How Does Power Transfer to a Capacitor in a High-Voltage RC Circuit?

Click For Summary

Discussion Overview

The discussion revolves around the power transfer to a capacitor in a high-voltage RC circuit, specifically focusing on the charging dynamics of a capacitor bank connected to a step-up transformer and the associated calculations. Participants explore the implications of transformer ratings, resistance, and charging rates in this context.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant describes a circuit setup involving a step-up transformer, full bridge rectifier, charging resistor, and capacitor bank, seeking clarity on the charging process and calculations.
  • Another participant notes that the transformer produces a peak voltage of 2828 volts, suggesting the capacitor should be rated higher for safety.
  • Concerns are raised about the secondary resistance of the transformer and its impact on the charging time constant, with calculations indicating a time constant of about 2.2 seconds.
  • There is a discussion about the nature of the charging process, indicating that the capacitor charges in bursts rather than continuously, which affects the overall charging time.
  • One participant questions the relationship between the charging power and the specifications provided by the manufacturer, particularly regarding the power factor and effective power calculations.
  • Another participant clarifies that 600 joules per second is equivalent to 600 watts, but emphasizes that the actual current decreases as the capacitor charges, providing a simulation result showing varying current values during the charging process.
  • Calculations are presented regarding the charge in the capacitor, average current, and efficiency of the charging process, highlighting discrepancies in expected versus actual performance.

Areas of Agreement / Disagreement

Participants express differing views on the calculations and implications of the transformer ratings, secondary resistance, and charging dynamics. There is no consensus on the exact relationships or calculations, indicating ongoing uncertainty and debate.

Contextual Notes

Participants mention various assumptions, such as the nature of RMS values and the impact of series resistance on charging time, without resolving these complexities. The discussion reflects a range of calculations and interpretations that may depend on specific circuit conditions.

Who May Find This Useful

This discussion may be useful for individuals interested in high-voltage circuits, capacitor charging dynamics, and the practical application of electrical engineering principles in transformer-based systems.

Nash78
Messages
20
Reaction score
0
Hi, Me again.

I have been tasked to replace a step up power transformer in a machine.
But i just can't get the answers i need after much thinking.

In a simplistic RC circuit, there are 4 items
DC Power source (Normally voltage driven)
Switch (On/Off the circuit)
Resistor
Capacitor

All are in series right?

In my simplified circuit.

1) Step up transformer (Pri230V:Sec2000V, 16A:1.84A, Single Phase, 50Hz)
2) Full Bridge Rectifer
3) Charging Resistor, 33 ohms
4) Capacitor Bank, 2000Vdc@ 2000uF, total energy rated 4000J

An SCR will turn on power to the transformer which in turn transfers power to the capacitors for charging till 2000Vdc.

My doubt is, this setup is able to charge the capacitor up at 600J/sec as stated by the manufacturer. The specifications are quite accurate. Normally it finishes before 6 seconds on my stopwatch.

I tried the few calculations but it didn't work out,

1) 2000V source with 33 ohms, RC constant does not work out right.
2) Using a source of 1.84A with 33 ohms, it does not work out right either.

Is my direction correct?:cry:
 
Engineering news on Phys.org
That transformer would give a peak voltage of 2828 volts and the capacitor would charge up to this voltage. So, the capacitor should be rated to at least this voltage and probably 3500 volts for a safety factor.

The secondary resistance of the transformer is not given but it might be as high as 1086 ohms (2000 V / 1.84 A). You would have to consider this in series with the 33 ohm charging resistor.
Using those figures, the time constant would be about 2.2 seconds. ( 2000 uF * 0.001119 Mohms)

Also, the capacitor is not being charged continuously. It is getting a series of bursts of charge with each rectified mains cycle.
So, it would take longer than if the source was constant DC.
 
Hi,

I assume 230V would already be the rms value going into the primary side, so output should still be 2000V instead of 2828V, yah? There is a feedback circuit which cuts off the SCR signal, so overcharging is well taken of.

So, the secondary resistance plays a big part in the calculations? I will measure it and calculate again.

Thanks,
Nash78
 
The 230 volts and 2000 volts are RMS values so you have to multiply them by 1.414 (square root of 2) to get the peak values.
So, the 2000 volts RMS will rectify and give pulsing DC with peaks at 2828 volts.

Actually, the 2000 volts is AT 1.84 amps, so it may be higher off load.

Yes, it would be worth measuring the resistance of the secondary. It is probably fairly high compared with your 33 ohm charging resistor.

This graph is for 1000 ohms series resistance and 2000 uF but 60 Hz input frequency. I tried 50 Hz and it didn't make any difference.

attachment.php?attachmentid=22931&d=1262939471.png
 

Attachments

  • capacitor charging.PNG
    capacitor charging.PNG
    14.8 KB · Views: 673
Any idea on what relation this has with the charging power?

I can't relate these two things together.

Let's say i measure the secondary resistance and get a calculated answer close to what i see in practical. The charging of the bank completes 2000Vdc within 6 secs. I did the test many times to make sure of it.

Manufacturer states it charges 600Joules per sec, is it equal to 600W?
Bank = 4000J
So calculations show ~5 secs.

The stepup transformer has a power of 230V x 16A = 3680VA
Effective power = 3680 x Power Factor = 600W
That is a very low power factor is my equations are correct.

Am i missing something?
 
600 joules / second is the same as 600 watts.

However, you can't take the rating of the transformer and say this is the current being used.

The actual current decreases as the capacitor charges up. My simulation shows it as starting at 2.8 amps and dropping to about 0.7 amps at the 6 second point. These are peak values.
Eventually, the current would drop to zero.

The capacitor has 4 coulombs of charge in it. (2000 V * 0.002 Farads). (Q = C * V)
So the average current to charge it was 4 coulombs / 6 seconds = 0.666 amps (Q = I * t)

So loss in 1000 ohms series resistor = I * I * R = .66 * .66 * 1000 = 443 watts or 443 joules / second.

Charge in capacitor = 0.5 * V * V * C = 0.5 * 2000 V * 2000 V * 0.002 F = 4000 joules

Charging rate = 4000 joules / 6 seconds = 666.6 joules / sec

Efficiency = (666.6 / 666.66 + 443) *100 = (666.6 / 1109.6) *100 = 60 %
 
Wow . . . . that's the BIG difference between just "knowing" and "knowing how to apply what u learnt"

I guess my constant snoozing during classes proved 1 thing.
10% knowledge and 90% crap

Thanks man.
 

Similar threads

  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 17 ·
Replies
17
Views
3K
Replies
12
Views
3K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 6 ·
Replies
6
Views
8K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 10 ·
Replies
10
Views
5K
Replies
5
Views
3K
Replies
7
Views
8K
  • · Replies 4 ·
Replies
4
Views
3K