AC Circuit (RL) Homework: Finding the Series R-L Equivalent for Two Loads

Click For Summary

Discussion Overview

The discussion revolves around finding the series R-L equivalent of two loads connected to a power source in an AC circuit. Participants explore the implications of load specifications, power factors, and the effects of cable impedance on the overall circuit behavior. The conversation includes elements of homework-related problem-solving and technical reasoning.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant questions whether supplying 230V, 50Hz to the loads guarantees a power output of 1kW, to which another confirms that each load can indeed draw 1kW.
  • There is a discussion about whether finding the series R-L equivalent involves converting the impedances of the loads from parallel to series, with some participants suggesting that the loads can be treated as combinations of resistors and inductors.
  • One participant expresses confusion about the nature of the loads, questioning if they are purely inductive given that they dissipate real power.
  • Another participant clarifies that each load comprises both resistance and inductance, which together determine the power factor.
  • There is a debate about the relevance of cable impedance, with some participants arguing that it is not a concern for calculating the loads' power output, while others express uncertainty about how it affects the voltage supplied to the loads.
  • One participant raises a concern about using the nominal power output of 1kW if the loads are not receiving the specified 230V, leading to further clarification about the nature of load specifications and their tolerance to voltage variations.
  • Participants discuss the implications of the cable's resistance and inductance, noting that it introduces realism into the problem but may not directly affect the calculations for the loads' impedances.
  • Some participants suggest that the cable impedance may become relevant in later parts of the problem, particularly regarding power factor and additional components like capacitors.

Areas of Agreement / Disagreement

Participants express differing views on the relevance of cable impedance and its impact on load specifications. While some agree that the nominal values can be used for calculations, others remain uncertain about how variations in voltage affect power output. The discussion does not reach a consensus on these points.

Contextual Notes

Participants acknowledge that the loads are specified at 230V, 50Hz, and that the calculations may not reflect real-world conditions due to cable impedance. There are unresolved questions about how to accurately account for these factors in the overall analysis.

galaxy_twirl
Messages
137
Reaction score
1

Homework Statement



In the circuit shown in Figure Q2(b), two loads A and B are connected to the source. The cable connecting the power supply to the load is modeled as series R and L of values R = 0.1Ω, L = 0.1 mH as shown in the figure.

The loads have the following specifications:
Load A: 230V, 50Hz, 1kW, pf=0.5 lagging.
Load B: 230V,50Hz, 1kW, pf=0.87 lagging

Find the series R-L equivalent of the two loads together.

Figure 2(b):
j9q00p.jpg


Homework Equations



ZL = jωL
Pactive = Vrms*Irms*cos∅ (∅ means phi)
Preactive = Vrms*Irms*sin∅ (∅ means phi)

The Attempt at a Solution



Given the specifications for loads A and B, am I right to say that as long as I supply 230V, 50Hz to those 2 loads, I will get a power output of 1kW? Just wondering, does "Find the series R-L equivalent of the two loads" mean I have to find the impedances of Load A and B and convert them from parallel to series connection (just like 2 parallel batteries)?

Since the loads have lagging power factor, they are inductors.

As I am not given more information on the loads, I can only deduce L from Pactive = Vrms*Irms*cos∅, and vL(t) = L(diL(t)/dt)). Am I right to say this? However, I am stuck as I don't know Vrms and Irms.

May I have some hints please?

Thank you. :)
 
Physics news on Phys.org
galaxy_twirl said:
Given the specifications for loads A and B, am I right to say that as long as I supply 230V, 50Hz to those 2 loads, I will get a power output of 1kW?
Yes, 1kW from each.
Just wondering, does "Find the series R-L equivalent of the two loads" mean I have to find the impedances of Load A and B and convert them from parallel to series connection (just like 2 parallel batteries)?
Convert from 2 inductors and 2 resistances to a single equivalent L-R.
 
NascentOxygen said:
Convert from 2 inductors and 2 resistances to a single equivalent L-R.

Thank you. :) What do you mean by 2 inductors and 2 resistances? Just to confirm, Load A and B are not purely inductors right? (I am getting a bit suspicious because it dissipates active(real) power, as stated, "1kW".)

If that is the case, I will have ZA = R + jX, where R is resistance and X is the inductance (or imaginary part), right?
 
Each load can be considered to comprise one R and one L, and the combination determines that load's power factor.

The R accounts for real power.
 
I see. Thanks. I shall go and try it and let you know if I can get the answer, prolly a few hours later as I have to run now. :)
 
I am still not getting what does "find the series R-L equivalent of the 2 loads together mean". Does it mean I find the total impedance and then do 1/Zeff = 1/Z1 + 1/X2 ?

i.e.: For Load A, I do:

Pactive = Vrms*Irms*cos∅ (phi).

