Discussion Overview

The discussion revolves around understanding wattmeter measurements in a 3-phase AC motor system, specifically in a Delta configuration. Participants explore the implications of connecting a wattmeter between the RS lines and how to accurately calculate power readings based on the motor's configuration and load characteristics.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant expresses confusion about calculating power in a 3-phase system, particularly regarding the relationship between phase and line voltages and currents.
  • Another participant suggests that the wattmeter will sense the phase current multiplied by √3, indicating a correction to the initial analysis.
  • Further contributions clarify that the power calculated for one phase should be multiplied by √3 to compare with total power, but there is uncertainty about the application of this factor.
  • Concerns are raised about the practicality of connecting a wattmeter in series with a phase of the motor, questioning the feasibility of measuring phase current directly.
  • Participants discuss the original multiple-choice answers provided for the problem, with some suggesting that the correct answer is likely 22 kW based on their calculations.
  • One participant notes that the original wording of the question may be unclear, leading to confusion about the setup.
  • Another participant mentions a drawing related to the question, indicating that it may provide additional context for understanding the arrangement.

Areas of Agreement / Disagreement

There is no clear consensus on the correct approach to calculating the wattmeter reading, with multiple interpretations and methods being discussed. Some participants agree on the likely correct answer of 22 kW, while others remain uncertain about the calculations and the role of √3.

Contextual Notes

Participants highlight potential ambiguities in the original problem statement and the setup, as well as the limitations of measuring phase current in a Delta configuration. There is also mention of a drawing that may clarify the arrangement, but its relevance remains uncertain.

ohadbx
Messages
5
Reaction score
0

Homework Statement


hello everyone
I'm a little confused with the whole 3- phase system.
for example:
An AC motor is connected to a 3-phase R-S-T system with 400 volts.
The motor is in Delta configuration and every load is Z=1+2.5j .
A wattmeter is connected between the RS lines.
W=|VRS|*|IR|*cos(∠IR-∠VRS)=?

I tried solving using differenet methods we were taught, but every way i try i get a different result.

For example: 1) I thought that the wattmeter will measure the Real Power of a single load, which should be a third of the total Real Power of the motor. so:
attachment.php?attachmentid=63770&stc=1&d=1383936769.jpg


on the other hand:
attachment.php?attachmentid=63775&stc=1&d=1383937564.jpg


I'm starting to feel lost in this, so any help would be appreciated.

P.S. Maybe I should have done a Y-DELTA transformation? Although I'm not sure what good would that do...

Thank you and have a great weekend
 

Attachments

  • 1.jpg
    1.jpg
    10.4 KB · Views: 501
  • 2.jpg
    2.jpg
    14 KB · Views: 454
Physics news on Phys.org
A wattmeter connected as described will sense the voltage of each phase of the motor, but it will sense more than the current of a single phase of the motor, it will sense the phase current x √3.

With this correction, does that confirm your analysis?
 
Thank you for your reply

when I chekced the reading of the wattmeter (the second solution) I did multply the phase current by sqrt(3).
Or am I not getting your point?
 
What you calculated in the first step is the power in one phase of the motor. You will want to multiply this by √3 to compare it with your second calculation.

Where you write VRS / Z I think there is a missing √3.

and a warm greeting :smile: ... http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif
 
Last edited by a moderator:
Thanks for the nice greeting :smile:

Sadly, I am still unsure of what I am doing wrong.
This is my understaing of the setup:
attachment.php?attachmentid=63794&stc=1&d=13839952995.jpg


To my understanding, in a delta configuration (such as shown),
VLINE=VPHASE , so wouldn't that mean that IPHASE=[itex]\frac{V}{Z}[/itex]? where does the √3 come from (if I want to use the power formula I mentioned in the first solution)?

BTW it has come to my attention that this question was originally a multiple-choise question.
The possible answers were: A. (-44.03) B. 22.07 C. (-14.68) D. 66.21 (all in [kW])
bit I have no Idea which is the correct one.
 

Attachments

  • Note_20131106_184216_2.pdf
    Note_20131106_184216_2.pdf
    64.9 KB · Views: 302
  • Note_20131109_125608_01.jpg
    Note_20131109_125608_01.jpg
    6.3 KB · Views: 429
  • 111.jpg
    111.jpg
    10.7 KB · Views: 492
A wattmeter has 2 pairs of sensing coils, one for voltage and another for current. I think it is unreasonable to believe you can routinely break open a delta motor and connect something in series with one of its phases to sense phase current!

You performed 2 calculations. Basically, the first is for 1/3 of the motor's power. The second is for 1/3 of (√3 of the motor's power).

My contention is that the best you can do is to have the wattmeter measuring the latter (whether you like it or not), sensing VRS and IR. You can't sense the motor's phase current, even if you wish you could. Well, that's my thinking.
 
A wattmeter is connected between the RS lines.
Is that the wording of the original question? It sounds a sloppy way of expressing the arrangement.

It seems motor phase power is 22kW and total power is 66kW. So they must want the answer of 22kW.
 
  • Like
Likes   Reactions: 1 person
NascentOxygen said:
Is that the wording of the original question? It sounds a sloppy way of expressing the arrangement.
Yes, that is the original statement, and in addition there is a drawing like the one I have posted.

I agree with you, I also think the right answer is 22. That means I shouldn't have multiplied by √3 in second solution, but the reason escapes me.

Thank you for your help
 
Last edited:
ohadbx said:
Yes, that is the original statement, and in addition there is a drawing like the one I have posted.
I'd like to see the original drawing. Can you attach it here?
 
  • #10
here you go, though its not very informative.
The switches are for a different, unrelated, part of the question- the setup is changed to Wye.
attachment.php?attachmentid=63854&stc=1&d=1384200685.jpg
 

Attachments

  • 111.jpg
    111.jpg
    8.7 KB · Views: 471
  • #11
So it looks like the construction brings out the ends of each motor phase so that you can connect a meter in series with a single phase of the motor to meter the phase current! (Or at least it is intended to represent that.)

Thanks.
 

Similar threads

  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
4
Views
4K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
7
Views
3K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K