Decrease the level of the battery for UPS syatem

  • Thread starter Thread starter eng_2009
  • Start date Start date
  • Tags Tags
    Battery decrease
Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
8 replies · 1K views
eng_2009
Messages
5
Reaction score
0
Hi,

I faced problem with the decrease the level of the batteries for UPS system and from time to time i filled the batteries but still the level decrease after one week...

what is the problem and solution؟

best regards,
 
Engineering news on Phys.org
If you had to fill them that sounds like lead-acid flooded batteries. Is that correct?

Gradual decrease in that type of battery is usually caused by sulphation. The cure is a special de-sulphating charge cycle, also called equalizing charge cycle. Only some chargers have that feature.

Another possibility is a cracked plate, but that would happen suddenly, not gradually.
 
there is no cracked plate
 
If it is lead acid flooded, then my previous reply about equalization charge is your answer.If it is lead acid sealed gel cell, then it can be easily damaged by charging it to too high a voltage. The UPS charging set point must be specific for gel cells.
 
it is on the float mode not on boost mode
 
You can float a flooded battery at 14.2 volts, but float a gel cell to 13.8 volts max. Which is it?
 
i have 60 battery cells connected in series
each cell 2.2 vdc
total voltage 132 vdc
 
Whoa, that is outside my experience base. I'll bow out of this thread. Hopefully, someone else can help you.