Dismiss Notice
Join Physics Forums Today!
The friendliest, high quality science and math community on the planet! Everyone who loves science is here!

Generator neutral grounding (NGR)

  1. Sep 11, 2014 #1
    Dear All

    here we have two examples of Generator Nuteral Grounding my question about earth switch closing

    Example -1

    if three generators are in operation and one earthing switch is closed, can we close generator-2 or generator-3 earthing switch closed at a time of parallel operation? yes or not ?
    if not please explain in detail

    example 2

    this operation has separate NGR no confusion we can closed individually.
     

    Attached Files:

  2. jcsd
  3. Sep 14, 2014 #2
    I'm sorry you are not finding help at the moment. Is there any additional information you can share with us?
     
  4. Sep 15, 2014 #3

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award


    Why would you want to close more than one ? Any one grounds all generators that are connected to the bus.

    On the other hand, it would hurt nothing provided there are not two simultaneous faults on different machines .

    And the resistor should be sized according to distributed capacitance of however many machines you intend it to serve.
     
Know someone interested in this topic? Share this thread via Reddit, Google+, Twitter, or Facebook




Similar Discussions: Generator neutral grounding (NGR)
  1. Neutral and ground (Replies: 2)

  2. Ground and neutral (Replies: 11)

Loading...