  • #1
1
0

Main Question or Discussion Point

cable size calculation
between QRM and 11kv to 400v transformer (1500 kva)
 

Answers and Replies

  • #2
8,245
5,064
  • #3
jim hardy
Science Advisor
Gold Member
2019 Award
Dearly Missed
9,839
4,868
What's a QRM?


Is your cable copper or aluminum, is it run in air or in conduit, and if buried what is thermal conductivity of earth covering it?
What is temperature rating of your insulation ?

That's why we have electrical codes, so that one avoids 'beginner's mistakes' .
 
  • #4
427
119
QRM has many meanings, I agree with you Jim. Anyway, in my opinion, the o.p. is
referring to Quadrilateral Ring Main Unit. RMU (Ring Main Unit) is of two types. TRM (Triangular Ring Main Unit) & QRM (Quadrilateral Ring Main Unit). TRM is (2 Feeder+ 1 Transformer Feeder) and QRM is (2 Feeder + 2 Transformer Feeder). RMU is mainly used for redundancy of feeders.
So, a sketch it could explain more.
upload_2018-6-21_9-17-16.png


The short-circuit current will state the cable cross-section area. If you know the circuit breaker short-circuit rated current then you may use the NEC Table 240.92(B) Tap Conductor Short-Circuit Current Ratings.[for copper conductor]:
A=I/SQRT(0.0297*LOG10((T2+234)/(T1+234))/t) where:
I = short-circuit current in amperes
A = conductor area in circular mils
t = time of short circuit in seconds (for times less than or equal to 10 seconds)
T1 = initial conductor temperature in degrees Celsius.
T2 = final conductor temperature in degrees Celsius.
T1=75oC usually T2=250oC for XLPE or EPR conductor insulation.
Let's say I=20000 A T2=250oC t=1 sec T1=75oC then A= A=26300 cmls [=135 mm^2].
 

Attachments

  • #5
jim hardy
Science Advisor
Gold Member
2019 Award
Dearly Missed
9,839
4,868
If you know the circuit breaker short-circuit rated current then you may use the NEC Table 240.92(B) Tap Conductor Short-Circuit Current Ratings.[for copper conductor]:
What an excellent answer !
 
  • #6
427
119
Thank you Jim.
Thank you very much indeed !
 

Related Threads on How to calculate the cable size between QRM and transformer

  • Last Post
Replies
6
Views
14K
  • Last Post
Replies
6
Views
10K
Replies
1
Views
2K
  • Last Post
Replies
2
Views
24K
  • Last Post
Replies
11
Views
2K
Replies
1
Views
831
Replies
4
Views
3K
  • Last Post
Replies
7
Views
6K
Replies
12
Views
16K
Top