Hello Everyone,
I am trying to calculate the openings of a sealed room according to a pressure drop in a specific time.
I have the following equation:
Q = 840*A*√(dP)
Q: differential airflow in liters/sec
A: room leakage in m2
dP: differential pressure in Pa
So, if for example we have a room of 500m3 at atmospheric pressure 101325 Pa and we increase its pressure** by 80 Pa and then measure how much time it will need to decrease for 30Pa we can calculate the differential airflow by the following:
(Psi + Pstart) * V1 = (Psi + Pfinish) * V2 <=>
(101325+80) * V1 = (101325+50) * V2 <=>
V2 = 500.148m3
So because of a dP of 30Pa we get 148 liters difference.
If that dP occurred in 180sec then we get Q= 148/180 = 0.82 liters/sec
If we then put this number to the initial equation we get the room leakage.
My problem is that the results that I get are different from another method that is used to find the room leakage. So obviously there is a mistake in the above calculations but I can't find what.
**The pressure increase of the room is achieved by using a blower and the temperature is stable.
Does anyone have an idea?
Thank you in advance!
I am trying to calculate the openings of a sealed room according to a pressure drop in a specific time.
I have the following equation:
Q = 840*A*√(dP)
Q: differential airflow in liters/sec
A: room leakage in m2
dP: differential pressure in Pa
So, if for example we have a room of 500m3 at atmospheric pressure 101325 Pa and we increase its pressure** by 80 Pa and then measure how much time it will need to decrease for 30Pa we can calculate the differential airflow by the following:
(Psi + Pstart) * V1 = (Psi + Pfinish) * V2 <=>
(101325+80) * V1 = (101325+50) * V2 <=>
V2 = 500.148m3
So because of a dP of 30Pa we get 148 liters difference.
If that dP occurred in 180sec then we get Q= 148/180 = 0.82 liters/sec
If we then put this number to the initial equation we get the room leakage.
My problem is that the results that I get are different from another method that is used to find the room leakage. So obviously there is a mistake in the above calculations but I can't find what.
**The pressure increase of the room is achieved by using a blower and the temperature is stable.
Does anyone have an idea?
Thank you in advance!