How does a Synchronous condenser shift the phase

Click For Summary
Over-excitation of a synchronous motor or under-excitation of a synchronous generator alters the phase relationship between current and voltage, shifting the power factor to leading. This occurs as changes in excitation modify the magnitude and phase of the resultant electromotive force (emf), affecting the armature current. The phase difference between the resultant emf and armature current leads to a change in the power factor angle, while the active component remains constant under unchanged loading conditions. Understanding these dynamics is simplified by using the D-Q (direct and quadrature) transformation framework. The armature reaction flux vector primarily influences the impedance magnitude, not the phase shift directly.
tim9000
Messages
866
Reaction score
17
Hi,
So when you over-excite the rotor of a synchronous motor, or under-excite the rotor of a synchronous generator, how is the flux actually changing the power factor of the armature to leading? (something to do with the magnitude of the armature reaction flux vector?)
That is to ask: by what mechanism does this modify the relation of the current to the voltage waveforms?

Pictures welcome.

Cheers!
 
Engineering news on Phys.org
tim9000 said:
Hi,
So when you over-excite the rotor of a synchronous motor, or under-excite the rotor of a synchronous generator, how is the flux actually changing the power factor of the armature to leading? (something to do with the magnitude of the armature reaction flux vector?)
That is to ask: by what mechanism does this modify the relation of the current to the voltage waveforms?

Pictures welcome.

Cheers!
The current flowing through the motor (Iph or Iaph) is due to the resultant emf i.e. vector sum of stator voltage applied(Vph) and back emf Eb.
images?q=tbn:ANd9GcSMwZ3lEGu84tDmQI6AMjEHij62cGqC16iL8OZa1L0FlbUBTXYs.png

When the excitation is changed, length of Eb vector changes (and Vph is constant throughout). This changes the magnitude as well as phase of the resultant emf. You can see it in the phasor diagram. There is a phase difference of θ(≅90°) between Er and Iph. So, as the Er vector changes its phase, I am vector is dragged along with it, thereby changing the power factor angle. Magnitude of I am also changes as magnitude of Er has changed (Er=Im*Zs) and it changes in such a way that its active component remains constant i.e. Im*cosΦ is constant since the loading condition is unchanged.
So, to summarize,
Change in excitation changes the phase angle of the opposing emf→Hence, the angle between resultant emf and supply voltage(Vph) changes. →As I am and Er have fixed phase difference, I am is modified as per the magnitude and position of Er→This changes the angle between I am and Vph(Vph is fixed)→This changes the p.f.
 
Last edited:
tim9000 said:
something to do with the magnitude of the armature reaction flux vector?
I believe armature reaction flux vector only determines the magnitude of Zs.
 
Last edited:
The secret to understanding synchronous machines is to shift your reference frame to the D-Q (direct and quadrature) axes. Everything becomes magically simpler and easy to understand in that frame.

https://en.wikipedia.org/wiki/Direct–quadrature–zero_transformation

Unfortunately, that Wikipedia article is not very good. Other PF regulars, maybe Jim Hardy, can think of a better reference for you to study.
 
I am trying to understand how transferring electric from the powerplant to my house is more effective using high voltage. The suggested explanation that the current is equal to the power supply divided by the voltage, and hence higher voltage leads to lower current and as a result to a lower power loss on the conductives is very confusing me. I know that the current is determined by the voltage and the resistance, and not by a power capability - which defines a limit to the allowable...

Similar threads

Replies
1
Views
3K
  • · Replies 4 ·
Replies
4
Views
4K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 8 ·
Replies
8
Views
13K
  • · Replies 2 ·
Replies
2
Views
1K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
2
Views
9K
  • · Replies 5 ·
Replies
5
Views
3K