Is it true that AC synchronous motors (the ones with the DC slip rings and excitation current running into rotor poles) have a power factor of 1.0 when they run in synchronous mode?
Would that be because with sufficient rotor DC current he rotating AC magnetic field is precisely counterbalanced so there is almost no induction and the incoming stator winding AC "sees" an almost resistive load instead of an inductive load like in a transformer or an induction motor?
can I say that in a sense the synchronous motor is like a magnetic amplifier (saturable reactor)


thanks
 

Answers and Replies

  • #2
anorlunda
Staff Emeritus
Insights Author
10,850
8,151
The power factor is adjustable by changing the exciter voltage. So you can have almost any power factor you want.

The picture shows the capability curve for a synchronous generator. It's the same for a synchronous motor. The point where VARs are zero and power factor is one is neither overexited or underexcited. It doesn't have a name but you can call it "just right" or maybe "excited to perfection". :biggrin:


loss-of-excitation-22-638.jpg
 

Attachments

  • loss-of-excitation-22-638.jpg
    loss-of-excitation-22-638.jpg
    71.4 KB · Views: 3,686
  • #3
girts
186
19
so I guess due to all the capacitive filters in power supplies and smps , the generators of today are rather overexcited then underexcited? to make the sine wave with a steeper climb in order to balance out the lagging current right?
 
  • #4
Windadct
1,433
400
You need to overexcite enough to compensate for the typical lagging PF on the grid (total load) as a whole.
 
  • #5
anorlunda
Staff Emeritus
Insights Author
10,850
8,151
so I guess due to all the capacitive filters in power supplies and smps , the generators of today are rather overexcited then underexcited? to make the sine wave with a steeper climb in order to balance out the lagging current right?

For the bulk power grid (think continental scale), the inductance and capacitance of the transmission lines are more significant than the L or C components of the loads.
 

Suggested for: AC synchronous motor power factor

  • Last Post
Replies
3
Views
5K
  • Last Post
Replies
1
Views
168
Replies
55
Views
5K
  • Last Post
Replies
3
Views
2K
  • Last Post
Replies
13
Views
26K
  • Last Post
Replies
2
Views
7K
Replies
9
Views
13K
  • Last Post
Replies
1
Views
5K
  • Last Post
Replies
11
Views
4K
  • Last Post
Replies
22
Views
2K
Top