Duct sizing chart - pressure loss

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
3 replies · 3K views
TSN79
Messages
422
Reaction score
0
I found this sizing chart for ventilation ducts. Notice the gray area for what I suppose is the accepted pressure loss area. What I wonder is why it changes as the sizes pass Ø800. From here on the upper pressure loss limit goes down to 0,7 Pa/m. Is this because of velocity issues or something else?
 

Attachments

  • preview006.jpg
    preview006.jpg
    70.3 KB · Views: 692
Physics news on Phys.org
That's something I should probably know, but I don't. It could be an issue of duct strength, economics, noise. I'm really not sure. I use a duct sizing calculator (rotary slide rule, basically) which has no similar markings. where did you get it?
 
I'm pretty sure it's a limit on velocity, and not on pressure losses. 200,000 l/s of gas rocketing through a pipe at 40 m/s is not within typical design limits.