How can I calculate the usage of a generator for a system?

  • Thread starter Thread starter Harry1984
  • Start date Start date
  • Tags Tags
    Generator System
Click For Summary

Discussion Overview

The discussion revolves around calculating the appropriate KVA rating for a generator to support a reverse osmosis (RO) system, particularly in the context of power fluctuations. Participants explore various methods for determining power requirements based on the system's components and their respective power consumption values.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant requests guidance on selecting a generator for an RO system without providing specific power requirements.
  • Another participant emphasizes the need to know the RO unit's power requirements to assist effectively.
  • Several power consumption values for different pumps are provided, with suggestions to sum these values for total power needs.
  • There is mention of additional power requirements for lights and miscellaneous equipment, with estimates for a bore pump's power needs being uncertain.
  • One participant suggests adding a 30% margin to the calculated generator capacity to account for uncertainty and future expansion.
  • A method involving measuring current with a grip-ammeter is proposed, with a recommendation to convert to KW and add a fudge factor.
  • Concerns are raised about the implications of poor power factor when running multiple small motors, suggesting that KVA ratings may be more appropriate than KW ratings for generators.
  • A participant shares a practical method for connecting generators to the distribution grid, emphasizing simplicity in calculations.

Areas of Agreement / Disagreement

Participants express differing views on the best approach to calculating generator capacity, with no consensus reached on the most effective method or the importance of power factor considerations.

Contextual Notes

Some participants note that the calculations depend on various assumptions, such as the simultaneous operation of all pumps and the accuracy of power utility data. There are also unresolved questions regarding the appropriate conversion between KVA and KW.

Harry1984
Messages
2
Reaction score
0
I've got an RO system and due to power fluctuations I need a generator for it. Can you tell me of what KVA generator should i buy for it and how to go about the calculations. Thank You
 
Engineering news on Phys.org
Moving to EE section...

Welcome to PF! Sure, we can help, but you haven't told us anything about the RO unit's power requirements!

Note: there shouldn't be much, if anything, to calculate here.
 
Thank You Sir.

This is the quotation i got for 5000gallons/day.

There are different pumps to be installed and their respective power consumption values are given.

Kindly help me out in this issue.

Thanks.
 

Attachments

Harry1984 said:
Thank You Sir.

This is the quotation i got for 5000gallons/day.

There are different pumps to be installed and their respective power consumption values are given.

Kindly help me out in this issue.

Thanks.
You need to add up all the power needed for the various components. One of these is not listed (your well pump).

I see:
  • Water feed pump -- 2kW (1.1kW is also listed; use the bigger number)
  • High pressure pump -- 3 kW
  • Pre-dosing pump -- 0.5kW
  • Drip cleaning pump -- 0.55kW
  • Anti-scalant dosing pump -- ?
  • Bore pump (well pump?) -- ?
In addition you will likely want some extra power for lights, small appliances (your laptop) or other miscellaneous gear. Bore pumps vary quite a bit depending on the depth of the well and the amount of water needed. (Remember you will need lots of extra water for backwash, etc. maybe 50,000 gallons extra for a 5,000 gallon output.)

As a rough guess, 2kw. More for a deep well. I would guess the Anti-scalant pump is similar to the regular dosing pump at 0.5W.

This gives a sum of about 10kW. You might have a minor power factor problem with all those motors.

You should be able to find a qualified installer who will sell you a system which integrates with utility power and comes on automatically when the power fails. They will run the numbers for you, but this should give you a ballpark figure.
 
Your power utility should also be able to give you historical data of your own power usage. I say that because there may be loads that aren't mentioned in the RO specifications.

To allow for uncertainty and future expansion, I would add 30% margin to the generator capacity you calculate.

Good luck
 
I connect a lot of generators and use a very simple method

Measure the current drawn using a grip-ammeter (you can do this during the times of highest load if you want) at the intake

Convert to KW, add fudge factor (25%)

done
 
anorlunda said:
Your power utility should also be able to give you historical data of your own power usage. I say that because there may be loads that aren't mentioned in the RO specifications.

To allow for uncertainty and future expansion, I would add 30% margin to the generator capacity you calculate.

Good luck

I like adding 30%.

I would be cautious about using the power company's data. It is unlikely all the pumps are typically on at the same time, thus the numbers could be low. But all the pumps could be on at the same time, so the generator needs to be able to supply that amount.
 
William White said:
I connect a lot of generators and use a very simple method

Measure the current drawn using a grip-ammeter (you can do this during the times of highest load if you want) at the intake

Convert to KW, add fudge factor (25%)

done
My understanding is that you should NOT convert to kW because the generator's limitation is that amperage through the windings, which means that when you have poor power factor (such as when running multiple small motors at part load), you risk burning it out. Perhaps residential generators aren't rated by kva, but I'm pretty sure commercial ones are.

But if anything, calculating the kva and using it as kw would provide the extra safety factor needed if the generator is rated by kw and the max amperage isn't specified.
 
russ_watters said:
My understanding is that you should NOT convert to kW because the generator's limitation is that amperage through the windings, which means that when you have poor power factor (such as when running multiple small motors at part load), you risk burning it out. Perhaps residential generators aren't rated by kva, but I'm pretty sure commercial ones are.

But if anything, calculating the kva and using it as kw would provide the extra safety factor needed if the generator is rated by kw and the max amperage isn't specified.

Correct me if I'm wrong.

It is my understanding that a bad power factor is caused by current being out of phase with voltage. Because the current is out of phase, it does register as power (and isn't power for that matter). But it will still register as current.

William White's measurements should work because he's measuring total current. Where he went wrong is in semantics. He called his measurements kW instead of kVA.
 
  • #10
When I worked in power distribution I connected generators live to the LV distribution grid a lot

There was the complicated way,

and the easy way.

Add up the all the currents in all the phases, divide by 4* and add a bit - and that's the answer in KW (which is what one would ramp the generator up to before closing its breaker onto the grid)

This ALWAYS works, you can do it in your head in a second

One can over-complicate matters. Connecting generators is easy peasy.So, if my grip ammeter read, 50A, 120A and 90A that's 260A, divide by 4

65

add bit

ramp generator up to 75-ish KW

*Assumes 4 amps per KW, which is a good approximation for the UK and allows an easy in your head division (halve you current, then halve it again). In other countries you could have the rule of thumb by dividing by whatever convient number you need.
 
Last edited:

Similar threads

  • · Replies 38 ·
2
Replies
38
Views
6K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 24 ·
Replies
24
Views
3K
Replies
2
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 9 ·
Replies
9
Views
2K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K
Replies
19
Views
3K