How to stop insulation from floating when flooded

  • B
  • Thread starter CWatters
  • Start date
  • #1
CWatters
Science Advisor
Homework Helper
Gold Member
10,533
2,298
Elsewhere someone is planning to install Under Floor Heating (UFH) in a house that is prone to flooding. UFH systems typically comprise a layer of insulation then a layer of concrete screed with UFH pipes in it.

Given this recent news story http://www.dailymail.co.uk/news/art...th-car-park-float-raises-floor-four-feet.html I'm trying to work out what thickness of screed you need to stop the insulation floating.

I think I've done the sums right but perhaps someone could check them for me?

The buoyancy force is equal to the weight of water displaced by the insulation and screed...

Water weighs 1000kg per m^3. If Ti and Ts are the thickness of the insulation and screed in mm and g = acceleration due to gravity, then the buoyancy force per square meter is..

= 1000 * g * (Ti + Ts)/1000
= g * (Ti + Ts) N/m^2

Insulation is very light so I'll ignore it's weight. Screed weighs about 2200 kg per m^3 so the downward force due to the weight of the screed is about

= 2200 * g * Ti /1000
= 2.2 * g * Ti N/m^2

The latter must be greater than the former to stop it floating so

2.2 * g * Ti > g * (Ti + Ts)
g cancels
2.2 * Ti > Ti + Ts
rearrange to give
Ts > 0.83 Ti
so the screed must be at least 0.83 times the thickness of the insulation.

If the insulation was 200mm thick the screed would need to be 0.83 * 200 = 166mm thick to stop it floating in a flood.

I've ignored the fact that there is UFH pipe in the screed making it lighter.

Any mistakes?
 

Answers and Replies

  • #2
jbriggs444
Science Advisor
Homework Helper
9,802
4,409
Looks good.

It passes the sanity check: 1 meter of insulation plus 0.83 meters of screed would be to 0.83 * 2200 ~= 1830 kg per square meter. By no coincidence, 1.83 meters of water is also 1830 kg per square meter.
 
  • #4
CWatters
Science Advisor
Homework Helper
Gold Member
10,533
2,298
Thanks folks.
 

Related Threads on How to stop insulation from floating when flooded

  • Last Post
Replies
4
Views
1K
  • Last Post
Replies
2
Views
965
Replies
5
Views
1K
Replies
4
Views
899
Replies
5
Views
1K
  • Last Post
Replies
19
Views
796
  • Last Post
Replies
5
Views
3K
Replies
12
Views
6K
Top