Overhead electrical lines and vehicles

In summary,There is a danger of striking low power lines in the more rural areas. The consequences range from nothing to death, and depend on the power line and the vehicle. There is a way to protect an RV from damage in the event of a strike.
  • #1
Ryder S
20
0
Hi all... practical applications here...

I have questions about RV travel, or travel trailer/ 5th wheel and electrical safety.

With taller RV's or trailers, there is a danger of striking low power lines in the more rural areas.

My question is specifically and only about what happens *when* the power line is *not* noticed... and there *will* be a collision between the vehicle and the power line.

First... what are the specifics of what might happen when the strike occurs? I assume occupant electrocution, fire danger, damage to electrical systems on the vehicle. Others? Are any of these unlikely?

I suppose it depends somewhat on what power the line is carrying...

For low rural wires, I tend to want to assume lower voltages. 240? Might there be others?

Then finally... what can be done to an RV ahead of time, to protected *in the event* of a strike, to protect against these kinds of damage? (electrocution, fire, electrical system).

I suppose there is the physical damage as well (a cable that catches a vehicle and doesn't break might do a hell of a lot of physical damage).

Thank you for your thoughts on this...

R
 
Engineering news on Phys.org
  • #2
The consequences range from nothing to death.

This YouTube video shows a truck, not an RV, that a line. Rescuers were unable to get the driver out.



Firemen are forbidden to approach the truck or the downed line because they too might get electrocuted.

[Moderator's note: removed a comment quoting a deleted post]
 
Last edited by a moderator:
  • #3
Ryder S said:
For low rural wires, I tend to want to assume lower voltages. 240? Might there be others?

Yes, and unfortunately the higher voltage is more likely in rural areas. The voltage in the power lines is typically 2 KV or more; it's stepped down to 240/120 by a transformer very near the building(s) being served. In a city, a single transformer may feed multiple buildings so some of the lines on the poles are 120/240 from the transformer to nearby houses. In a rural area, chances are that the line along the road is the line to a transformer, so carrying distribution voltages.
 
  • #4
The particular voltages don't matter, 120 VAC is just as fatal as distribution voltages. The zero current/power trip on the circuit is the significant protection. The vehicle tires are significant.

My father was a Cupertino PG&E distribution engineer and gave me a 25 cubic inch chunk of pavement boiled and blackened by a transmission line which trips failed.
 
  • #5
Doug Huffman said:
The particular voltages don't matter, 120 VAC is just as fatal as distribution voltages. The zero current/power trip on the circuit is the significant protection. The vehicle tires are significant.

My father was a Cupertino PG&E distribution engineer and gave me a 25 cubic inch chunk of pavement boiled and blackened by a transmission line which trips failed.

Hi Doug...

I'm pretty sure that voltages have to matter... that's why distribution lines are low and easily accessible... while HT lines are suspended hundreds of feet into the air.

For any given system (r), the sole determining factor of current is voltage. That which determines the lethal component of discharge through a given system has to matter.For example... and this is slightly off the question being posed... but in a *near miss* of a tractor trailer to a power line... a 1 inch gap will not likely be bridged by a 120vac source... however, a 30,000 volt line... passing 1" above a tall truck let's say... a discharge is far more likely, is it not?

R
 
  • #6
anorlunda said:
The consequences range from nothing to death.

This YouTube video shows a truck, not an RV, that a line. Rescuers were unable to get the driver out.



Firemen are forbidden to approach the truck or the downed line because they too might get electrocuted.


Thanks, anorlunda... I did happen to see such videos (including this one) in my search for information. But of course in physics... the consequences ranging from nothing to death (and fire, etc), are where physics comes in.

You can work with and even "touch" very high voltage systems... and you don't have to die (no consequences). These aren't random. Not acts of god. So understanding/dealing with the actual physics so that the former instead of the latter consequence occurs is what science/engineering is all about.

What I notice about the events with serious consequences... is that they seem to correlate with being "stuck" on a line, or otherwise in continual contact... leading me to wonder if brief/controlled contact is a far safer situation.

For example, helicopters face a similar danger with respect to the physical damage of a cable strike. To combat this, they have devices that, along with the shape of the airframe, cause the cable to ride up or down to a cable cutter as the aircraft moves forward into the obstruction. Causing the cable to part allows the contact with the cable to be brief, and therefore more survivable. For electrical hazard, clearly the specifics are different... any instantaneous discharge through a body is a big issue... in a practical sense, there is no such thing as a "brief" discharge through your body from a high voltage/high current source.
 
  • #7
Doug Huffman said:
I'm pretty sure that voltages have to matter... that's why distribution lines are low and easily accessible... while HT lines are suspended hundreds of feet into the air.

...

For example... and this is slightly off the question being posed... but in a *near miss* of a tractor trailer to a power line... a 1 inch gap will not likely be bridged by a 120vac source... however, a 30,000 volt line... passing 1" above a tall truck let's say... a discharge is far more likely, is it not?

If Doug is trying to say that you shouldn't be complacent just because it's "only" a 240V line, he's right - 240V is lethally dangerous.
And you are right that higher voltages are even more lethally dangerous.

