Recent content by Harsh864

  1. H

    Timer based switch for a power capacitor

    Sure, I will be having a electrician doing the work. Thanks a lot for helping me out @Asymptotic
  2. H

    Timer based switch for a power capacitor

    Yes neutral line available and will provide MCB. Capacitor and it's contactor will be 415V/50hz I hope that's not a issue. Edit - sorry, I got your point. The contactor coil should be 230 vac, along with fuses/MCB. Am I right.? Is there any contactor available for such a low capacitor - 3kvar.?
  3. H

    Timer based switch for a power capacitor

    Can I go without adding any transformer, sir.? Things I need - 1. Capacitor duty contactor 2. Digital Timer 3. 3 kvar capacitor Digital timer will be connected to contactor and will control it. It will turn on/off the contactor and Therefore the capacitor. Digital timer will be connected to...
  4. H

    Timer based switch for a power capacitor

    Sir, this may sound good but how that tiny transformer will handle incoming current if there's is some load required at any time.? I am more inclined towards the intermatic mechanical switch but the voltage should 415v-440v
  5. H

    Timer based switch for a power capacitor

    I considered this things, but this all are rated at 240vac, whereas our line is 415vac, 50hz, 3 phase. The transformer is 500kva rating.
  6. H

    Timer based switch for a power capacitor

    No it doesn't have logic input
  7. H

    Timer based switch for a power capacitor

    To cover transformer loss at no load and maintain pf, we are needing 6kvar at day time and 9 kvar at evening. Is there any time based switch available, such that it can switch ON 3 kvar at evening, say 8:00pm and turn off automatically at 8:00AM morning
  8. H

    How to correct for a Leading Power Factor (kVArh)

    Yes, this change is brought last month only, we became aware after checking the bill. Yes, I will be consulting for moving the capacitor to larger motor feeds. This is what I am looking for. how to do it. Will the dynamic power correction system help me. As this system is for switching load...
  9. H

    How to correct for a Leading Power Factor (kVArh)

    We are in Industrial area. And our connetion is high tension line of 11kv. We pay electricity charges based on kWh only. Incentive is given on pf 0.95 and above(half percent for each 0.01) Penalty is levied on pf 0.90 and below (half percent for each 0.01) (on a percentage basis of electricity...
  10. H

    How to correct for a Leading Power Factor (kVArh)

    Hi guys, We have a industrial connection of 225 kW. Our industry consists mostly of Induction motors and runs in night shift mostly. So we use capacitor banks for lower factor correction. And so far we have maintained 0.995-0.999 pf (sometimes even 1) over the years. Previously, the power...