Looking to create a temperature rate of rise table for air

Click For Summary
SUMMARY

The discussion centers on calculating the temperature rate of rise (RoR) in an IT space measuring 20' x 15' x 10' with an 80 kW load, assuming no air conditioning. The ambient temperature is set at 50°F, and the equipment will shut off at temperatures exceeding 105°F. The calculations indicate that the temperature rise occurs rapidly, potentially within seconds, due to the significant heat output. The formula m * Cp * ΔT = Q is essential for determining the heat input and subsequent temperature change.

PREREQUISITES
  • Understanding of thermodynamics, specifically Newton's laws of heat transfer.
  • Familiarity with HVAC systems and their operational parameters.
  • Knowledge of heat capacity and mass calculations in relation to air.
  • Experience with Excel for data analysis and modeling.
NEXT STEPS
  • Research HVAC load calculations for data centers.
  • Learn how to apply the formula m * Cp * ΔT = Q in practical scenarios.
  • Explore methods for measuring and managing heat output in server rooms.
  • Investigate tools for creating temperature rise graphs and simulations.
USEFUL FOR

IT professionals, HVAC engineers, data center managers, and anyone involved in thermal management and equipment safety in high-load environments.

Sola
Messages
8
Reaction score
3
How did you find PF?: Google

l was asked how hot would our IT space get if we lost all air conditioning. The space is 20' x 15' x 10', We keep set point at 70 F and have 80 kW of load. Assuming this exists in a well insulate container with 20 racks of equipment. Doesn't have to be perfect but a general idea as we compare to various equipment failure thresholds
 
Engineering news on Phys.org
Welcome to PF. :smile:

How much airflow is there in and out of the room under those conditions? Are you assuming no forced air at all, so only convection flow? What is the ambient temperature outside of the room and outside of the building? How big are the vents into the bottom of the room and out of the top of the room?

Also, how hot does it need to get in there before some of that load automatically sheds? I assume there are temperature sensors that have some shutdown capability when the racks start overheating?
 
  • Like
Likes   Reactions: russ_watters
I am making broad analysis without many specifics,
No air flow,
minor leakage (10%)
There are split systems in the space.
Ambient I choose is 50 F.
The various IT equip will shut off at various temps above 105 F.
My question is "what is the heat RoR" with the 80 continuing to heat the space. How much time in an emergency before we do a graceful shutdown vs hard stop. I am trying to graph this so we can show operators the data
 
  • Like
Likes   Reactions: berkeman
BTW as a new user, where would I find posting procedures? TY for the help
 
Sola said:
BTW as a new user, where would I find posting procedures? TY for the help
Under INFO at the top of the page you'll find the Rules and About Us pages. But for general posting guidelines, there are only a few:

** Schoolwork-type questions (even for self study) go in the Homework Help forums, and the student is required to show their work before we can help. We can't post solutions for them; we can only help guide them with questions and suggestions so that they figure out their schoolwork problems on their own.

** Technical posts go in the appropriate technical forum (which is why I moved your thread to the ME forum). It's best to post links to what you have been reading to try to figure out your question when starting a new thread. That helps others to see your level of understanding and tailor their responses accordingly.

** In some of the technical forums, there is a "Thread Prefix" A/I/B that is used to indicate the level of discussion that the Original Poster (OP) wants. A is Advanced (graduate school and above), I is Intermediate (undergraduate school level) and B is Beginner (high school level).

** Since we focus on mainstream science here at PF, we will generally require a link to a peer-reviewed journal article to start some of the more advance technical discussions.

That's about it, I think. Feel free to send me a Personal Message (PM, click my avatar and "Start a conversation") if you have any more questions about PF. Enjoy! :smile:
 
Sola said:
l was asked how hot would our IT space get if we lost all air conditioning...Doesn't have to be perfect but a general idea as we compare to various equipment failure thresholds
HVAC engineer here. The short answer is infinity. The longer answer is extremely difficult to calculate but suffice to say the room would be uninhabitable and the IT equipment would fail before it got to an equilibrium - in a matter of minutes.

For the room air, you can calculate the rate of rise from mass, heat capacity and heat input. The mass of equipment won't matter immediately so that should get you through the first 5-10 min.

[Edit] Nope, just ran the numbers and it's seconds, not minutes.
 
Last edited:
  • Wow
  • Like
Likes   Reactions: Lnewqban and berkeman
TY Russ, Is there a formula or calculator to input the room data. Per above without getting very specific on building envelope for a telco hut. 20 x 15 x 10' CMU exterior, r-19 wall insulation, no windows, metal truss roof with 4" roof rigid roof insulation on a metal corrugated deck. We use split hvac systems. I am learning Newton's laws and looking to build an excel sheet that I can do high level comparisons at different loads. TY for comments.
 
Sola said:
TY Russ, Is there a formula or calculator to input the room data. Per above without getting very specific on building envelope for a telco hut. 20 x 15 x 10' CMU exterior, r-19 wall insulation, no windows, metal truss roof with 4" roof rigid roof insulation on a metal corrugated deck. We use split hvac systems. I am learning Newton's laws and looking to build an excel sheet that I can do high level comparisons at different loads. TY for comments.
m * Cp * ΔT = Q (heat input)

And pick a rate (E.G. heat rate per minute, ΔT per minute).

You have a fixed mass of air in the room, it has a certain heat capacity and you apply heat at a certain rate, resulting in a rate of temperature change. That enough to run the calculation yourself?