You don't want to drive your RV into any power line carrying any voltage for the same reasons that you don't want to to drive your RV off a cliff.
 
  • #8
Nugatory said:
Yes, and unfortunately the higher voltage is more likely in rural areas. The voltage in the power lines is typically 2 KV or more; it's stepped down to 240/120 by a transformer very near the building(s) being served. In a city, a single transformer may feed multiple buildings so some of the lines on the poles are 120/240 from the transformer to nearby houses. In a rural area, chances are that the line along the road is the line to a transformer, so carrying distribution voltages.

Well, that's a useful thing to know... (higher voltages in rural areas).

But in this case, I have to wonder about only one kind of line... and that would be the low lines that directly cross a roadway.

There has to be some confusion about what is exactly crossing a road. A wire is could be phone or cable service, I suppose.

But it's best to assume that it's going to be power. Perhaps state or county regs have a strong influence on this. These visually appear to be the smallest lines in the system. Thicker lines run along a road, and tend to cross high at intersections... but the thinner, low lines that cross at unpredictable locations, bringing power in lot by lot or house by house, are quite probably stepped down, yes? I guess these are questions for the power company...

But for purposes here, let us assume somewhat higher voltages.

For an RV striking a 2-3KV line, and a range of damage possible (fire, electrocution, etc)... the issue of survivability comes down to physics.

I notice a cursory correlation between a strike that is sustained (the vehicle hangs up on the line), versus a strike that happens briefly, then is broken.

This seems to point to preventing a snag, first and foremost... this would seem to accomplish three things: little chance of downing the wire, little chance of downing a pole, a higher likelihood that the vehicle will be stopped after the incident, and no longer be subjected to the voltage (making it safe to exit the vehicle, or be tended to by EMS).

But this brings into question some ancillary issues:

What happens to the engine during the strike?
What happens to the breaking system during the strike?
What happens to the driver during the strike?

If current passes into the metal skin of the vehicle... then through the tires to ground... then is there a high likelihood that the driver will not be especially affected during the initial strike? If so, then this would allow the driver to control the vehicle... (like steering and application of brakes).

(I notice that drivers tend to die when they hop OUT of the vehicle, while still holding onto it: Path = vehicle -> person -> ground).

If we have vehicular control... we now have to ask what is the condition of the vehicle? Is it likely that the engine is still running for several seconds? Is it likely that the brake system is still working?

In the case of electrical brakes (which many/most trailers have), will these probably be disabled? Or the converse... might they be fully actuated during the discharge ? (after all, they are electrically actuated!) If the latter, this might be a problem... rapidly stopping a trailer while in contact with the line, might cause the vehicle to essentially park itself while in contact...

R
 
  • #9
Nugatory said:
If Doug is trying to say that you shouldn't be complacent just because it's "only" a 240V line, he's right - 240V is lethally dangerous.
And you are right that higher voltages are even more lethally dangerous.

You don't want to drive your RV into any power line carrying any voltage for the same reasons that you don't want to to drive your RV off a cliff.
Interestingly, I have driven a VW bug off a cliff... with a drop of only three feet. Apart from embarrassment... no real damage. I think the old bugs were tougher than the new ones.

But this does bring up an interesting distinction... and that is the case of *not* driving into the line, but merely passing a fraction of an inch beneath it. I think that the potential (no pun intended) for an incident in these "near miss" situations might be important to understand...

Do you think that such a thing might also be a dangerous situation? Or do you think that only in the cases of a strike?
 
Last edited:
  • #10
The vehicle is insulated by the tires. The cab/body is a Faraday cage of some effect.
 
  • #11
Ryder S said:
If current passes into the metal skin of the vehicle... then through the tires to ground... then is there a high likelihood that the driver will not be especially affected during the initial strike? If so, then this would allow the driver to control the vehicle... (like steering and application of brakes).
(I notice that drivers tend to die when they hop OUT of the vehicle, while still holding onto it: Path = vehicle -> person -> ground).
That's right. Step and touch voltage outside the vehicle is higher, higher is the power line voltage. Just one more reason HV line is more dangerous than LV line.

Ryder S said:
But this does bring up an interesting distinction... and that is the case of *not* driving into the line, but merely passing a fraction of an inch beneath it. I think that the potential (no pun intended) for an incident in these "near miss" situations might be important to understand...

Do you think that such a thing might also be a dangerous situation? Or do you think that only in the cases of a strike?

Ask yourself why HV power lines pylons have a long insulators (higher the voltage, longer the insulator required).
Doug Huffman said:
The vehicle is insulated by the tires.
Are you sure?*

*rethorical question
 
  • Like
Likes Nugatory
  • #12
Typical distribution is in the 4 to 32 kv range,
A clean dry tire ought to withstand 16KV.
We had a sailboat on a trailer being pulled out of the water , the guy got his mast into a medium voltage distribution line and the wet salty trailer tires burst into flame. Luckily the line relayed out but his fiberglass hull caught fire too..

Woe to the guy who steps out placing one foot on the ground... his left leg just completed the circuit, same as would a wet tire.

