Arcing in electrical relay contacts due to different types of loads

Click For Summary
SUMMARY

The discussion centers on arcing in electrical relay contacts, particularly how it varies with different load types. Inductive loads produce significantly greater arcing compared to resistive loads due to higher voltage surges during circuit interruption. Even resistive loads can cause arcing due to inherent inductance in the wiring and mechanical contact bounce. Effective methods to mitigate arcing include using RC networks, catching diodes, and understanding the voltage and current ratings of switches and relay contacts.

PREREQUISITES
  • Understanding of electrical relay operation
  • Knowledge of inductive and resistive load characteristics
  • Familiarity with arcing phenomena in electrical contacts
  • Basic principles of voltage and current ratings in electrical components
NEXT STEPS
  • Research "RC snubber circuits for relay contacts" to learn about arcing mitigation techniques
  • Explore "Inductive load characteristics and their impact on relay performance"
  • Study "AC vs. DC arcing in electrical contacts" to understand differences in arcing behavior
  • Investigate "Catching diodes and their applications in relay circuits" for practical implementation
USEFUL FOR

Electrical engineers, technicians working with relays, and anyone involved in designing or maintaining electrical systems that utilize relay contacts will benefit from this discussion.

srinaath
Messages
51
Reaction score
2
TL;DR
Arcing occur in a relay's contact due to closing and opening action. Does the arcing depends on the type of load? For example will there be any arc in a resistive load?
Arcing in a contact occurs due to open and close action of the switch. I am curious if the arc intensity depends on the type of load. For example the arcing (arc intensity) due to induction load will be greater than arcing due to resistive load?
 
Engineering news on Phys.org
You can definitely get a lot more arcing with an inductive load.
As the circuit is interrupted, the voltage across the contacts rises.
In the worse case, you have a current source with enough reserve voltage to continue the circuit even when the relay is fully open.
The same problem exists with circuit breakers and regular mechanical switches.
 
  • Like
Likes   Reactions: anorlunda and srinaath
.Scott said:
You can definitely get a lot more arcing with an inductive load.
As the circuit is interrupted, the voltage across the contacts rises.
In the worse case, you have a current source with enough reserve voltage to continue the circuit even when the relay is fully open.
The same problem exists with circuit breakers and regular mechanical switches.
Thanks @.Scott
quick clarification though - do we even see arcing in resistive load?
 
You do get some arcing with resistive loads - it's due to the fact that contacts can be 'close enough' to ionize air very near actual contact. Most contacts also 'bounce' a bit. for AC switching, polarity changes tend to 'extinguish' the arcs. For HV DC contactors, arc extinguishing is a major design consideration.
 
  • Informative
  • Like
Likes   Reactions: srinaath and anorlunda
Also - while the load may be resistive - the system will have parasitic (unintended) inductance.
 
srinaath said:
quick clarification though - do we even see arcing in resistive load?
Yes. Because the wires delivering the current to the relay contacts, and the wires connecting the resistive load to the relay contacts have some inductance.
 
Even if the load is not inductive at all, the mechanical process of separating the conductors can draw an arc.
In fact, when I look at a physical contact that is breaking a resistive load on the oscilloscope - and spread the timeline out to nanoseconds, I can see many makes and breaks - as the contacts slide across each other and finally separate.

What the induction does for you is provide a voltage surge just as the break occurs. But you may already have sufficient voltage to provide an arc. Aside from wear and tear on the contacts and the potential to trigger an explosive gas, arcing will also result in a very wide band of EM emisions.
 
  • Like
Likes   Reactions: anorlunda
When we close a contact, the volts/meter gradient in the air gap must approach infinity as the meters in the gap approaches zero. That is until we get some electrical breakdown (an arc) or the height of molecular irregularities of the surface become significant.

As @Dullard said, closing contacts also bounce. If we ionize a few molecules of air on the initial contact, that makes it easier to create an arc on the second and subsequent bounces.

So as others have said, even with DC, the arcing on switch contact surfaces is nonzero.

When we open a current carrying switch, then ##L\frac{dI}{dt}## becomes an additional or dominant factor, but even without L, the volts/meter across the gap begins at very large values.

But when low voltage relay contacts have a short lifetime, look for inductance as the cause.
 
  • Like
Likes   Reactions: Dullard
  • #10
Classic 'Bad Load' is 'traditional' small electric motor. It has just enough inductance for a lot of make/break arcing, which erode the brushes and commutator. You may hang a 'catcher' capacitance or back-to-back zener diodes across the motor terminals, which some-what limits the voltage excursions. This also mitigates EMP and line noise...
 
  • #11
This Spark suppression .pdf file may be useful to others.
To prevent the contacts from being eroded a RC network is placed across the contacts. When the contacts open the applied voltage is placed across the capacitor and not the contacts. The capacitor is to charge up at a rate faster than the contacts open thus preventing an arc from forming across the contacts.
suppression 1.jpg

suppression 2.jpg
 
  • Like
Likes   Reactions: Nik_2213
  • #12
The point about an inductor is that it tries to keep the current flowing through it constant ... which means the current tries to flow through the now open switch contacts.

The voltage across the open contacts rises until the medium breaks down and allows the current to flow.

Years ago I used an oscilloscope to measure the voltage spike generated when a tiny 12V reed relay was switched off. It generated an extremely short duration 1.5kV spike on top of the 12V rail. Adding a tiny catching diode limited it to 0.7V ... but held the relay closed for much longer.

Check the voltage and current ratings for switches or relay contacts. You will see that the DC current rating is usually far smaller than the AC current rating. As has been said, AC extinguishes the arcs at the zero voltage crossing thus reducing damage to the contacts.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
1K
Replies
9
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 5 ·
Replies
5
Views
5K
Replies
8
Views
9K
  • · Replies 25 ·
Replies
25
Views
6K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 9 ·
Replies
9
Views
3K