Find the reactive power before power factor correction

1 reply · 1K views · last reply
falyusuf
Messages
35
Reaction score
3
Homework Statement
The power factor of a certain load is improved to 0.92 lagging with the addition of a 30 kVAR bank of capacitors. If the resulting supply apparent power is 200 kVA, determine the power factor before correction.
Relevant Equations
Attached below.
Relevant Equations:
Handwritten-style typeset equations: Qc = Q1 - Q2; Q = S sin θ, P = S cos θ; C = (Q1 - Q2)/(w.Vrms^2) = P(tan θ1 - tan θ2)/(w.Vrms^2).


My solution:
Handwritten-style typeset working for a power factor correction problem: P = S cos θ, P = 200k × 0.92 = 184 kW, θ2 = cos⁻¹(0.92) = 23.07°, Qc = Q1 − Q2, 30k = Q1 − S2 sin θ2, Q1 = 108.2827 kVAR, Qc = P(tan θ1 − tan θ2), θ1 = 30.496°, cos θ1 = 0.862 lagging.


Could someone please verify my answer?