About Governor speed droop settings

  • Thread starter Thread starter b.shahvir
  • Start date Start date
  • Tags Tags
    Speed
Click For Summary
SUMMARY

The discussion centers on the implications of governor speed droop settings in generator systems, specifically the advantages and disadvantages of low and high droop settings. A droop setting of around 4% is generally recommended, as lower settings increase sensitivity to frequency changes, potentially leading to instability, while higher settings risk overspeed conditions if a breaker trips. The relationship between speed set points and bus frequency is critical, with a 4% droop equating to a 2 Hz variation affecting load significantly.

PREREQUISITES
  • Understanding of governor control systems
  • Knowledge of frequency response in electrical systems
  • Familiarity with load dynamics in generator operations
  • Basic principles of power system stability
NEXT STEPS
  • Research "Governor control theory and applications"
  • Study "Impact of droop settings on generator stability"
  • Explore "Frequency response analysis in power systems"
  • Learn about "Load sharing in parallel generator systems"
USEFUL FOR

Electrical engineers, power system operators, and anyone involved in the design or operation of generator control systems will benefit from this discussion.

b.shahvir
Messages
284
Reaction score
24
Hi all, :smile:

Can someone pls. elaborate on the following;

1) Advantage/disadvantage of very low governor speed droop setting and why...

2) Advantage/disadvantage of very high governor speed droop setting and why...

The ideal droop setting is normally recommended to be around 4%... Pls. comment.

Thanks & Kind regards,
Shahvir
 
Engineering news on Phys.org
Someone pls. reply! :frown:
 
If you have a very low droop setting the load on the machine will be very sensitive to small frequency changes on the bus.
If you have a very high droop setting the speed set point can be such that if your breaker trips you drive into overspeed.
 
Jobrag said:
If you have a very low droop setting the load on the machine will be very sensitive to small frequency changes on the bus.

Thanks, but could you pls. elaborate a bit more on the above; i.e. load being sensitive to small frequency changes on the bus?

Regards,
Shahvir
 
When running in droop the load on the machine is proportional to the difference between the speed set point (set on the fuel controller) and the actual speed that the machine is running (bus frequency).
Lets put some numbers in
50 Hz system
100 MW machine
4% droop
4% droop equates to 2 Hz so for every 1Hz difference between set point and bus frequency the load will be 50 MW

Suppose you put the set point at 51 Hz the machine will load to 50 MW, but if the bus frequency now drops to 49.9 Hz the machine load will increase to 55 MW if it increases to 50.1 the load will decrease to 45 MW.

If you reduce the droop to 2% the effect of changes in the bus frequency will be doubled etc etc.
 
Dear Jobrag,

Thanks very much for reply. Can the Generator system become unstable as a result of low droop settings? how serious can it get?

Best Regards,
Shahvir
 

Similar threads

  • · Replies 46 ·
2
Replies
46
Views
6K
Replies
4
Views
4K
Replies
5
Views
2K
  • · Replies 22 ·
Replies
22
Views
4K
  • · Replies 14 ·
Replies
14
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 15 ·
Replies
15
Views
2K
Replies
51
Views
21K
  • · Replies 31 ·
2
Replies
31
Views
8K