How Do You Calculate Armature Current and Efficiency in a DC Shunt Motor?

Click For Summary
SUMMARY

The discussion focuses on calculating the armature current and efficiency of a 20 kW, 500 V DC shunt motor. The armature current at full load is determined to be 42.7 A after accounting for the field current of 2.3 A. When the torque is reduced to half, the armature current decreases to 21.35 A, resulting in an increased speed of 608 rev/min. The efficiency at half torque is calculated to be 80%, considering total losses including fixed losses and field losses.

PREREQUISITES
  • Understanding of DC motor principles
  • Knowledge of electrical power calculations
  • Familiarity with efficiency and loss calculations in electrical machines
  • Basic grasp of armature and field current relationships
NEXT STEPS
  • Study the impact of armature resistance on motor performance
  • Learn about fixed losses in DC motors and their calculation
  • Explore the relationship between back EMF and motor speed
  • Investigate methods for improving motor efficiency
USEFUL FOR

Electrical engineers, students studying motor control, and professionals involved in the design and analysis of DC motors will benefit from this discussion.

zsolt2
Messages
19
Reaction score
2

Homework Statement


Hello I have a bit of a problem solving this
A 20 kW, 500 V d.c. shunt wound motor draws a current of 45 A when running at full load with a speed of 600 rev min–1. On no load, the current drawn from the supply is 5 A. If the armature resistance is 0.3 Ω and the shunt field resistance is 220 Ω, calculate the armature current, speed and efficiency of the motor when the torque falls to half of its full load value, assuming that the flux per pole does not change.

Homework Equations


Armature current: Ia=20000/500=40A
Field current= 500/220=2.3A

The Attempt at a Solution


Now first i don't understand where is the missing 2.7A or is the field current=5A?
If the torque falls half of its value the armature current falls to half as well Ia=20A
Speed:
On full load E=V-Ia x Ra=500- 40 x 0.3=488V
When Ia falls to half= E=500-20 x 0.3=494V
if the back e.m.f. increases the speed increases: 494/488=1.012 new speed= 600 x 1.012=607 rev/min
Efficiency:
V x Ia=Ia^2 x Ra + E x Ia
500 x 20=20^2 x 0.3 + 494 x 20=10000W

Can anyone tell me if I am right so far
Thank you
 
Physics news on Phys.org
zsolt2 said:
Now first i don't understand where is the missing 2.7A
zsolt2 said:
Armature current: Ia=20000/500=40A
That's not correct.
5kW is the mechanical power output of the motor and not electrical power input.
zsolt2 said:
Field current= 500/220=2.3A
That's 2.2728 A(≈2.3 A).
So the armarure current would be simply supply current minus field current.
 
  • Like
Likes   Reactions: zsolt2
Thank you for your answer!

So the armature current Ia=45-2.3=42.7
Then the power=V x Ia=500 x 42.7=21350W
And that 1350W is a fixed lost?
Ia on half torque = 42.7/2=21.35A
Speed:
On full load
E=V-ia x Ra=500-42.7 x 0.3=487V
Half torque
E=500-21.35 x 0.3=494V
The speed increases if the back e.m.f. grows (Ia decreases) 494/487=1.014
n2=n1 x 1.014=600 x 1.014=608 rev/min
 
zsolt2 said:
Thank you for your answer!

So the armature current Ia=45-2.3=42.7 A
Ia on half torque = 42.7/2=21.35A
Speed:
On full load
E=V-ia x Ra=500-42.7 x 0.3=487V
Half torque
E=500-21.35 x 0.3=494V
The speed increases if the back e.m.f. grows (Ia decreases) 494/487=1.014
n2=n1 x 1.014=600 x 1.014=608 rev/min
Looks good!
 
  • Like
Likes   Reactions: zsolt2
Thank you!
And the efficiency :
Total power used: V x Ia = 500 x 21.35= 10675W
Losses:
Armature loss: Ia^2 x Ra =21.35^2 x 0.3=136.7W
Field loss: If^2 x Rf= 2.3^2 x 220=1163.8W
Brush losses: 2 x Ia= 2 x 21.35=42.7W
Fixed loss: 1350W
All losses:136.7+1163.8+42.7+1350=2693.2W
Is that looks right?
 
zsolt2 said:
And that 1350W is a fixed lost?
I didn't qoute this part in my previous post. You should use the no load data to find the fixed loss.
zsolt2 said:
Brush losses: 2 x Ia= 2 x 21.35=42.7W
You need not take brush drop into account if it is not mentioned in the problem.
 
  • Like
Likes   Reactions: zsolt2
Ok
So the current drawn on no load is 5A the power consumed is 500 x 5=2500W
Field loss is 2.3^2 x 220=1163.8~ 1164W
Then the fixed loss: 2500-1164=1336W
Efficiency at half torque :
10675/10675+1336+1164+137=0.8
Efficiency =80%
 
zsolt2 said:
Then the fixed loss: 2500-1164=1336W
To be accurate, you should also subtract armature copper loss from this. Usually, because of low armature resistance, armature copper loss is neglected on no load but here, since nothing is mentioned as such, you should calculate it.
 
  • Like
Likes   Reactions: zsolt2
Ok thank you very much for the help!
 
  • Like
Likes   Reactions: cnh1995

Similar threads

  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 13 ·
Replies
13
Views
3K
  • · Replies 14 ·
Replies
14
Views
5K
  • · Replies 41 ·
2
Replies
41
Views
7K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
6
Views
4K
  • · Replies 2 ·
Replies
2
Views
2K