sophiecentaur said:
From the fact that you seem to regard the Earth conductor as a possible backup for the neutral circuit
You misunderstand. The closest thing I've said to that is probably the fact that the neutral could concievably be a backup (or replacement) to ground. That was once standard (cost related) and still exists regularly in dwellings.
Scary. Here's the thing, and yes it's been alluded to already, so long as circumstances, for example wood construction and dryness, ensure that one remains isolated the system works just fine to prevent ground faults from starting a fire with little or no potential for shock.
I can see by your many many citings of RCDs that you are very comfortable in total reliance on them. Unless they are priced at hundreds of dollars apiece I judge your trust as poorly placed. Once again, do you TEST your RCD? Ever? How old are they? Do you have any idea how much GFCIs and the standards behind them have changed in NA just in the last decade? How do you know it will detect any leak in the neutral, and trip in such a condition, instead of happily frying you if you somehow end up solidly connected between neutral and local ground potential?
Consider a situation where your utility loses your PE connection in the circuit that serves your electrical works*. Maybe with a mostly underground system that's difficult to imagine but we will consider it since a great many power lines still exist on poles. You don't own or control the PE connection so as far as maintaining it you are at the mercy of the utility. Even if you were in an underground situation in NA this is not a situation you ever have to worry about. Why is that?
Because at this point of the system the "PE" is the NEUTRAL conductor! Yes, it's the zero potential wire but since it's zero it is used as a fault current path for non-circuit metal parts as well. So when the neutral connection is lost on a UK system, the lights go out. When the neutral connection is opened on a NA system, well, something is likely to go, somewhere. A loss of PE before the service is tantamount to a loss of neutral in the NA system. But when the utility side PE goes out in a UK system,
nothing happens!
This can have serious ramifications aside from the fact that it occurs without indication. Since on the system a circuit conductor exists which is zero
somewhere is in close proximity to a conductor which is zero locally there is the chance of a fault developing between them. The fault will likely happen at a low potential since zeros might be relatively close. But low potential might also create the balance of a current sufficient to start a fire but too low to clear a main. The RCD is intended to prevent this but unless it is self-diagnosing with a fail-safe design it is a single point failure in the protection chain under these circumstances.
I will state this again, if you can't guarantee that a zero will not become more than zero the safest way to handle it is to connect it to as local a zero as possible. Your system gives up on that a step before ours. Probably on cost with no real consideration beyond that. Maybe it's not a big deal there; the world is a bit smaller. It can be a big deal here. As far as knowing where the standards come from, well it's part of continued training that I attend for example informationals put on by the people who are, yes, developing and writing the standards, they are not some inaccessable oracle in a far off high-tower but are in fact regular people like you and me who don't hide their reasoning behind some smokescreen.
The statement that with no faults there will be no trips is idealized, yes. I'm familiar with the devices and their uses, yes they do nuisance trip in all kinds of situations. But you don't appreciate that 5mA point of use devices may be much more abundand than probably even RCDs, and nobody deems them useless due to spurious trips. 30mA range devices are used here, too. They are only permitted to be applied in situations where human safety is not the reason for the ground fault detection, it is an equipment protection standard to keep monster sparks from shooting out of things. Equipment protection is common in another range, the 1000A+ devices that need big overgrown RCD/GFCI circuits to keep a high impedance fault from burning down the gear without ever drawing enough amps to trip a thousands of amp device set to accommodate a large building's inrush.
And I don't consider it to be bringing in extra issues when I'm illustrating my side of an argument with the full implementation of the system I'm favoring. Just as RCDs are integral to the safe function of your side, GFCIs are necessary and required at times on my side. And you still seem to be ignoring my presentation of another reason why the more local the grounding, the better: fault/surge energy dissipation, in other words, abnormal circuit conditions that you seem intent to lump in with Earth return circuiting.
*"Service" or "Service point" = The spot where your main OCP is in UK, the spot where your main OCP and last neutral earthing is in NA. Usually at this point "you own it"
edit: zero will NOT become more than zero