CT for restricted earth fault (REF) protection

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
3 replies · 16K views
saragiha
Messages
3
Reaction score
0
Does somebody could advice me, whether the nominal primary CT to be used for REF protection must be same?

The CT I have now as follow:
Power Transformer: 60MVA, 150/20kV, Ynyn(0)d1
CT on 20kV switchgear 2000/5, class 5P20
CT on neutral Power Transformer: 1200/5, class X
Relay to be used: Areva Micom P632
 
Engineering news on Phys.org
Generally in high impedance Restricted Earth Fault (REF) protection, the ratio of involved CTs must be same, but in low impedance type it can be difference.
For more information about low and high differential protection also REF you can refer to Protection Riddle No.59 and other riddles from http://electrical-riddles.com
 