The discussion revolves around the need for a timer-based switch to control a power capacitor for maintaining power factor and covering transformer losses at different times of the day. Participants explore various options for implementing this system, including the specifications and requirements for components such as contactors and timers.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants express the need for a time-based switch to activate a 3 kvar capacitor in the evening and deactivate it in the morning.
  • One participant suggests checking the features of the current circuit breaker for remote logic inputs, but another confirms it lacks such capabilities.
  • There are discussions about using a contactor controlled by a timer, with considerations for voltage ratings and specifications for a 600V bank.
  • Participants mention the need for a transformer to step down from 415V to a suitable control voltage, while others question how a small transformer would handle incoming current under load.
  • Some participants propose using an Intermatic mechanical switch rated for 415V-440V, while others discuss the sizing of control voltage transformers based on contactor specifications.
  • There is a suggestion to use a digital timer connected to a contactor to control the capacitor, with links to available products provided by one participant.
  • Concerns are raised about ensuring that control components are rated appropriately for the system's voltage and frequency, with mentions of fusing the control circuit for safety.
  • Participants inquire about the availability of contactors suitable for a 3 kvar capacitor and are advised to consult manufacturer catalogs.

Areas of Agreement / Disagreement

Participants express a variety of views on the best approach to implement the timer-based switch, with no consensus on a single solution. There are differing opinions on the necessity of a transformer and the specifications for components, indicating ongoing debate and exploration of options.

Contextual Notes

Participants mention specific voltage ratings and the need for components to be compatible with a 415V, 50Hz, 3-phase system. There are unresolved questions regarding the sizing of transformers and contactors, as well as the appropriateness of various timer products.

Who May Find This Useful

Individuals interested in electrical engineering, particularly those working with power factor correction, capacitor banks, and timer-controlled systems, may find this discussion relevant.

Harsh864
Messages
10
Reaction score
1
TL;DR
Switch On in evening and off at night
To cover transformer loss at no load and maintain pf, we are needing 6kvar at day time and 9 kvar at evening.

Is there any time based switch available, such that it can switch ON 3 kvar at evening, say 8:00pm and turn off automatically at 8:00AM morning
 
Engineering news on Phys.org
Have you studied the features of the circuit breaker you are currently using? It may have capabilities for remote logic inputs.
 
No it doesn't have logic input
 
Harsh864 said:
Summary: Switch On in evening and off at night

To cover transformer loss at no load and maintain pf, we are needing 6kvar at day time and 9 kvar at evening.

Is there any time based switch available, such that it can switch ON 3 kvar at evening, say 8:00pm and turn off automatically at 8:00AM morning
Sure, plenty of ways to do this, but it is difficult to say without a better understanding of the specifics. For example, if this is a 600V bank then size a contactor to suit (check the contactor manufacture's recommendations) and control the contactor with a 24 hour timer along the lines of the Intermatic pictured below, or program an intelligent relay such as a Siemens Logo! to do the job.
244848
 
  • Like
  • Informative
Likes   Reactions: dlgoff and anorlunda
Asymptotic said:
Sure, plenty of ways to do this, but it is difficult to say without a better understanding of the specifics. For example, if this is a 600V bank then size a contactor to suit (check the contactor manufacture's recommendations) and control the contactor with a 24 hour timer along the lines of the Intermatic pictured below, or program an intelligent relay such as a Siemens Logo! to do the job.
View attachment 244848
I considered this things, but this all are rated at 240vac, whereas our line is 415vac, 50hz, 3 phase.
The transformer is 500kva rating.
 
Harsh864 said:
I considered this things, but this all are rated at 240vac, whereas our line is 415vac, 50hz, 3 phase.
The transformer is 500kva rating.
Add a transformer to step down from 415V to whatever control voltage you desire.
 
Asymptotic said:
Add a transformer to step down from 415V to whatever control voltage you desire.
Sir, this may sound good but how that tiny transformer will handle incoming current if there's is some load required at any time.?

I am more inclined towards the intermatic mechanical switch but the voltage should 415v-440v
 
Harsh864 said:
I considered this things, but this all are rated at 240vac, whereas our line is 415vac, 50hz, 3 phase.
415 VAC, 3 Phase is actually three lines, each 240 VAC relative to the neutral, separated by 120° phase.
 
  • Like
Likes   Reactions: Ganesh1199, Asymptotic, anorlunda and 1 other person
Control voltage transformer need only be sized large enough to handle contactor coil inrush current (plus whatever else may be connected to it - indicating pilot lamps, timer, and whatnot).

Work back from the contactor specifications, for example, if the contactor coil is rated 220V, 70 VA inrush and the timer consumes 5VA, a transformer rated 150 VA will easily handle the load.

Have you looked into any Intermatic timer specs? I don't know what they may offer in 415V/50 Hz, but their 60 Hz timer product line includes 480V timer motor supply with 20 amp contacts rated for up to 480V AC operation, and will easily handle a contactor coil. Be sure if you use a motor-based timer like this that the motor is rated 50 Hz, or the timing will be thrown off.
 
  • #10
Can I go without adding any transformer, sir.?

Things I need -
1. Capacitor duty contactor
2. Digital Timer
3. 3 kvar capacitor

Digital timer will be connected to contactor and will control it. It will turn on/off the contactor and Therefore the capacitor.
Digital timer will be connected to 1live wire and neutral phase.
Am I Right..??

We have these products available here -

https://www.havells.com/en/consumer.../digital-weekly-programmable-time-switch.html
https://www.bestomart.com/products/l-t-crono-digital-time-switch-1000010836?variant=9605099520057
https://www.bestomart.com/products/l-t-gic-time-switch-j648b1analog-version-1000009126?variant=33729359630&currency=INR&gclid=EAIaIQobChMI5aHc4b_h4gIVAmoqCh1Z7Q0EEAQYByABEgIV1fD_BwE
 
  • #11
Harsh864 said:
Can I go without adding any transformer, sir.?
Sure, if you have a neutral line available, and the control components are rated 240V/50Hz.
You'll want to fuse the control circuit to prevent damage in case a short circuit failure of the timer or contactor coil occur.

Before you order parts and build the KVAR capacitor bank and controls have a qualified electrician look over your plans.
 
  • #12
Asymptotic said:
Sure, if you have a neutral line available, and the control components are rated 240V/50Hz.
You'll want to fuse the control circuit to prevent damage in case a short circuit failure of the timer

Yes neutral line available and will provide MCB.
Capacitor and it's contactor will be 415V/50hz
I hope that's not a issue.

Edit - sorry, I got your point. The contactor coil should be 230 vac, along with fuses/MCB.

Am I right.?

Is there any contactor available for such a low capacitor - 3kvar.?
 
Last edited:
  • #13
Harsh864 said:
Is there any contactor available for such a low capacitor - 3kvar.?

Search "capacitor contactor selection", pick a manufacturer (ABB, Schneider, Siemens, etc) and study their catalogs.

Harsh864 said:
Am I right.?
Best advice I can give you is have a qualified electrician look over your plans, and do the wiring. I think you have the general idea, but the nature of your questions suggest limited background in electrical applications.
 
  • #14
Sure, I will be having a electrician doing the work.
Thanks a lot for helping me out @Asymptotic
 
  • Like
Likes   Reactions: anorlunda

Similar threads

  • · Replies 31 ·
2
Replies
31
Views
5K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 17 ·
Replies
17
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 16 ·
Replies
16
Views
4K
Replies
11
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 16 ·
Replies
16
Views
2K
  • · Replies 6 ·
Replies
6
Views
11K