How to conduct continuity test for cable sized 250 sq. mm?

  • Thread starter xiv_wolf
  • Start date
  • #1
7
0

Main Question or Discussion Point

Good day everyone!

I would like to ask if it's ok to use a digital or analog multi-tester in testing a 15 meters, 250 sq.mm cable? We are tracing buried cables from the main circuit breaker to the concrete post. We are connected to Delta X'mer, 230 V, 4 wire w/ ground System. The x'mer will not be connected to the system while testing. I've attached the schematic diagram of the proposed method of testing. I appreciate any suggestions/recommendations. Thank you very much.

2lw86bp.jpg
 

Answers and Replies

  • #2
247
1
If the purpose of the continuity test is to verify which cable is which, then a VOM (digital or analog) will certainly do the job. If you have known, or suspect issues with the integrity of the cables then you should consider more robust testing methods suggested and approved by a certified engineer. 500kVA is a lot of current, and demands rigid compliance with codes and safety guidelines.

Fish
 
  • #3
7
0
Thanks for the reply Fish4Fun! We're conducting continuity test to verify which cable is which so that the provider of x'mer can connect the correct cable for each phase. When the provider initially connects all the 4 wires of each phase, the fuse cut-out of the x'mer tripped off. We are instructed to determine the correct groupings of the cable because all of the markings have been erased. The Electrical Engineer of the building has passed away and the blue print that left is quietly old.
 
  • #4
davenn
Science Advisor
Gold Member
2019 Award
9,193
7,373
ok You have stated ALL power is disconnected!!!

so you dont have to extend the meter leads between the far ends of the cables.
At the top of the post end in the first group of 4 conductors strap a pair of them together
at the main panel board end look for a s/c between a pair of cables in that group
you can then use that to identify the other 2 cables of the group.
Once those 2 cables have been marked you can remove the short between the the initial 2 you shorted together and identify them individually using a short between one of them and one of the 2 marked cables.
10 minute job ... piece of cake :)

Dave
 
  • #5
634
1
Dave's idea seems pretty good. We did that once.

You could also try connecting the cables to a voltage source one at one side and measure the voltage on the other side. Maybe use a car battery. Two wires one to + and other to -ve terminal of battery. Measure the voltage on the other side and you'll have a match.
 

Related Threads on How to conduct continuity test for cable sized 250 sq. mm?

  • Last Post
Replies
11
Views
2K
Replies
5
Views
1K
  • Last Post
Replies
7
Views
6K
  • Last Post
Replies
6
Views
14K
  • Last Post
Replies
6
Views
10K
  • Last Post
Replies
5
Views
1K
  • Last Post
Replies
11
Views
13K
Replies
21
Views
4K
Replies
2
Views
7K
  • Last Post
Replies
4
Views
1K
Top