Power factor of a retrofitted LED unit in a fluorescent fitting

In summary: That means I'll need a Disassembly Machine and a good solder refiner before I can really start....In summary, it is unclear whether the LED tube light is consuming the claimed 24W or 80W. When the ballast is removed, it will be possible to calculate the real power consumption.
  • #1
Guineafowl
762
366
TL;DR Summary
How does leaving the ballast and capacitor in circuit affect power factor of LED lights?
A poster on another forum has fitted a large number of 230V 50Hz 24W nominal LED tubes, apparently designed to be plugged straight into the old fluorescent fittings.

He has found, by clamp meter measurement, that the new LED lights appear to be consuming 80W, not the claimed 24W.

A number of us pointed out the difference between apparent power as measured by the clamp meter, and real power as charged by the power company, and the possible effects of leaving the ballast and capacitor in circuit.

An engineer from the supplier has visited, and merely measured the consumption by clamp meter again. I would be very interested in the input from members on here.

May I link the thread here?: https://www.mig-welding.co.uk/forum...florescent-led-replacement-efficiency.128634/

edit: I should add that this class of LED tube must have a minimum power factor of 0.5. In my scribblings, I have (for now) modelled them as 24W resistive loads. It might be more meaningful to assume a 0.5 (leading?) PF and calculate the complex impedance of the tubes as such.
 
Last edited:
Engineering news on Phys.org
  • #2
The inductors were there to keep current flowing through the tubes for a greater angle, not just at the peak of the voltage cycle.
The capacitor was there to neutralise the inductance, to partly restore the PF.

The clamp current being measured now is the reactive capacitor current. That will be of the same magnitude as the original tube current through the inductor. That explains why the clamp current shows the VA of the original tubes. Depending on the type of metering used and tariff, they may actually be paying for the reactive current.

Removing both the inductor and the capacitor will reduce the reactive current, and the circulating energy. It will minimise the bill for lighting, by an unknown amount, depending on the metering.
 
  • Like
Likes Windadct and Guineafowl
  • #3
Thanks. The OP is, I believe, on a domestic three phase tariff, meaning only real power is charged. This may change in the future.

The height of the ceiling means that removing the inductors/caps would be a significant upheaval. Given that the ‘extra’ current is not being charged for, it looks like the job would not be worth it.

May I quote, or at least link to your post?
 
  • #4
Guineafowl said:
May I quote, or at least link to your post?
Feel free.
 
  • #5
I have a magnifier/desk lamp at my work station with an 8 inch Circ-line LED lamp in it. The LED lamp is a plug-in replacement for the original fluorescent tube, the ballast is still in the circuit.

I plugged it in to a KIL A WATT meter and here are the numbers with the LED:
V = 118.5
A = 0.42
W = 32.1
VA= 49.8
PF= 0.64

If I did the math right, that shows a phase angle of 50°.

Cheers,
Tom
 
  • #6
Tom.G said:
I have a magnifier/desk lamp at my work station with an 8 inch Circ-line LED lamp in it. The LED lamp is a plug-in replacement for the original fluorescent tube, the ballast is still in the circuit.

I plugged it in to a KIL A WATT meter and here are the numbers with the LED:
V = 118.5
A = 0.42
W = 32.1
VA= 49.8
PF= 0.64

If I did the math right, that shows a phase angle of 50°.

Cheers,
Tom
Would that be an electronic ballast?
 
  • #7
Guineafowl said:
Would that be an electronic ballast?
I haven't taken it apart, but:
It used a conventional starter for the original lamp.
The housing size where the ballast seems to be is 3 x 3.5 x 2.5 inches in size.
It is about 12 to 15 years old.

I vote for a magnetic (transformer) ballast.
 
  • #8
Tom.G said:
I haven't taken it apart, but:
It used a conventional starter for the original lamp.
The housing size where the ballast seems to be is 3 x 3.5 x 2.5 inches in size.
It is about 12 to 15 years old.

I vote for a magnetic (transformer) ballast.
…and when can we expect the stripdown and analysis? :wink:
 
  • #9
'Fraid not, the steel case, presumably with the ballast, is crimped together.
 

1. What is the power factor of a retrofitted LED unit in a fluorescent fitting?

The power factor of a retrofitted LED unit in a fluorescent fitting refers to the ratio of the actual power used by the LED unit to the apparent power drawn from the power source. It is a measure of how efficiently the LED unit is using the power supplied to it.

2. How does the power factor of a retrofitted LED unit compare to that of a traditional fluorescent bulb?

The power factor of a retrofitted LED unit is typically higher than that of a traditional fluorescent bulb. This is because LED technology is more efficient and requires less power to produce the same amount of light.

3. Why is the power factor of a retrofitted LED unit important?

The power factor of a retrofitted LED unit is important because it affects the overall efficiency of the lighting system. A higher power factor means less energy is wasted, resulting in lower electricity bills and reduced strain on the power grid.

4. Can the power factor of a retrofitted LED unit be improved?

Yes, the power factor of a retrofitted LED unit can be improved by using a power factor correction device. This device helps to balance the reactive power and improve the overall efficiency of the LED unit.

5. Are there any potential drawbacks to a high power factor in a retrofitted LED unit?

One potential drawback of a high power factor in a retrofitted LED unit is the increased cost of the unit. Power factor correction devices can be expensive, and the cost may outweigh the potential energy savings. Additionally, a high power factor may also cause interference with other electronic devices in the area.

Similar threads

  • Electrical Engineering
Replies
2
Views
1K
Replies
4
Views
2K
Replies
1
Views
2K
  • Electrical Engineering
Replies
3
Views
3K
Replies
5
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
2K
  • Introductory Physics Homework Help
Replies
4
Views
1K
  • Special and General Relativity
3
Replies
75
Views
3K
  • Biology and Medical
Replies
4
Views
4K
  • Other Physics Topics
Replies
4
Views
14K
Back
Top