As to the wattage, heat only gets to the garage whatever can be transferred through a one-inch text line at 22gpm
This discussion focuses on calculating the BTU requirements for heating a 40x60x14 foot garage from 40°F to 60°F in four hours, with an outdoor temperature of 20°F and humidity at 60%. The garage has three walls insulated to R19, one wall at R10, and a ceiling at R30. Participants recommend using the formula for heat transfer through walls, which is 1/R*A*dT, and suggest a safety factor of 50% to account for thermal inertia. The calculated heat requirement is approximately 9,095 BTU/hr, although this may be underestimated due to potentially optimistic insulation values.
PREREQUISITESHomeowners, HVAC professionals, and DIY enthusiasts looking to effectively heat garages or similar spaces, particularly in cold climates.
lurch85 said:How does that figure sort of aspect for time? Given being as decently sealed building??
lurch85 said:R 7-10 is probably more likely... 1 1/2 inch of low grade foam
24 hr * 5200 ft^2 * 20°F
------------------------- = 7.75
322,000 BTU
Time is generally not considered in this, since people rarely cycle the heat like this. But it shouldn't make much of a difference: If you've properly sized your heater, with the appropriate safety factor, the time to heat the room will be fairly short. No more than an hour and probably much less.lurch85 said:How does that figure sort of aspect for time? Given being as decently sealed building??