot water out (H water out)
m2U2 - m1U1 - H'(m2 - m1) = 0

The Attempt at a Solution



i fond the mass flow rate of steam going into turbine using m dot * delta H = -Power
- 4000 kW (1 kJ/s / 1 kW) = m dot steam (2584.8 kj/kg - 3411.3 kJ/kg)
mass flow of steam = 4.84 kg/s

then when i try to use the last equation in the above section I get stuck because I can't
figure out U2 or the outlet states. H' = 2779.7 kj/kg, U1 = 2438.0 kJ/kg, m1 = 25000 kg, m2 =?

please help!
 
Physics news on Phys.org
  • #2
Problem asks for flow rate of cooling water supplied to condensener if water enters at 15 deg C and is heated to 25 deg C

In order to solve this problem you have to assume a pressure for the cooling water in the condenser. I recommend 1 atm.

I don't really understand where you are having a problem. You found the states of the steam entering the condenser and you know the states of the cooling water coming in and out of the condenser. It is a simple energy balance;

dQsteam/dt = dQwater/dt

dms/dt * (hi - ho)s = dmw/dt * (ho - hi)w
 
  • #3




To calculate the mass flow rate of cooling water needed in the condenser, you can use the energy balance equation for the condenser:

Power (in) = Power(out)

In this case, the power in is the power produced by the turbine (4000 kW). The power out is the power carried by the steam at the outlet of the condenser. We can assume that the steam is saturated at the outlet, so we can use the steam tables to find the specific enthalpy (H) and specific internal energy (U) at the outlet temperature of 30 deg C (H = 251.86 kJ/kg and U = 251.86 kJ/kg).

We also know the inlet temperature and outlet temperature of the cooling water (15 deg C and 25 deg C, respectively). We can use the specific heat capacity of water (4.18 kJ/kgK) to calculate the specific enthalpy of the cooling water at these temperatures (H = 62.7 kJ/kg and H = 104.3 kJ/kg).

Now, we can plug these values into the energy balance equation and solve for the mass flow rate of cooling water (m dot water):

4000 kW = 4.84 kg/s * (251.86 kJ/kg + 251.86 kJ/kg) + m dot water * (104.3 kJ/kg - 62.7 kJ/kg)

m dot water = 14.63 kg/s

Therefore, the mass flow rate of cooling water needed in the condenser is 14.63 kg/s.
 

What is the mass flow rate of cooling water in a condenser?

The mass flow rate of cooling water in a condenser refers to the amount of water that is flowing through the condenser unit per unit time. It is typically measured in kilograms per second (kg/s) or gallons per minute (gpm).

Why is the mass flow rate of cooling water important in a condenser?

The mass flow rate of cooling water is important in a condenser because it determines the efficiency of the heat transfer process. If the flow rate is too slow, the condenser may not be able to remove enough heat from the system, leading to decreased efficiency and potential damage. On the other hand, if the flow rate is too high, it can result in unnecessary energy consumption and increased operating costs.

How is the mass flow rate of cooling water calculated?

The mass flow rate of cooling water can be calculated using the formula: mass flow rate = volume flow rate x density. The volume flow rate can be measured using a flow meter, while the density of water can be found from reference tables. Alternatively, it can also be calculated using a pressure drop method, where the pressure drop across the condenser is measured and used to determine the flow rate.

What factors can affect the mass flow rate of cooling water in a condenser?

The mass flow rate of cooling water in a condenser can be affected by several factors, including the temperature and pressure of the water, the size and design of the condenser, the type and condition of the cooling system, and the flow rate and type of the cooling medium (e.g. air or water).

How can the mass flow rate of cooling water in a condenser be optimized?

The mass flow rate of cooling water in a condenser can be optimized by properly sizing and designing the cooling system, maintaining the equipment and water quality, and monitoring and adjusting the flow rate as needed. Regular maintenance and performance evaluations can help ensure that the flow rate is at the optimal level for efficient heat transfer and cost-effectiveness.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
2
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
5
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
526
  • Engineering and Comp Sci Homework Help
Replies
13
Views
10K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
630
  • Engineering and Comp Sci Homework Help
Replies
28
Views
4K
Back
Top