Efficiency Calculation of 10-kVA Transformer at 0.85 Power Factor Lagging

  • Context: Archived 
  • Thread starter Thread starter graygoh
  • Start date Start date
  • Tags Tags
    Physics Transformer
Click For Summary
SUMMARY

The efficiency of a 10-kVA transformer operating at a 0.85 power factor lagging is calculated to be 89%. The transformer was tested under open circuit conditions, yielding a core loss of 450W, and under short circuit conditions, resulting in a copper loss of 600W. The total losses amount to 1.050 kW, which is used to determine the efficiency using the formula η = Output power / Input power.

PREREQUISITES
  • Understanding of transformer operation and efficiency calculations
  • Knowledge of power factor and its implications in electrical systems
  • Familiarity with electrical losses: core loss and copper loss
  • Proficiency in using formulas for calculating efficiency in electrical devices
NEXT STEPS
  • Study the principles of transformer efficiency calculations
  • Learn about the impact of power factor on transformer performance
  • Explore methods for minimizing core and copper losses in transformers
  • Investigate the differences between open circuit and short circuit tests in transformer analysis
USEFUL FOR

Electrical engineers, students studying power systems, and professionals involved in transformer design and efficiency optimization will benefit from this discussion.

graygoh
Messages
1
Reaction score
0

Homework Statement


A 10-kVA, 200:400 V transformer gave these test results:
open circuit (LV winding supplied): 200V, 3.2A, 450W
short circuit (HV winding supplied) : 38 V, 25A, 600W
calculate the efficiency when the transformer delivers its rated kVA at 0.85 power factor lagging

Homework Equations



efficiency = output power / input power

The Attempt at a Solution


I totally don't know how to start. help pls. thanks
 
Physics news on Phys.org
graygoh said:
open circuit (LV winding supplied): 200V, 3.2A, 450W
This gives the core loss of the transformer.
Pi=450W
graygoh said:
short circuit (HV winding supplied) : 38 V, 25A, 600W
This gives the copper loss of the transformer at full load.
Pcu=600W
Iron loss is fixed loss and doesn't depend on the load. Copper loss varies proportional to the square of the current. In general, copper loss=x2Pcu, where x is the fraction of full load with which the transformer is loaded. Since the transformer is operated at full load, x=1 and the losses will be,
P=Pi+Pcu
=450+600=1.050kW.
Efficiency η= Output power/input power
=Output kW/(Output kW+losses)
∴ η=10×0.85/(10×0.85+1.050)
∴ η=0.89
The transformer is 89% efficient.
 
Last edited:

Similar threads

  • · Replies 3 ·
Replies
3
Views
3K
Replies
10
Views
5K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
3K