11kV vs 22kV electric distribution voltage

Click For Summary
SUMMARY

The discussion centers on the selection of 11kV versus 22kV underground electric distribution systems for a compact urban project with a maximum demand of 250 MW. Key advantages of 22kV include reduced space requirements for cable laying, lower energy losses in medium voltage networks, and minimal differences in operation and maintenance compared to 11kV. The drawbacks of using 33kV include high costs, increased space requirements, and complexity in handling and maintenance. Accurate pricing details for cables and RMUs are essential for making an informed decision.

PREREQUISITES
  • Understanding of medium voltage distribution systems
  • Familiarity with cable specifications and costs
  • Knowledge of electrical fault levels and their implications
  • Experience with urban electrical distribution planning
NEXT STEPS
  • Research the cost differences between 11kV, 22kV, and 33kV cables and RMUs
  • Learn about the impact of fault levels on motor starting and system stability
  • Investigate case studies of urban projects utilizing 22kV distribution systems
  • Explore the design considerations for compact urban electrical distribution networks
USEFUL FOR

Electrical engineers, urban planners, and project managers involved in designing and implementing electric distribution systems in compact urban areas.

asela115
Messages
4
Reaction score
0
Hi,

what are the possible reasons for selecting 11kV underground distribution system vs 22kV underground distribution system for urban area.
I know about 22kV can carry twice the load compared to 22kV.

How about impacts of pricing, fault level, stepdown from 132 kv to 22/kv etc.

Thanks
 
Engineering news on Phys.org
That is far too broad a question to ask or answer on an online forum. Planning engineers use many tools to evaluate all the pros and cons of design choices. Your question could apply to any and every power distribution and transmission project.

If you don't have access to professional engineers in this field, I suggest that you search for textbooks.
 
  • Like
Likes   Reactions: davenn
anorlunda said:
That is far too broad a question to ask or answer on an online forum. Planning engineers use many tools to evaluate all the pros and cons of design choices. Your question could apply to any and every power distribution and transmission project.

If you don't have access to professional engineers in this field, I suggest that you search for textbooks.
agreed
and as a generalisation ... the obvious reason would be that it's much easier to insulate 11kV conductors than 22kV ones where they are pretty much in contact with each other ... lower voltage, lower chance of dielectric failure

Dave
 
thank you all for your valuable feedback (I should have shared following details beforehand)
this is a special project with following details. it has residential, hotels, government offices, cultural & educational centers etc. compacted in small area (a luxury compacted city build in small area).
  • land area - 275 hectare
  • population -300,000
  • total expected maximum demand - 250 WM
  • total demand- 500 MW
we are to justify a suitable distribution voltage for this special project. based on the feedback and details observed so far, i have summerised below details,
advantage of 22kv
1)Reduce by 50%
  • space requirement for laying cables
  • No of feeder bays
2)For double the capacity
  • Increase only by around 10% to 15% cable cost
  • Small price difference between 11kV and 22kV panel -design the panels for 22kV and fix 12kV equipment
3)Low energy loss in MV network
4)Low energy loss in HV equipment- 220kV can be directly stepped down to 22kV
5)No much difference in operation & maintenance of 11kV & 22kV cables & equipment
why 33kv is not best for this kind of project
1)33kV is a sub transmission voltage not a distribution voltage.
2)Cables and equipment very expensive.
3)RMUs are very expensive and very rare.
4)Cable systems are difficult to handle, operate & maintain.
5)Need more space for switch gear and cables
6)High fault level.
7)Cable capacitance would be high and need to have reactors at GSS

are there any technical matters we should consider beyond this. Especially I'm missing with accurate pricing details of cables and RMU/Switchgears (pricing comparison of 11kV, 22kV and 33kV).
Further in some posts I saw that having higher fault levels is good when considering starting of large motors etc. where neighboring consumers won't feel much (So, is 22kV better than 11kV)
Are there any examples where this kind of projects were carried out using 22kV (instead of 11kV)
 
OK well none of that was mentioned earlier

for all that you shouldn't be asking these sort of Q's on a forum
Instead hire qualified electrical engineers to assess the required specifications

Dave
 
@asela115 -- we are contacting your employer to let them know that you are trying to design this project on your own using web forums, instead of paying a professional to do it for you. Good luck, this thread is closed.
 
  • Like
Likes   Reactions: CalcNerd and davenn

Similar threads

  • · Replies 6 ·
Replies
6
Views
6K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 13 ·
Replies
13
Views
3K
  • Poll Poll
  • · Replies 6 ·
Replies
6
Views
9K
  • · Replies 4 ·
Replies
4
Views
12K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 35 ·
2
Replies
35
Views
11K