Hence, Pactive = Vrms*(Vrms / Z)*cos∅, so substituting all values in, we have:

1000 = (2302 / ZA)*cos∅.

However, I was wondering, the active power will not be the same since the inductor and resistor took up some voltage before it reaches the node of Load A. Am I right to say this? And may I know if my working above is correct?

Thanks!
 
Yes, you can sum the reciprocals of the impedances, the loads are parallel. Your method looks like it should work.

Inclusion of the cable impedance gives the problem realism. You are correct in saying the loads will not receive their rated 230V, but that is not relevant to the specific task you are tackling here.
 
NascentOxygen said:
Yes, you can sum the reciprocals of the impedances, the loads are parallel. Your method looks like it should work.

Inclusion of the cable impedance gives the problem realism. You are correct in saying the loads will not receive their rated 230V, but that is not relevant to the specific task you are tackling here.

I see. I didn't know the cable will have impedance. I suppose it is linked to resistance in the cable and passing an AC voltage changes the term resistance to 'impedance', right?

May I know why is it not a concern that the loads are not receiving 230V? I thought they will not give the max rated power output of 1kW if they are not supplied with 230V of p.d. across them.

Thank you. :)
 
The calculations you are doing concern load specifications, and these are specified at 230V.

A cable has resistance, also inductance, as well as capacitance to earth, so it has a characteristic impedance.
 
Last edited:
  • #10
NascentOxygen said:
The calculations you are doing concern load specifications, and these are specified at 230V.

I see. But if I don't supply 230V as in this case, won't I be wrong if I use 1kW as the power output? Sorry. I am a bit confused at the moment. :(
 
  • #11
galaxy_twirl said:
I see. But if I don't supply 230V as in this case, won't I be wrong if I use 1kW as the power output? Sorry. I am a bit confused at the moment. :(
The loads are defined by Specification:

galaxy_twirl said:
The loads have the following specifications:
Load A: 230V, 50Hz, 1kW, pf=0.5 lagging.
Load B: 230V,50Hz, 1kW, pf=0.87 lagging

That means that these loads, if connected to an ideal 230 V, 50 Hz source without any intervening cable would draw the specified power at the specified phase angle. This gives you enough information to characterize these loads in terms of their impedances. The power cable is irrelevant for this problem.

Perhaps there are other sections to the problem which you've not mentioned yet where the cable impedance becomes important?
 
  • #12
galaxy_twirl said:
I see. But if I don't supply 230V as in this case, won't I be wrong if I use 1kW as the power output? Sorry. I am a bit confused at the moment. :(
In practice, the supply voltage is never going to be exactly what the load was nominally specified to operate from. This is a fact of life, and power engineers accept this. Sure, it does mean that the load probably won't be drawing exactly 1,000.0 watts of power whenever its voltage departs from 230.0V but loads are designed to be tolerant of voltage errors (and may compensate for it by various means if ever it's important). If precise calculations are needed then that can be done, but here you are basing your calculations on the nominal design voltage, 230V. So long as the cable impedance is within acceptable limits, the loads will work just fine on whatever the voltage ends up being.
 
  • #13
gneill said:
The loads are defined by Specification:
That means that these loads, if connected to an ideal 230 V, 50 Hz source without any intervening cable would draw the specified power at the specified phase angle. This gives you enough information to characterize these loads in terms of their impedances. The power cable is irrelevant for this problem.

Perhaps there are other sections to the problem which you've not mentioned yet where the cable impedance becomes important?

I see. Thanks for your explanation. :)

Perhaps there are other sections to the problem which you've not mentioned yet where the cable impedance becomes important?

Hmm. There are 2 small question parts related to this question. They are:

Part ii) Find the power factor as seen from the source.
Part iii) Find the value of the capacitor to be connected across the source so that the source voltage and the total current drawn from it are in phase with each other.

I think the questions above should not interfere with how I see/factor in the RL of the cable. :)
 
  • #14
NascentOxygen said:
In practice, the supply voltage is never going to be exactly what the load was nominally specified to operate from. This is a fact of life, and power engineers accept this. Sure, it does mean that the load probably won't be drawing exactly 1,000.0 watts of power whenever its voltage departs from 230.0V but loads are designed to be tolerant of voltage errors (and may compensate for it by various means if ever it's important). If precise calculations are needed then that can be done, but here you are basing your calculations on the nominal design voltage, 230V. So long as the cable impedance is within acceptable limits, the loads will work just fine on whatever the voltage ends up being.

I see. Alright. I shall try it out later. :) Thanks! I am just a bit puzzled about the voltage issue but other than that, I should be fine. :)
 
  • #15
galaxy_twirl said:
Hmm. There are 2 small question parts related to this question. They are:

Part ii) Find the power factor as seen from the source.
Part iii) Find the value of the capacitor to be connected across the source so that the source voltage and the total current drawn from it are in phase with each other.

