What secondary circuit breaker should I use for my fridge compressor?

  • #1
stryped
51
3
TL;DR Summary
I am replacing a broken inverter compressor with a regular compressor that has the standard electromechanical relay. I plan on controlling the compressor/electro relay with an ac to ac Ssr. The Ssr will be triggered by the condenser fan that is a 110v circuit.
The compressor looks like it runs on 2 amps, but has 15 locked rotor amps. I would like to install a self resetting circuit breaker between the compressor and Ssr. What amperage breaker would I need? 15 seems too high and 2 too low.
I am replacing a broken inverter compressor with a regular compressor that has the standard electromechanical relay. I plan on controlling the compressor/electro relay with an ac to ac Ssr. The Ssr will be triggered by the condenser fan that is a 110v circuit. The compressor looks like it runs on 2 amps, but has 15 locked rotor amps. I would like to install a self resetting circuit breaker between the compressor and Ssr. What amperage breaker would I need? 15 seems too high and 2 too low.

Reference: https://www.physicsforums.com/forums/electrical-engineering.102/post-thread
 
Engineering news on Phys.org
  • #2
Please, see picture of nameplate of an AC condenser unit, which fan's label shows MCA of 1.0 A
Note how much over the recommended maximum protection (30 A) is respect to the total MCA of the condenser (17.8 A).

I would see what breaker sizes are available to install between the solid state relay and the start circuit of the compressor (assuming the run circuit is left out of the additional protection).
Most compressors are damaged by overcurrent at the starting phase.

DE338103-B9AB-47C9-86C7-21379A4FA236.jpeg
 
  • #3
How do I determine the proper in line circuit breaker? This is a refrigerator compressor and it does not say much on it, other than it is 15 locked rotor ampsHere are some specs:
1/3- hp
Displacement 7.7cc
From 100W to 671W Cooling (341 to 2289BTUs) ASHRAE : 220w - 751btu
110-120VAC
50-60Hz
R134A
Low Back Pressure
PTC Starting Relay
Motor Type CSIR
Includes electricals, grommets and sleeves.

Cooling capacity ASHRAE
-35C (-31F) - 100w - 341btu
-30C(-22F) - 130w - 444btu
-25C(-13F) - 169w - 577btu
-23.3C(-10F) - 220w - 751btu - input power 165W - current 2.40 Amps - COP 1.35 - EER 4.55
-20C(-4F) - 275w - 938btu
-15C(5F) - 344w - 1174btu
-10C(10F) - 430w - 1467btu
-5C(23F) - 537w - 1832btu
0C(32F) - 671w - 2289btu
Certification : UL Underwriters Laboratories Recognized
Nationally Recognized Testing Laboratories (NRTL)
Reply
 
  • #4
The 1/3 HP compressor will draw around 2 to 3A running.
With the locked rotor current of 17.8A (as @Lnewqban mentioned) I suggest a Thermal, Slow Trip (time delay), Auto Reset breaker rated around 8 to 12A. (I'm leaning towards the 12A range.)

That will yield a delay long enough for the compressor to reach operating speed but low enough to trip if the compressor gets fluid locked or the motor develops an internal short circuit.

Picking an exact breaker is not possible without details of the starting current and the delay curves of available breakers. The above values, however, should be well within the working range.

By the way, be aware that once the refigerant line is opened, the dessicator will need replacement, and the system evacuated with a vacuum pump before charging with refrigerant - otherwise the ambient moisture that enters the system will freeze in the evaporator (and also dilutes the oil in the compressor, sometimes causing it to foam).

Cheers,
Tom

p.s. Let us know what works -- or doesn't!
 
Last edited:
  • Like
Likes DaveE and Lnewqban
  • #7
That looks like a decent option.

The actual current rating needed depends on the compressor starting (locked rotor) current. The breaker ratings so far are based on 18Amps peak load.

Let us know if your chosen compressor is significantly different.

After looking at the data sheet, I would suggest a 10Amp rating if it is used in a conditioned (living) area. If in an area that gets cold (close to freezing) then a 8Amp or maybe 6Amp is more appropriate.

As @DaveE noted, if it is in an un-heated or un-cooled garage or utility room, then the temperature extremes need to be accounted for because the time to trip depends on the ambient temperature.

Cheers,
Tom
 
Last edited:
  • #9
I just re-read this thread and realized your compressor is rated at 10A Locked Rotor. Based on this I change my Breaker suggestion to 5Amp.

Now to the MOV:
:cry: Sorry, neither DigiKey nor LittleFuse search pages will talk to my old browser.

However based on the information on the page you linked to, that MOV should be quite sufficient, Good Choice!

Cheers,
Tom
 

What is a secondary circuit breaker?

A secondary circuit breaker is an additional safety device used in electrical circuits to protect appliances from overcurrents and short circuits. It acts independently from the main circuit breaker to provide a specific line of defense for individual appliances or sections of your home's electrical system.

How do I choose the right size of secondary circuit breaker for my fridge compressor?

To choose the right size of secondary circuit breaker for your fridge compressor, you need to check the compressor's specifications for its amperage draw, usually found in the appliance's manual or on a label attached to the unit. The circuit breaker should match or slightly exceed this amperage to ensure safety and efficiency without tripping unnecessarily.

Can I install a secondary circuit breaker myself?

While it is possible to install a secondary circuit breaker yourself if you have some electrical knowledge, it is generally recommended to hire a licensed electrician. This ensures that the installation complies with local electrical codes and standards, and is safely integrated into your home’s electrical system.

What are the consequences of using an incorrectly rated circuit breaker for my fridge compressor?

Using an incorrectly rated circuit breaker can lead to several problems. If the breaker is rated too low, it will trip frequently, causing inconvenience and potential damage to the fridge compressor due to power interruptions. If it's rated too high, it may not trip when needed, risking damage to the compressor from overcurrents or even causing electrical fires.

Are there specific brands or types of secondary circuit breakers recommended for fridge compressors?

There are no specific brands that are universally recommended for fridge compressors, but it is crucial to choose a secondary circuit breaker that is of high quality and from a reputable manufacturer. Look for breakers that meet the necessary local and international standards. It is also advisable to consult with a professional about the best type and brand for your specific fridge and electrical setup.

Similar threads

Replies
5
Views
2K
Replies
11
Views
4K
  • Electrical Engineering
Replies
3
Views
1K
  • Electrical Engineering
Replies
7
Views
2K
  • Electrical Engineering
Replies
17
Views
11K
Replies
6
Views
1K
Back
Top