The rate of temperature rise is way too fast for the heat loss through the walls to matter.
 
  • Like
  • Informative
Likes   Reactions: Lnewqban, Dullard and berkeman
I just did a similar analysis for a customer who wanted me to build him a bitcoin mining container. 80KW in that space (without ventilation or refrigeration) will get really hot really fast (like: RUN!). 80KW is approx 23 Tons of heat load.
 
  • Like
  • Informative
Likes   Reactions: russ_watters and berkeman
  • #10
russ_watters said:
m * Cp * ΔT = Q (heat input)

And pick a rate (E.G. heat rate per minute, ΔT per minute).

You have a fixed mass of air in the room, it has a certain heat capacity and you apply heat at a certain rate, resulting in a rate of temperature change. That enough to run the calculation yourself?

The rate of temperature rise is way too fast for the heat loss through the walls to matter.
So ?
m= mass (volume of air in the space )3000 cu ft or 229 lbs ?
Cp=total heat capacity of air would I use 1 or .718 (Cv)
Delta T
I think so.. Let me take a shot.
My initial approach was to convert the 80 kW to Btuh (276,300) / 60 (minutes), div by 229 (lbs) = 20 deg F per minute. That seemed really high so here I am
 
  • #11
Additionally I would have a start point of 70 F and average ambient of 50 F, as we have locations across the country
 
  • #12
To figure the equilibrium temperature you need the surface area (I got 1700 ft2) and an estimate of the heat transfer coefficient from interior to ambient. With no forced convection (fans) the free convection coefficient would be limiting (unless the wall insulation is really good).

A typical free convection coefficient would be 1 or 2 Btu/hr-ft2-F. The the temperature drop across the wall would then be 80 to 160F (to transfer your 273,000 Btu/hr). So for 50F ambient, the interior would be 130 to 210F. That's about as rough an estimate as you're likely to get. No leakage, no equip shutoff, ...
 
  • #13
Sola said:
So ?
m= mass (volume of air in the space )3000 cu ft or 229 lbs ?
Cp=total heat capacity of air would I use 1 or .718 (Cv)
Delta T
I think so.. Let me take a shot.
My initial approach was to convert the 80 kW to Btuh (276,300) / 60 (minutes), div by 229 (lbs) = 20 deg F per minute. That seemed really high so here I am
Close, but I think you mixed units there. In English units, the heat capacity is about 0.24 (but you didn't use it?). So the answer is about 84F / min.

So, even worse but you were in the right OOM.
 
  • #14
gmax137 said:
To figure the equilibrium temperature you need the surface area (I got 1700 ft2) and an estimate of the heat transfer coefficient from interior to ambient. With no forced convection (fans) the free convection coefficient would be limiting (unless the wall insulation is really good).

A typical free convection coefficient would be 1 or 2 Btu/hr-ft2-F.
Wall insulation was provided and it's really good: R-19 = U of 0.053 BTU/hr/ft2-F. That's why convective heat transfer is usually ignored for walls for building envelope loads.
 
  • Informative
Likes   Reactions: gmax137
  • #15
Thanks @russ_watters -- I didn't know or didn't remember that the R "value" is the inverse of the U (with U in "imperial" units: Btu/hr ft2 F).
russ_watters said:
The short answer is infinity.
Yes, using that 0.05 Btu/hr ft2 F the equilibrium temperature works out to >3000 F. Showing it is silly to ignore the leakage etc. Rather, best to focus on the rate of rise and the given temperature limits, as you said in your original reply.
 
  • Like
Likes   Reactions: russ_watters
  • #16
russ_watters said:
Close, but I think you mixed units there. In English units, the heat capacity is about 0.24 (but you didn't use it?). So the answer is about 84F / min.

So, even worse but you were in the right OOM.
Russ,

Thank you, This is a great learning experience.
 
  • Like
Likes   Reactions: berkeman
  • #17
Russ,
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
 
  • #18
Sola said:
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
I think you're just expecting another variable to be there that isn't. Watts is watts and 80 kW is a lot of watts. Period. Every watt that the data center uses is converted to heat.

Maybe if you think about it in terms of a unit of heat you recognize. Like a hairdryer for example (on full). This is 55 hairdryers.

Or, I live in a 1500 sq ft townhouse in the northeast of the US and my central heating is generously sized. This data center is 4x the heat output of my house's heater in 1/5 the space. It's enough to run all of the air in the room through the heater, with it's 60F temperature rise, in 30 seconds.
 
Last edited:
  • Like
Likes   Reactions: Lnewqban and anorlunda
  • #19
Sola said:
Russ,
Ok now the formula makes sense but I am stunned how much heat is generated and how quick. Still thinking I am missing some variable
I would say that you can’t have so much generated heat within that space.
In my experience designing cooling for server rooms, it is safer and more practical to measure the actual amount of amps used by all the electronic equipment in the room in normal operation.
When the approach was adding up all the amps shown in the nameplate of each piece of equipment, the AC units resulted grossly oversized.

Another way to approach your problem could be to calculate how much heat your AC equipment is normally moving out of the room while keeping set temperature, based on its performance and capacity at normal working temperatures.
 
Last edited:
  • Like
Likes   Reactions: russ_watters

Similar threads

  • · Replies 8 ·
Replies
8
Views
6K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 13 ·
Replies
13
Views
2K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
12
Views
2K
  • · Replies 11 ·
Replies
11
Views
4K
Replies
1
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K