I think the questions above should not interfere with how I see/factor in the RL of the cable. :)
Okay, these two questions are where the cable impedance comes into play. The source sees the cable impedance as part of its total load.
 
  • #16
gneill said:
Okay, these two questions are where the cable impedance comes into play. The source sees the cable impedance as part of its total load.

I see. Thanks! I will take a look again tomorrow and if I have any problems I will post here again. :)
 
  • #17
I got ZA = 26.45 Ohms after working out the above. However, how do I express this in terms of Z = R + jX = R + jωL?

I realized my teacher somehow arrived at 13.23 Ohms for R. How and why did my teacher do that? *puzzled* :S
 
  • #18
galaxy_twirl said:
I got ZA = 26.45 Ohms after working out the above. However, how do I express this in terms of Z = R + jX = R + jωL?

I realized my teacher somehow arrived at 13.23 Ohms for R. How and why did my teacher do that? *puzzled* :S
26.45 is the magnitude of the "A" impedance. What's its angle?
 
  • #19
gneill said:
26.45 is the magnitude of the "A" impedance. What's its angle?

From power factor = cos∅, cos∅=0.5, hence, by cos-1 0.5 = 60°. Angle = 60°
 
  • #20
galaxy_twirl said:
From power factor = cos∅, cos∅=0.5, hence, by cos-1 0.5 = 60°. Angle = 60°
Yup. So you have the polar form of that impedance. Convert to rectangular.
 
  • #21
gneill said:
Yup. So you have the polar form of that impedance. Convert to rectangular.

OH! I get the picture now. Oh dear. I think one really cannot do engineering without a strong Maths foundation. Sigh.

Thanks for pointing it out. :)
 
  • #22
galaxy_twirl said:
I got ZA = 26.45 Ohms after working out the above. However, how do I express this in terms of Z = R + jX = R + jωL?

I realized my teacher somehow arrived at 13.23 Ohms for R. How and why did my teacher do that? *puzzled* :S
You said the power factor (which means cos ɸ) is 0.5 here,
so to find the real component of Z you can go 26.45Ω x 0.5
 
Last edited:
  • #23
NascentOxygen said:
You said the power factor (which means cos ɸ) is 0.5 here,
so to find the real component of Z you can go 26.45Ω x 0.5

Ah yes, I forgot for a moment about complex numbers, and hence I couldn't see that I need to convert polar back to rectangular form, which is:

x = rcosθ
y = rsinθ

Thanks for your help! :)
 
  • #24
Finding the real component was straight-forward.

Q: how to determine sin ɸ without needing to determine ɸ itself?
 
Last edited:
  • #25
I am guessing, I have to use the Power Triangle, with Apparent Power, on the HYP, Active power as the base of the triangle and Reactive Power as the vertical of the triangle. The triangle is a right-angled triangle. Am I right? :)
 
  • #26
galaxy_twirl said:
I am guessing, I have to use the Power Triangle, with Apparent Power, on the HYP, Active power as the base of the triangle and Reactive Power as the vertical of the triangle. The triangle is a right-angled triangle. Am I right? :)
All very true, and that's what you will use ...

though doesn't touch on the answer I had in mind. oo)
 
  • #27
NascentOxygen said:
All very true, and that's what you will use ...though doesn't touch on the answer I had in mind. oo)

I see. Haha. :) You may want to share your answer in mind with me, perhaps I may learn something new. :D
 
  • #28
I had in mind Euler's Theorem. Undoubtedly you have studied it in maths, but perhaps not yet related it to engineering. (pronounced OILERS)
 
  • #29
NascentOxygen said:
I had in mind Euler's Theorem. Undoubtedly you have studied it in maths, but perhaps not yet related it to engineering. (pronounced OILERS)

I see. I heard of Euler's formula when learned complex number at A levels, which is, any complex number of the form:

z = a + bi

can be expressed in the form z = re. where r = √(a2 + b2) and θ = tan-1(b/a).

Is this the Euler's Theorem in your mind? :)
 
  • #30
Oops, :oops: what I had in mind is a Pythagorean identity

trig_ID.gif


Using that first one, you can find the magnitude of sine (x) if you already know cosine (x).

(I'm not sure why I decided to credit it to Euler, but Euler has enough to his credit without me heaping more still, even in error.)
 

Similar threads

  • · Replies 26 ·
Replies
26
Views
4K
Replies
19
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 43 ·
2
Replies
43
Views
17K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 2 ·
Replies
2
Views
5K
  • · Replies 35 ·
2
Replies
35
Views
6K