Calculation - impact force on a bollard

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
5 replies · 6K views
Ziv7
Messages
23
Reaction score
0
i need to work some estimations for this case for an assignment

30mph vehicle hits a bollard with 667kJ
bollard height = 1m
vehicle hits the bollard at approx height of 0.7m
material = mild steel
ultimate strength = 400mpa

in one case the bollard is 219mm ext diameter with 10mm wall thickness
the information given is that the bollard withstood the impact

The second case i need to work out what the wall thickness should be for a 150mm ext diameter bollard to withstand the same impact

assume the failure won't be at the floor fixings
for the time being i will ignore the fact the car deforms as well as the bollard, and there are different levels of impact(front bumper, engine etc.)
 
Physics news on Phys.org
i've worked out 46mm wall thickness for the second case if i equate second moment of area of the first and second case.
is that a fair estimation?
 
If a limiting stress isthe crierion, then use elastic section modulus (I/y), rather than second moment of area I. If collapse is the criterion use plastic section modulus.
 
Thanks for the advice

Do you know of a way to calculate the thickness without comparing it to the initial case?
 
The information on energy given suggests you can obtain an equivalent static force.