Power Factor Correction for a 230V Single Phase Lighting Installation

Click For Summary

Discussion Overview

The discussion revolves around calculating the size of a capacitor bank needed to achieve a power factor of 0.95 for a single-phase, 230V, 50Hz lighting installation with a load current of 17.5 A and an initial power factor of 0.8. Participants explore various methods and calculations related to power factor correction, including the use of nomograms, phasor diagrams, and admittance.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant calculates the required capacitor size using two different approaches, arriving at 550μF and 173μF, but expresses uncertainty about the first method.
  • Another participant suggests using a phasor diagram to determine the change in the reactive component needed for the power factor correction, estimating a capacitor size of 123μF.
  • A later reply questions the calculations of inductive reactance and emphasizes the importance of using admittance for parallel components, suggesting a smaller capacitance value.
  • Subsequent calculations refine the values for inductive reactance and capacitive reactance, with one participant arriving at 54.22μF and later correcting it to approximately 79.5μF.
  • There is a discussion about the relationship between impedance and admittance, with clarifications on how to correctly calculate the components involved in the power factor correction.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the final capacitor size, with multiple competing calculations and methods presented throughout the discussion. Uncertainty remains regarding the accuracy of various intermediate steps and the final results.

Contextual Notes

Participants express limitations in their calculations, including potential errors in determining inductive reactance and the need for more precision in intermediate values to improve final results.

topcat123
Messages
77
Reaction score
1
The problem statement

Using the nomogram of FIGURE 10, calculate the size of
capacitor bank to give a final power factor of 0.95 for a single phase,
230 V, 50 Hz lighting installation which has a load current of 17.5 A and
operates at 0.8 pf.

The nonogram gives a value k = 0.44

Relevant equations

Qc = Pk

Xc = 1/2pifC

P = VI



The attempt at a solution

I have come up with two ways but i think the first is wrong as the current though the capasitor (If in parrallel) will not be the same as the load current.

Attempt 1

P = 230 x 17.5 = 4025W

Qc = 4.03 x 0.44 = 1.77 KVAr

P = I^2 x Xc

Xc = P/I^2 = 1.77 x 1000 x 17.5^2 = 5.783Ω

so C would come out at 550μF (as I said I think this is wrong)

Attempt 2

Power still = 4025W and Qc = 1.77 KVAr

but P = V^2/Xc so Xc = V^2/P

Xc = 230^2 x 1.77 x 1000 = 18.38Ω

so C would work out at 173μF

Just a bit of guidance would be appreciated.
 
Physics news on Phys.org
Hi topcat123, Welcome to Physics Forums.

While I'm not that familiar with the usual methodologies used in Power Systems (like the nomogram you mention), I can suggest a more generic approach.

Since you are given the current magnitude and the power factor you can write the current phasor (complex or polar form). Knowing the voltage too, you can write the impedance or admittance of the load (Y = 1/Z = I/V).

Recalling that admittances add in parallel, you can find the admittance (of a capacitor) to add in order to bring the pf from 0.8 to 0.95; It's just a matter of reducing the imaginary component of the total admittance to the desired value, and capacitors have negative imaginary admittance...
 
gneill said:
Hi topcat123, Welcome to Physics Forums.

capacitors have negative imaginary admittance...

Ahem ... :smile:
 
rude man said:
Ahem ... :smile:

Hah! Well caught. Dunno why that brain cell fired :smile:
 
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF
 
topcat123 said:
So draw a phase diagram for 0.8 pf.
Work out the restive current.
Overlay the new 0.95 pf and work out the change in the reactive component.
from that i con work out the capacitor size.

Doing it this way i get 123μF

before i got 173μF

Can you show more of your work?

I think it would be better to work with admittances, since they add in parallel (presumably the capacitor bank will be placed in parallel with the load). I'm seeing a smaller value of capacitance for the result.
 
  • Like
Likes   Reactions: 1 person
Ok

Z=V/I = 230/17.5 = 13.14Ω

cos θ = 0.8 so R = 0.8 x 13.14 = 10.512Ω

Xl = √Z^2 - R^2 = 62.16Ω

New pf = 0.95 = cos θ
θ = 18.19°
R tan 18.19° = Xl-Xc =3.455Ω

There for Xc = 58.71Ω

C=1/2πfXc = 54.22μF
 
Check your calculation of Xl. 62.16Ω looks too large.

Remember that impedances in parallel don't add algebraically. Admittances (1/Z) add.
 
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?
 
  • #10
topcat123 said:
yes Xl should be 7.88Ω forgot to √it.

So Xl-Xc = 3.455Ω
(1/3.455)-(1/7.88) = 1/Xc

Xc = 6.152Ω

C=1/2πfXc = 1/(2π x 50 x 6.152) = 0.000517F

Is this better?

One problem, while it is true that admittance is the inverse of impedance, Y = 1/Z, it is not true that the imaginary part of the admittance is equal to the inverse of the imaginary part of the impedance. That is, Im(Y) ≠ 1/Im(Z).

Start by finding Y = 1/Z. Then work with its components; you want to reduce its polar angle in the same fashion that you're trying to do for the impedance.
 
  • #11
Z = V/I = 230/17.5 = 13.14Ω

Y = 1/Z = 0.076

G = Y cosθ = 0.076 x 0.8 = 0.061

Bl =√z^2 - G^2 = 0.076^2 - 0.061^2 = 0.045

new pf 0.95

cosθ = 0.95 θ = 18.19°

Bl-Bc = G tan 18.19° = 0.020

Bc = 0.025

Xc = 1/Bc = 40Ω

which makes C = 79.5μF

Hope i have it this time...
 
  • #12
That looks MUCH better! I think if you hang on to a few more digits of accuracy for intermediate values your final result will be closer to 81.6 μF.

Cheers!
 
  • #13
Thanks for the help gneill.
 
  • #14
topcat123 said:
Thanks for the help gneill.

No worries, I'm glad to help!
 

Similar threads

  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 6 ·
Replies
6
Views
4K
  • · Replies 20 ·
Replies
20
Views
5K
Replies
2
Views
4K
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 2 ·
Replies
2
Views
6K
  • · Replies 2 ·
Replies
2
Views
2K