If you get into that situation, be aware the car body will make a Faraday cage around you. Sit still until you figure out what to do.
Foremost, don't complete a path from vehicle to Earth with your own body parts.
Myself I'd try to extricate the vehicle, maybe backing out from under the wire. If exit were a must because of fire i'd leap as far as i could and hop away on one foot.

old jim
 
  • #13
jim hardy said:
A clean dry tire ought to withstand 16KV.
We had a sailboat on a trailer being pulled out of the water , the guy got his mast into a medium voltage distribution line and the wet salty trailer tires burst into flame. Luckily the line relayed out but his fiberglass hull caught fire too..
In many cases contact of road vehicles with 10kV+ power lines results in arcing. This means tyres are not clean and dry enough.

Regards
 
  • #14
Ryder S said:
You can work with and even "touch" very high voltage systems... and you don't have to die (no consequences). These aren't random. Not acts of god. So understanding/dealing with the actual physics so that the former instead of the latter consequence occurs is what science/engineering is all about.

I agree when you know who your audience is. But this is a public forum. Not only that, but it is archived and searchable meaning that it persists indefinitely with the whole world as a potential audience.

Common sense should make us fear that non science/engineering people might read portions of this thread in the future, and be led to behavior that causes serious harm.

Just as doctors should not joke on a public forum about fun ways to make psychedelic drugs in the kitchen, neither should we shop talk on public forums about subjects that can be hazardous to laymen readers in the future.

The self-censoring rule I strive to follow before posting anything online is, "Would I be upset if what I write ends up on the front page of tomorrow's newspaper?" If the answer is yes, then do not press SEND.

I'm distressed that this whole thread is part of the record. I hope that the mentor will delete it.
 
  • Like
Likes davenn and Nugatory
  • #15
Pending moderation
 
  • #16
anorlunda said:
I agree when you know who your audience is. But this is a public forum. Not only that, but it is archived and searchable meaning that it persists indefinitely with the whole world as a potential audience.

Common sense should make us fear that non science/engineering people might read portions of this thread in the future, and be led to behavior that causes serious harm.

Just as doctors should not joke on a public forum about fun ways to make psychedelic drugs in the kitchen, neither should we shop talk on public forums about subjects that can be hazardous to laymen readers in the future.

The self-censoring rule I strive to follow before posting anything online is, "Would I be upset if what I write ends up on the front page of tomorrow's newspaper?" If the answer is yes, then do not press SEND.
Anorlunda has explained the reasoning behind the PF policy on dangerous activities well. There's also this recent thread.

I'm distressed that this whole thread is part of the record. I hope that the mentor will delete it.
I thought about it, and I've already taken down one post that was egregiously wrong and irresponsible. I've closed the thread, but I'm going to leave it up because I think on balance the discussion is now making the right points. But lest there be any misunderstanding about what we're saying here:

Line voltage can kill you or people around you. Some ways of mishandling it are more likely to kill than others, but that does not make any mishandling acceptable under any circumstances.
What I notice about the events with serious consequences... is that they seem to correlate with being "stuck" on a line, or otherwise in continual contact... leading me to wonder if brief/controlled contact is a far safer situation.
Playing russian roulette with one chamber loaded is a far safer situation than with two chambers loaded. But the Darwin award was earned when you decided to play at all, not when you started thinking about how many chambers were loaded.
 
Last edited:
  • Like
Likes anorlunda and davenn

1. What are overhead electrical lines?

Overhead electrical lines are wires that are suspended above ground level to carry electricity from one location to another. They are typically made of aluminum or copper and are insulated to prevent the risk of electric shock.

2. How are overhead electrical lines different from underground electrical lines?

Overhead electrical lines are suspended above ground, while underground electrical lines are buried underground. Overhead lines are more visible and easier to access for maintenance, while underground lines are protected from weather elements and have less risk of damage from external factors.

3. What types of vehicles should be cautious of overhead electrical lines?

Any vehicle that has the potential to come in contact with overhead electrical lines should exercise caution. This includes tall trucks, cranes, trailers, and any other vehicle that has an elevated structure. It is important to always be aware of the height of your vehicle and the location of overhead lines.

4. What are the potential dangers of coming into contact with overhead electrical lines?

Contact with overhead electrical lines can result in electric shock, which can be fatal. It can also cause power outages and damage to the electrical equipment. In addition, vehicles can become entangled in the wires, causing accidents and injuries.

5. How can I stay safe when driving near overhead electrical lines?

To stay safe when driving near overhead electrical lines, always be aware of your vehicle's height and the location of overhead lines. If you are operating a tall vehicle, make sure to plan your route accordingly and avoid areas with low-hanging lines. If your vehicle does come in contact with overhead lines, stay inside and call for help immediately.

Similar threads

  • Electrical Engineering
4
Replies
117
Views
8K
Replies
13
Views
4K
  • Electrical Engineering
Replies
2
Views
1K
Replies
1
Views
903
  • Electrical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
4
Views
2K
  • Electrical Engineering
Replies
4
Views
5K
  • Electrical Engineering
Replies
2
Views
6K
  • Biology and Medical
2
Replies
35
Views
3K
  • Sci-Fi Writing and World Building
Replies
6
Views
676
Back
Top