In order to do some welding a long way from a power socket, I have made up a 200m long ‘extension lead’ from some 6mm2 armour cable. The cable is needed for another job later on.
I have an test unit that:
1. Checks earth/ground bond with 8Vac and 25A.
2. Then measures insulation resistance between L+N and Earth at 1250Vac.
The Earth test passed, but the IR test failed (trip at 4mA).
However, when I repeated the IR test using a 1000Vdc (another tester - I like testers) the test passed (IR >10Gohm).
Why? I see two possibilities:
1. 1250Vac has a much higher peak voltage than the DC 1000V.
2. The ac test was affected by wire-wire capacitance.