Homework Statement



The load in Fig. 11.44 draws 10 kVA at PF =0.8
lagging. If |IL |=40 A rms, what must be the value of C
to cause the source to operate at PF =0.9 lagging?

Homework Equations



P(apparent power VA)= |I| |V| cos@
@ = @V - @I
cos@= p.f
X= Xrms*(2)^0.5
S(complex power)= 0.5 * I * V (cos@ - j sin@)

The Attempt at a Solution


I just face a difficulty in knwoing the face of IL
I will be thankful if you solved the wole problem.
 

Attachments

  • Ele204.gif
    Ele204.gif
    11.8 KB · Views: 477
First, there is no capacitor. And, you have 10 kVA at 0.8 so 8 kW.

You add a capacitor and you get 10 kVA at 0.9 and 8KW

Find the reduction in the reactive power required to make the pf equal to 0.9. To find the capacitor value now you have its reactive power and you need voltage which is equal to the voltage across the source.

You can find the voltage across the source using the initial condition when there is no capacitor.
 

Similar threads

  • · Replies 21 ·
Replies
21
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 30 ·
2
Replies
30
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K