Heat pump supply and return temperatures

Click For Summary

Discussion Overview

The discussion revolves around the operational dynamics of an air-water heat pump system used for heating a building via radiators. Participants explore the implications of supply and return water temperatures on system efficiency, radiator sizing, and overall performance, addressing both theoretical and practical aspects of heat pump operation.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Conceptual clarification

Main Points Raised

  • One participant expresses a desire for a high supply temperature of 55°C to minimize radiator size, questioning the impact of lowering the return temperature through pre-heating tap water.
  • Another participant emphasizes the importance of low return water temperatures for both radiator efficiency and heat pump performance, suggesting that high return temperatures could lead to inefficiencies or inadequate heating.
  • A different viewpoint suggests that a high supply temperature with a low delta-T could be beneficial, raising concerns about radiator efficiency at lower temperatures.
  • One participant notes that there are flow and delta-T limitations in refrigerant systems, indicating that vendor literature may provide necessary specifications for optimal operation.
  • Another participant discusses the relationship between supply temperature, air temperature, and heat pump efficiency, suggesting that engineering design may impose additional limits on performance.
  • A proposal is made to consider systems where refrigerant condenses in radiators, highlighting potential advantages and challenges of such an approach.

Areas of Agreement / Disagreement

Participants express differing views on the optimal balance between supply and return temperatures, with no consensus reached on the best approach for maximizing efficiency and performance of the heat pump system.

Contextual Notes

Participants mention various technical limitations, including delta-T constraints, flow rates, and the impact of domestic water heating on overall capacity, which remain unresolved in the discussion.

TSN79
Messages
422
Reaction score
0
A building is to be heated by radiators using an air-water heat pump. While radiators are not the ideal choice, it's beyond my decision making. Naturally I want the supply temp. to be as high as possible, hoping for 55°C in order to keep the physical size of the radiators to a minimum.

As low return temperature supposedly is what every heat pump wants, the return water temperature can be reduced even more by pre-heating tap water through a heat-exchanger before returning to the heat pump. What I wonder is, will this additional reduction in temperature spell doom for my 55°C supply? Is there a maximum temperature difference between the supply and return?
 
Engineering news on Phys.org
You want the return water to be as low a temperature as possible because you want: a) your radiators to be functioning efficiently and heating your building, and b) you want your heat pump to be functioning efficiently and not pumping in unnecessary heat to the system.

By that I mean, if you put X amount of energy into the system and the radiators dissipate Y (a number significantly less than X) then your system is not operating efficiently and you are wasting money by having heated that water up in the first place.

Then there's the issue that if you return water is too hot, two things may happen: a) your heat pump will not have the delta-T required in order to heat the water to the proper temperature, and if it does, it will be operating extremely inefficiently, or b) the heat pump will do it's job, but intstead of having, say, 60 C water to the radiators, you get 80 C water, and so on.

The heat pump acts by adding energy to the system, it has a limit on how much it can add, so yes there is a maximum delta-T which will change based on system conditions.
 
Travis_King said:
You want the return water to be as low a temperature as possible because you want: a) your radiators to be functioning efficiently and heating your building

But isn't a high supply temperature and a low delta T to radiators a good thing? For instance, if the supply temp. is 80C and the return is 70C, the radiator surface would be 75C. If the supply and return temperatures were to be 55/35, a given radiators' Watts would drop significantly, and would have to be physically larger to make up for it - which is of course bad.
 
I haven't done much with waterside heat pumps, but typically there are flow and delta-T limitations on refrigerant systems. Minimum flow rates are common, then a maximum delta-T follows based on the capacity. In addition, there is often a low temperature limit on the incoming water. And, of course, you'll need to account for the extra load of the domestic water heating in the total capacity of the heat pump.

All of this will be discussed in the vendor's literature (engineering literature, not sales literature) and/or can be answered by a good sales engineer. That's what sales engineers are for.
 
TSN79 said:
But isn't a high supply temperature and a low delta T to radiators a good thing? For instance, if the supply temp. is 80C and the return is 70C, the radiator surface would be 75C. If the supply and return temperatures were to be 55/35, a given radiators' Watts would drop significantly, and would have to be physically larger to make up for it - which is of course bad.
Define "good". Physically larger, with higher delta-t means more efficient. And if you have control valves to vary output, it will vary anyway, providing better efficiency at part load.
 
Unless you do the final part of the water heating by desuperheating the refrigerant in the heat pump I would think there would be limited efficiency gain making the return water temperature as low as possible as the lowest condensing temperature still has to be above that of the supply water to get the heat to flow from the condensing refrigerant to the water otherwise the refrigerant won't condense ( it will the condensing pressure/temperature will go up till the system balances) There is only so much high temp discharge temperature (from the compressor) superheat that the refrigerant will have. You would have to plot the refrigerant cycle on a (sorry can't spell PF won't like me) pressure/enalthpy chart to see how much.
 
What I'm saying is it is the supply temp, and the air temp. where it is getting its heat from, which governs the limit on the max possible efficiency of the heatpump. However how the way heat pump is engineered may place additional limits . Real outputs can be gained from sales technical information. A heat pump is able to heat from a low return to relatively high supply, one just reduces the water flow to get it at the expense of reduced total output from the heatpump and reduced efficiency of the heat pump plus there is a limit on the temp. the heat pump can to heat for most standard heat pumps where the life of the heatpump is not reduced.
New inverter heatpumps where the compressor is slowed down at low loads means that there is lower temp. differences between the air and refrigerant, and the refrigerant and water creating a lowest temp. distance that the heat pump has to pump the heat making it more efficient.
 
Maybe we should make systems where refrigerant condenses in a radiator as most split heat pumps (a high wall) have a air off temp. at full throttle mostly at 50 degrees C (assuming a temp. in the room of 23 degrees C)so the refrigerant is condensing hotter about 60 degrees C and you could have the whole radiator at that temp. But one would have to pipe refrigerant all around the place with potential leaks developing. However they pipe refrigerant all around now in complicated variable refrigerant flow air conditioning systems. Be a nicer heat than the pure convective heat from a high wall.
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 4 ·
Replies
4
Views
1K
Replies
1
Views
3K
  • · Replies 15 ·
Replies
15
Views
4K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 6 ·
Replies
6
Views
4K
Replies
6
Views
4K