How far can a motor be overloaded?

  • Thread starter Thread starter kyaw min
  • Start date Start date
  • Tags Tags
    Motor
AI Thread Summary
Using a 37kW AC motor instead of a 40kW motor is possible, but it requires careful consideration of power calculations and potential underestimation of load requirements. Most motors have a service factor (SF) of 1.15, allowing them to handle short-term overloads, but relying on this can compromise safety and motor lifespan. The cost difference between the two motors is minimal compared to the operational costs, making it unwise to skimp on motor size. Continuous operation above the rated load can lead to inadequate performance and potential damage. Properly sizing the motor is crucial for ensuring reliability and efficiency in operation.
kyaw min
Messages
1
Reaction score
0
According to the caculation, we need a 40kW 3 phase AC asychorne motor. Could we use 37kW AC motor instead of 40kW? If yes, what kind of precautions have to be taken?

thanks
 
Engineering news on Phys.org
I don't know what kind of calculations you did, but are you sure you didn't understimate the power requirement?
If you ignored things like friction and people holding it with their fingers then you might prefer something higher than 40 kW instead?
 
Most motors have a service factor of 1.15, meaning they can be run for shot durations at 115% of nameplate rating. But as CompuChip suggested, you're not giving yourself any safety factor and you really should ask yourself just how confident you are in your calcs and whether the peace of mind and assurance of lifespan of having a properly sized motor is worth the extra 5% cost.

Put another way, the cost difference between the two motors is equivalent to the cost of the first four days of running the motor (assuming it runs 24 hrs a day). So is it really worth it to skimp?
 
Service factor (SF) is an indication of how much overload a motor can withstand when operating normally within the correct voltage tolerances. For example, the standard SF for open drip-proof (ODP) motors is 1.15. This means that a 10-hp motor with a 1.15 SF could provide 11.5 hp when required for short-term use. Some fractional horsepower motors have higher service factors, such as 1.25, 1.35, and even 1.50. In general, it's not a good practice to size motors to operate continuously above rated load in the service factor area. Motors may not provide adequate starting and pull-out torques, and incorrect starter/overload sizing is possible.
Traditionally, totally enclosed fan cooled (TEFC) motors had an SF of 1.0, but most manufacturers now offer TEFC motors with service factors of 1.15, the same as on ODP motors. Most hazardous location motors are made with an SF of 1.0, but some specialized units are available for Class I applications with a service factor of 1.15.

--------------------------------
Creative thinking is breezy, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...
Back
Top