The discussion centers around whether a Direct On Line (DOL) starter can effectively support a 160 kW, 1000 kVA sump pump. Participants highlight that while DOL is a simple switching method, it may not be suitable due to the high starting current, which can cause significant voltage drops in the grid. Alternative starting methods such as star-delta, autotransformer, and soft starters are suggested as potentially more effective options. The pump specifications indicate that starting multiple pumps simultaneously could exacerbate voltage drop issues, raising concerns about the grid's capacity to handle the load. The consensus leans towards needing a more robust starting solution to ensure reliable operation of the pumps.
Lincoln
Messages
3
Reaction score
0
Hello! Everyone,

I am Lincoln from Singapore. I am from mechanical background. Recently, I am handling a rain-water tank with sump pumps project.

May I seek you guys who are in electrical expertise for some professional advice for the following:

Is the DOL starter possible to support 160 KW, 1000 KVA sump pump?

Beside DOL, any other starter is optional to support this pump's capacity?

Hear you soon. Thanks. :shy:
 
Engineering news on Phys.org
Lincoln said:
160 KW, 1000 KVA sump pump?
160 KW ?
Three phase or single phase?

DOL = “Direct On Line” is not a starter, it is a simple switch or contactor.
A 1kW, 3 phase motor can probably be started DOL as the pump impeller does not represent a significant initial load.
 
It mainly depends on the grid it is connected to. The problem faced with starting is the voltage drop in the cables/grid becomes to large due to the large starting current. Thus a reduced terminal voltage will reduce the output torque of the motor, and it may not be enough to overcome the load torque.

The DOL starting current may be in the range of 4-6 times the nominal current. Does the grid support this with respect to protective relays and such?

Other starting methods are:
autotransformer
start-delta
softstarter
variable frequency drive
(there exists many more, but these are the most used)
 
We need confirmation from the OP of the power involved here.
If it is really a 1 MW motor then it will need a star-delta starter.
I suspect that there are scale factors here that are out by a factor of 1000.
 
Hi! Baluncore,

I checked the specification of the motor, its stated as following:

Power Supply: 3 Phase x 400V x 50Hz
Rated Power: 160 KW
No of Poles: 6P
Rated current: 288A
Load: 50% 75% 100%
Efficiency: 89.3% 90.7% 82.1%
Power Factor: 78.4% 83.5% 87.0%

Likewise, the pump specification as follows:

Pump Eff: 81.0%
Shaft Power: 138.1 KW
Revolution: 980 rpm

Having given the above data from the pump manufacturer, is it ok to use DOL to start this motor? If we use Soft-starter, how much the voltage drop by starting a pump?

The project needs to start 4 pumps in operation.

Baluncore said:
160 KW ?
Three phase or single phase?

DOL = “Direct On Line” is not a starter, it is a simple switch or contactor.
A 1kW, 3 phase motor can probably be started DOL as the pump impeller does not represent a significant initial load.
 
Hi! SirAskalot,

I refer back to the pump manufacturer proposal, the recommended electrical connection is DOL and Star-delta starting. The electrical engineer proposed the motor starters shall be DOL type.

"Where Star-delta or Autotransformer Starters are used with Closed Transition type and the maximum transient current surge changing from one stage to another must not exceed 3 x motor Full Load Current (FLC)."

With both pump and motor technical specifications and the above proposal, do u guys think is it workable?

Let's say if Star-delta is used, how much voltage drop to drive the initial torque? There are 4 pumps in operation. Can this starter design start a pump at a time or 2?

Please impart me any input to rectify any potential problem. During the meeting, the contractor's engineer failed to draw a conclusion. They simply said they couldn't drive any of the 4 operating pumps.

Thanks. :-)

SirAskalot said:
It mainly depends on the grid it is connected to. The problem faced with starting is the voltage drop in the cables/grid becomes to large due to the large starting current. Thus a reduced terminal voltage will reduce the output torque of the motor, and it may not be enough to overcome the load torque.

The DOL starting current may be in the range of 4-6 times the nominal current. Does the grid support this with respect to protective relays and such?

Other starting methods are:
autotransformer
start-delta
softstarter
variable frequency drive
(there exists many more, but these are the most used)
 
Last edited:
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...