Main Points Raised

  • One participant suggests using four 12V batteries connected in series to achieve the required voltage.
  • Another participant clarifies that the -48VDC specification is from the device's datasheet, not the solar panel.
  • A detailed calculation is provided by a participant, outlining the steps to determine the minimum battery size and solar panel requirements based on assumed current and operational hours.
  • Concerns are raised about the high voltage requirement for typical consumer WiFi devices, prompting further calculations regarding battery capacity and solar panel size.
  • Discussion includes the arbitrary nature of selecting ground reference points in DC systems, explaining how to interpret the -48V requirement based on battery connections.
  • References to Power Over Ethernet (PoE) are made, suggesting that the necessary power supply may be included with the device, along with links to relevant documentation.
  • Another participant humorously notes the common use of 48V in stage microphones, indicating a broader context for the voltage standard.

Areas of Agreement / Disagreement

Participants express multiple viewpoints regarding the best method to achieve -48 VDC, with no consensus on a single solution. The discussion remains unresolved as participants explore different approaches and calculations.

Contextual Notes

Participants make various assumptions regarding current draw, operational hours, and charging efficiency, which may affect the calculations presented. The discussion also highlights the importance of understanding the device's specifications and the implications of using different battery types.

dufferdev
Messages
5
Reaction score
0
Hi,

I want to power a wifi device using solar power. But I see the datasheet which has input voltage -48 VDC.

I am confused on how to power this system using battery ?

Any suggestions are welcome.

Thanks a ton...
 
Engineering news on Phys.org
Use 4 12V batteries connected in series
 
f95toli said:
Use 4 12V batteries connected in series

Thanks for your quick reply will try this...
 
Just to be clear...which data sheet specifies 48V? Is it the WiFi device or the solar panel?

Fish
 
Fish4Fun said:
Just to be clear...which data sheet specifies 48V? Is it the WiFi device or the solar panel?

Fish

The -48VDC is specified in the datasheet of the DEVICE and not the solar panel.
 
48Vdc is a lot for a typical consumer WiFi device, but ok. The steps to calculating your system should go like this:

First Determine:

System Voltage = 48V
System Current = ??
System Power Consumption = 48 * I
Number of Hours of Operation Per Day = ??

For now I will Assume:
I = 1A
H = 24 Hours

From here we can determine the minimum battery size:

24 hours * 1A = 24Ah

Next we need to know something about the amount of full sun in the place the device will be located on the Winter Equinox. I will assume this is 4 hours.

You will need to charge the batteries back to at least 24Ah each day. I will assume an 80% charging efficiency, so:

(24Ah / 0.80) * 48V = 1440W / 4hours = 360W

You would need a minimum panel size of 360W @ 48V.

Next you need to evaluate how critical the device is to determine and calculate how long you might want the device to withstand adverse weather conditions. Let's say the device is highly critical, and you want to ensure there are NO interruptions for up to 7 consecutive days of 100% cloud cover.

So, our minimum battery size would be 24Ah * 7days = 168Ah

To charge our 168Ah battery bank, we would want to ensure the batteries could be fully recharged in no more than 4 days of full sun, so:

(168Ah/0.80) + (4 Days * 24Ah) / (4 Days * 4 Hours) = 19.125Ah * 48V = 918W

So, for this level of protection you would need a minimum of 1kW of panels and 210Ah of storage. If you plan on using lead acid batteries, you would want to ensure that you never discharged them more than 50%, so you might use two parallel banks of 4 series connected 210Ah batteries (total of 8 batteries). If you plan on using Lithium Ion batteries rated @ 3.6V & 2.5Ah, you would use 84 parallel connected banks of 14 series batteries (1176 batteries).

The cost of the system is extremely sensitive to actual power consumption and the fault tolerance duration.

For Zero Fault Tolerance, 14 * 2.5Ah Lithium Ion Batteries in series charged by a pair of 180W solar panels might be built for less than $2,000. For the 7 day fault tolerance system, the cost would certainly exceed $15,000. Cutting the power consumption by 25% could easily cut the cost of the system by 50%.

Hope that helps,

Fish
 
Fish4Fun said:
48Vdc is a lot for a typical consumer WiFi device, but ok. The steps to calculating your system should go like this:

First Determine:

System Voltage = 48V
System Current = ??
System Power Consumption = 48 * I
Number of Hours of Operation Per Day = ??

For now I will Assume:
I = 1A
H = 24 Hours

From here we can determine the minimum battery size:

24 hours * 1A = 24Ah

Next we need to know something about the amount of full sun in the place the device will be located on the Winter Equinox. I will assume this is 4 hours.

