AC synchronous motor power factor

In summary: So the power factor of the overall grid depends mostly on the inductive or capacitive nature of the transmission lines. In summary, AC synchronous motors have a power factor of 1.0 in synchronous mode due to the precise counterbalance of the rotating AC magnetic field and adjustable exciter voltage. Generators today are typically overexcited to compensate for lagging power factor on the grid.
  • #1
girts
186
22
Is it true that AC synchronous motors (the ones with the DC slip rings and excitation current running into rotor poles) have a power factor of 1.0 when they run in synchronous mode?
Would that be because with sufficient rotor DC current he rotating AC magnetic field is precisely counterbalanced so there is almost no induction and the incoming stator winding AC "sees" an almost resistive load instead of an inductive load like in a transformer or an induction motor?
can I say that in a sense the synchronous motor is like a magnetic amplifier (saturable reactor)thanks
 
Engineering news on Phys.org
  • #2
The power factor is adjustable by changing the exciter voltage. So you can have almost any power factor you want.

The picture shows the capability curve for a synchronous generator. It's the same for a synchronous motor. The point where VARs are zero and power factor is one is neither overexited or underexcited. It doesn't have a name but you can call it "just right" or maybe "excited to perfection". :biggrin:
loss-of-excitation-22-638.jpg
 

Attachments

  • loss-of-excitation-22-638.jpg
    loss-of-excitation-22-638.jpg
    36.8 KB · Views: 3,871
  • Like
Likes cnh1995
  • #3
so I guess due to all the capacitive filters in power supplies and smps , the generators of today are rather overexcited then underexcited? to make the sine wave with a steeper climb in order to balance out the lagging current right?
 
  • #4
You need to overexcite enough to compensate for the typical lagging PF on the grid (total load) as a whole.
 
  • Like
Likes jim hardy
  • #5
girts said:
so I guess due to all the capacitive filters in power supplies and smps , the generators of today are rather overexcited then underexcited? to make the sine wave with a steeper climb in order to balance out the lagging current right?

For the bulk power grid (think continental scale), the inductance and capacitance of the transmission lines are more significant than the L or C components of the loads.
 
  • Like
Likes cnh1995

1. What is the power factor of an AC synchronous motor?

The power factor of an AC synchronous motor is a measure of how efficiently the motor is converting electrical energy into mechanical energy. It is a dimensionless number between 0 and 1, with a higher power factor indicating a more efficient motor.

2. How is power factor related to the efficiency of an AC synchronous motor?

The power factor is directly related to the efficiency of an AC synchronous motor. A higher power factor means less energy is being wasted and more of the electrical energy is being used to power the motor's mechanical output.

3. What factors can affect the power factor of an AC synchronous motor?

The power factor of an AC synchronous motor can be affected by factors such as the motor's design, load, and operating conditions. For example, a heavily loaded motor will typically have a lower power factor than a lightly loaded motor.

4. How can the power factor of an AC synchronous motor be improved?

To improve the power factor of an AC synchronous motor, it is important to match the motor's load to its rated capacity. Installing power factor correction equipment, such as capacitors, can also help to improve the power factor.

5. What are the advantages of a high power factor in an AC synchronous motor?

A high power factor in an AC synchronous motor has several advantages. It can lead to lower energy costs, improved motor performance and efficiency, and reduced strain on the motor and other electrical equipment in the system.

Similar threads

  • Electrical Engineering
Replies
18
Views
2K
  • Electrical Engineering
Replies
3
Views
816
  • Electrical Engineering
Replies
8
Views
1K
Replies
14
Views
3K
  • Electrical Engineering
Replies
2
Views
591
  • Electrical Engineering
Replies
1
Views
1K
Replies
1
Views
947
  • Electrical Engineering
Replies
13
Views
3K
  • Electrical Engineering
Replies
6
Views
3K
  • Electrical Engineering
Replies
5
Views
973
Back
Top