Flap Valve Opening - Rope Tension and Anchor Pull Out Force

Click For Summary

Discussion Overview

The discussion revolves around the mechanics of lifting a hinged flap valve using a rope and anchor system. Participants explore the forces involved, particularly the pull-out force on the anchor bolt and the tension in the rope at various angles of the flap's opening. The context includes statics and mechanical advantage considerations in the design of the lifting mechanism.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant describes the setup involving a 10kN flap and a 40kN rated anchor bolt, seeking to calculate the pull-out force and rope tension at a 30-degree opening angle.
  • Another participant questions whether there is any additional load on the flap when it is vertical, suggesting that the problem is fundamentally a statics issue.
  • Concerns are raised about the cable connection point on the flap, with suggestions that moving it higher could affect the mechanical advantage during the lift.
  • A participant expresses confusion about resolving moments and angles as the flap opens, indicating a need for clarity in calculations.
  • One participant cautions that while a higher connection point may improve the pulling angle initially, it could reduce mechanical advantage at lower angles.
  • A participant shares their calculation of rope tension at a small opening angle, expressing doubt about the low value obtained and seeking feedback on their method.
  • Another participant proposes an alternate calculation method that yields a higher tension value at the specified angles.
  • A participant addresses concerns about the safety of uploaded files by providing a jpeg image of their calculations instead of an Excel file.

Areas of Agreement / Disagreement

Participants express varying opinions on the optimal connection point for the lifting cable and the implications of different angles on mechanical advantage. There is no consensus on the best approach to the calculations or the implications of the flap's angle on the forces involved.

Contextual Notes

Participants mention the need for scale drawings to better understand the forces and moments involved, indicating that assumptions about the flap's loading conditions and connection points may affect the calculations. The discussion reflects a range of uncertainties regarding the mechanics of the system.

RandomUser_87
Messages
3
Reaction score
1
Hi everyone,

I have attached a sketch which may help understand the question I have.

I have a hinged flap which hangs vertically (hinge at top). The flap weight is 10kN and it is 1.8m tall (uniform mass). At the bottom of the flap is a lifting eye.

2.5m away and 0.3m above height of the hinge is an anchor bolt, to which i will connect a lifting block. I then intend on lifting the flap with a single rope through this block.

The question I have is, the anchor bolt is rated to 40kN pull out force so I would like to see what
a) the pull out force will be on the anchor bolt when the flap is open 30deg
b) what the tension is in the rope at the same angle.

The calcs are just to give a ballpark figure for now and will be determined by a supplier later. I would just like an indication of what lifting gear will be required.

I have looked through previous questions and a lot seem to relate to a horizontal flap being lifted and i am struggling to get my head around things when rotated 90deg.I assume that tension is zero when the flap is just hanging down on its own and is a maximum when the flap is fully open (90deg) but I am struggling to make this work.

Thanks for you help.
 

Attachments

  • physics forum - flap opening.png
    physics forum - flap opening.png
    35.3 KB · Views: 801
  • Like
Likes   Reactions: berkeman
Engineering news on Phys.org
Is there any load against the flap when in is vertical (such as impounded water?)? In any case, this is nothing more than a statics problem. Where is the difficulty?
 
upload_2017-11-3_15-33-10.png


The cable may not be connected to the flap at the ideal position . There could be significant advantage in moving the connection point up some way from the bottom edge . Exactly where you can determine from a scale drawing showing the line of pull of the cable at start , middle and end of lift .
 

Attachments

  • upload_2017-11-3_15-33-10.png
    upload_2017-11-3_15-33-10.png
    35.3 KB · Views: 1,520
Dr.D said:
Is there any load against the flap when in is vertical (such as impounded water?)? In any case, this is nothing more than a statics problem. Where is the difficulty?

You are correct it is a simple statics problem, unfortunately its been quite a while since high school. But my assumption is to resolve the moments about the pivot to determine the tension force required for equilibrium. Then to resolve the tension force to determine the horizontal/pull out force?

Unfortunately the angles have me a little confused and I am unsure what is really happening as the angle increases (and ultimately approaches 90deg.

Nidum said:
View attachment 214272

The cable may not be connected to the flap at the ideal position . There could be significant advantage in moving the connection point up some way from the bottom edge . Exactly where you can determine from a scale drawing showing the line of pull of the cable at start , middle and end of lift .

This is a very good point, the flap valve has not been installed yet so the attachment positioned might be better located further up the valve if need be.
 
From the diagram shown, I would caution about moving the cable connection to the flap higher. While this would improve the pulling angle early in the lift, it would also reduce the distance between the CG of the flap and the connection point thereby reducing the mechanical advantage at the closed position and all additional lifted points of the flap; and, as the flap approaches 90° it results in an increased angle between the pulling line and flap at the point of maximum weight effect of the flap.
 
Thanks for the replies everyone,

Before I go further and look at moving the anchor position the flap is lifted from, could someone please sense check my calc on the Tension, T in the rope at a small opening angle, the Tension seems to be quote low for me (approx 1.5kN to open a 10kN valve 15degrees).

I have calculated the moments by resolving for the vertical and horizontal, but I seem to recall a way to find the angle of the moment lever, making the calc a bit easier. Any feedback would be appreciated.

Thanks
 

Attachments

  • Flap Tension Calc - 15deg.JPG
    Flap Tension Calc - 15deg.JPG
    37.3 KB · Views: 754
After some consideration, I am attaching an alternate method of calculation that results in a bit higher T value at the given angles.
 

Attachments

It has been brought to my attention that some are concerned about the safety of uploaded Excel files; so, to address that concern I have uploaded the below jpeg file showing the above calculation.
 

Attachments

  • Flap Rope Tension Calc.JPG
    Flap Rope Tension Calc.JPG
    52.8 KB · Views: 762

Similar threads

  • · Replies 9 ·
Replies
9
Views
1K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 1 ·
Replies
1
Views
9K
Replies
4
Views
4K
Replies
13
Views
3K
  • · Replies 38 ·
2
Replies
38
Views
5K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
22
Views
4K
  • · Replies 13 ·
Replies
13
Views
3K
  • · Replies 19 ·
Replies
19
Views
2K