You will need to charge the batteries back to at least 24Ah each day. I will assume an 80% charging efficiency, so:

(24Ah / 0.80) * 48V = 1440W / 4hours = 360W

You would need a minimum panel size of 360W @ 48V.

Next you need to evaluate how critical the device is to determine and calculate how long you might want the device to withstand adverse weather conditions. Let's say the device is highly critical, and you want to ensure there are NO interruptions for up to 7 consecutive days of 100% cloud cover.

So, our minimum battery size would be 24Ah * 7days = 168Ah

To charge our 168Ah battery bank, we would want to ensure the batteries could be fully recharged in no more than 4 days of full sun, so:

(168Ah/0.80) + (4 Days * 24Ah) / (4 Days * 4 Hours) = 19.125Ah * 48V = 918W

So, for this level of protection you would need a minimum of 1kW of panels and 210Ah of storage. If you plan on using lead acid batteries, you would want to ensure that you never discharged them more than 50%, so you might use two parallel banks of 4 series connected 210Ah batteries (total of 8 batteries). If you plan on using Lithium Ion batteries rated @ 3.6V & 2.5Ah, you would use 84 parallel connected banks of 14 series batteries (1176 batteries).

The cost of the system is extremely sensitive to actual power consumption and the fault tolerance duration.

For Zero Fault Tolerance, 14 * 2.5Ah Lithium Ion Batteries in series charged by a pair of 180W solar panels might be built for less than $2,000. For the 7 day fault tolerance system, the cost would certainly exceed $15,000. Cutting the power consumption by 25% could easily cut the cost of the system by 50%.

Hope that helps,

Fish


Hello Fish,

Thanks for your support and help.

However, I am clear on the solar calculation.

I want to know how to generate minus (- 48VDC) which is stated in the wifi device datasheet ?
 
It might be best if you posted the data sheet to determine what the -48V reference is to, but in general, a DC device has two supply inputs. Choosing which is "ground" is fairly arbitrary. If you select the positive terminal of a 48V battery as "ground", then the negative terminal, by definition is -48V. If you select the negative terminal as "ground" then the positive terminal is, by definition +48V. If there is some Voltage Reference, and relative to that reference you need -48V, then you simply connect the positive terminal of the battery to that reference point.

Fish
 
Fish4Fun said:
It might be best if you posted the data sheet to determine what the -48V reference is to, but in general, a DC device has two supply inputs. Choosing which is "ground" is fairly arbitrary. If you select the positive terminal of a 48V battery as "ground", then the negative terminal, by definition is -48V. If you select the negative terminal as "ground" then the positive terminal is, by definition +48V. If there is some Voltage Reference, and relative to that reference you need -48V, then you simply connect the positive terminal of the battery to that reference point.

Fish

Thanks for your reply fish, I have attached the datasheet here
 

Attachments

  • #10
  • #11
  • #12
PoE, Power Over Internet,

I wish. Can I have some too?

Interestingly 48 volts is the standard phantom power supply for stage microphones.
 
  • #13
Studiot said:
I wish. Can I have some too?

Interestingly 48 volts is the standard phantom power supply for stage microphones.

ooops...PoE => Power Over Ethernet

I got the link right, by my dyslexic brain transposed Internet for Ethernet...

Fish
 
  • #14
Studiot said:
[...]Interestingly 48 volts is the standard phantom power supply for stage microphones.

-48V is also the DC supply voltage on phonelines. I wonder where else this might be used?

To the OP, if you Google for solar POE, there are various [strike]hobbiest[/strike] hobbyist project pages and commercialish devices that may help with that aspect of the problem.

EDIT: Fixed that for me...
 
Last edited:
  • #15
MATLABdude said:
-48V is also the DC supply voltage on phonelines. I wonder where else this might be used?...

also on telephone systems in NZ and Australia and its almost universally used on much RF telecomm's equip world wide and has been since Adam was a boy ;)

Dave
 
  • #16
Telephone exchanges used to have vast banks of -48V battery supply and backup, on float charge, for the 'old fashioned' switching and signalling circuits. Using the same supply voltage for other electronic equipment would make a lot of sense as you'd have a built in UPS for the electronics. I can't think that -48V would be a good idea under any other circs where 12V and 5V are the most common power supply voltages. All the internal devices would use these lower voltages, after all.
It makes me wonder why not use a different, more convenient WIFI modem?
 

Similar threads

Replies
8
Views
2K
  • · Replies 18 ·
Replies
18
Views
3K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
30
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
3K
Replies
61
Views
10K
Replies
6
Views
4K
  • · Replies 38 ·
2
Replies
38
Views
5K
  • · Replies 8 ·
Replies
8
Views
3K