Current rating for an electromechanical contactor

Click For Summary

Discussion Overview

The discussion centers around the current ratings of an electromechanical contactor, specifically why the rated inductive current is lower than the rated resistive current. Participants explore the implications of these ratings in various applications, including AC and DC loads.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested

Main Points Raised

  • Some participants note that inductive current ratings are typically lower due to the inrush current experienced by inductive loads like motors.
  • One participant emphasizes the importance of the application for which the contactor is intended, mentioning that different utilization categories exist for AC and DC loads.
  • Another participant references a document to explain the behavior of inductors when interrupting current, suggesting that this is relevant to understanding the ratings.
  • Concerns are raised about the operating conditions affecting the ratings, such as the frequency of operations and ambient temperature, which may necessitate a higher-rated contactor.

Areas of Agreement / Disagreement

Participants generally agree on the reasons behind the difference in inductive and resistive current ratings, but there is no consensus on the implications for specific applications or the best practices for selecting contactors.

Contextual Notes

Participants mention various utilization categories and operating conditions that may affect the ratings, but these are not fully resolved or detailed in the discussion.

srinaath
Messages
51
Reaction score
2
I have a elctromechanical contactor (contactor is an electrically operated switch - It is larger version of relay) which has following specification,
Inductive full load current - 30A
Resistive full load current - 40A

Why is rated inductive current less than rated resistive current?
 
Engineering news on Phys.org
Could you supply the manufacturer and part number of the contactor? Is the controlled load AC or DC?

Generally speaking, inductive current rating is lower because inductive loads such as motors experience significant inrush current.
Another specification to pay attention to is the kW or HP power rating.

Contactors for DC loads require more scrutiny during selection, and are often designed specifically for DC operation.
 
  • Like
Likes   Reactions: Delta2
srinaath said:
Why is rated inductive current less than rated resistive current?

You already know the answer. What happens when you interrupt current through an inductor?

see section "Contact" about 1/3 of the way down this document.

https://media.digikey.com/pdf/Other%20Related%20Documents/Panasonic%20Other%20Doc/Small%20Signal%20Relay%20Techincal%20Info.pdf
 
  • Like
Likes   Reactions: Asymptotic and davenn
jim hardy said:
You already know the answer. What happens when you interrupt current through an inductor?

see section "Contact" about 1/3 of the way down this document.

https://media.digikey.com/pdf/Other%20Related%20Documents/Panasonic%20Other%20Doc/Small%20Signal%20Relay%20Techincal%20Info.pdf
great datasheet, @jim hardy thanks for that ... has been saved :)

Dave
 
  • Like
Likes   Reactions: jim hardy
srinaath said:
I have a elctromechanical contactor (contactor is an electrically operated switch - It is larger version of relay) which has following specification,
Inductive full load current - 30A
Resistive full load current - 40A

Why is rated inductive current less than rated resistive current?
This has been answered in the posts above, but another, and perhaps more important question is, "What do you intend to use the contactor for?" A particular make and model contactor will be rated differently depending upon the application.

In the IEC world the nature of the application is called it's utilization category. Categories prefaced with "DC" describe DC load applications. AC-1 (switching AC to resistive loads), AC-3 (switching AC to squirrel cage induction motors in typical start-stop service), and AC-4 (same as AC-3, except the contactor must withstand locked rotor amp breaking currents encountered when the application includes inching and/or jogging service) are the most common. Transformer, capacitor, and various forms of lighting present different challenges to the contacts, and have their own utilization categories.

Unusual operating conditions must also be accounted for. For example, a manufacturer's specifications may be valid for 50 operations or less per hour, and a higher-rated contactor will likely be required to provide more frequent operation. Same goes for operation in high ambient temperature environments, and so on.

Siemens, ABB, Eaton-Cutler Hammer, Allen-Bradley, and other contactor manufacturers provide detailed information in their specifications, and typically offer additional sizing and application guidelines, for instance, "Low-Voltage Switchgear and Controlgear - An Application Guide", document # LVSAM-RM003A-EN-P from Allen-Bradley.
 
  • Like
Likes   Reactions: jim hardy

Similar threads

  • · Replies 25 ·
Replies
25
Views
6K
Replies
47
Views
11K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 36 ·
2
Replies
36
Views
6K
Replies
12
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
5
Views
3K
  • · Replies 25 ·
Replies
25
Views
6K
Replies
10
Views
9K