Generator neutral grounding (NGR)

Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
2 replies · 3K views
Asghar Hussain
Messages
3
Reaction score
0
Dear All

here we have two examples of Generator Nuteral Grounding my question about Earth switch closing

Example -1

if three generators are in operation and one earthing switch is closed, can we close generator-2 or generator-3 earthing switch closed at a time of parallel operation? yes or not ?
if not please explain in detail

example 2

this operation has separate NGR no confusion we can closed individually.
 

Attachments

  • DSC04745.JPG
    DSC04745.JPG
    31 KB · Views: 882
Engineering news on Phys.org
if three generators are in operation and one earthing switch is closed, can we close generator-2 or generator-3 earthing switch closed at a time of parallel operation? yes or not ?


Why would you want to close more than one ? Any one grounds all generators that are connected to the bus.

On the other hand, it would hurt nothing provided there are not two simultaneous faults on different machines .

And the resistor should be sized according to distributed capacitance of however many machines you intend it to serve.